    <font face="Helvetica, Arial, sans-serif">This may be useful:<br>
      <a class="moz-txt-link-freetext" href="http://www.cobrawire.com/lugs/lugs.php?cat=xflex">http://www.cobrawire.com/lugs/lugs.php?cat=xflex</a><br>
      <br>
      <br>
      <br>
      <br>
    </font>
    <div class="moz-cite-prefix">On 2014/4/30, 14:25, William Miller
      wrote:<br>
    </div>
    <blockquote
      cite="mid:B011C0A2-DE9C-4ABD-A1E6-0FD1BE37D5DC@millersolar.com"
      type="cite">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <div>Ray:</div>
      <div><br>
      </div>
      <div>Thanks for sharing the research. If you could forward to me
        of-line an email contact and part number I need to order for
        4/0. <br>
        <br>
        Miller Solar</div>
      <div><br>
        On Apr 30, 2014, at 10:22 AM, Ray Walters <<a
          moz-do-not-send="true" href="mailto:ray@solarray.com">ray@solarray.com</a>>
        wrote:<br>
        <br>
      </div>
      <blockquote type="cite">
        <div>
          <meta content="text/html; charset=ISO-8859-1"
            http-equiv="Content-Type">
          <div class="moz-cite-prefix">What I'm finding in my research
            is that most of the manufacturers are just not keeping up
            with this requirement, meanwhile the use of fine stranded
            cable is increasing dramatically.<br>
            ILSCO, BURNDY, and Quick Cable all barely mention fine
            strand ratings.  I have their catalogs in hand.  Even the
            SMA manual does not mention this issue, I had to call tech
            support.<br>
            BTW, there appears to be some big name integrators just
            using flex cable directly.  Meanwhile, I can share a pic of
            the one lug I torqued down, and didn't like, which lead to
            all this:<br>
            Little copper hairs tearing, or not part of the connection
            at all.<br>
            How did we survive the 90s stuffing welding cable into
            Heinemann breakers in Trace DC boxes?<br>
            <br>
            Also, when you go into major Electrical suppliers that sell
            the flex cable, and ask if the connectors are rated for fine
            stranding, all you get is that "deer in the headlights"
            stare.<br>
            I was used to having to figure all this out in the old days
            of solar, but now that every electrical supplier in town is
            claiming to be a solar expert/ distributor, I really should
            be able to just walk in and get the parts I need for a Code
            compliant installation.  If you sell the inverter and the
            cable, you really should stock the connector.<br>
            <br>
            On another note, the ferrules/ sleeves seem to be the
            ticket, as confirmed by Schneider.  Also they appear to be
            40 times cheaper than pin adapters, and don't take up extra
            room in the wiring compartment.  Now I just have to find
            some TODAY.  Ugh...<br>
            <br>
            And like Allan, I lost sleep over this issue last night.  <br>
            <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
            On 4/30/2014 10:38 AM, Glenn Burt wrote:<br>
          </div>
          <blockquote
            cite="mid:007101cf6492$a6a83cc0$f3f8b640$@burt@glbcc.com"
            type="cite">
            <pre wrap="">There are many available lugs that are listed for use with finely stranded
conductors - this is not an excuse to not use the proper lugs and required
equipment to ensure a safe and reliable installation (per the NEC).

Thomas & Betts is the manufacturer I use.
Indeed the tool is pricey, however it is  necessary to produce a compliant
installation (per 110.3(B)).

-Glenn

-----Original Message-----
From: <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
[<a moz-do-not-send="true" class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of jay peltz
Sent: Wednesday, April 30, 2014 10:09 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Flexible stranded Connectors

Hi ray

As an FYI. Most of the lugs we all use are not "rated" for fine stranded
wire. 
 Quick cable is the only one I'm aware of that if you use their tool and
ends says its UL for fine stranded. 

I prefer ferrules for those applications vs pin adapters. 
(Schneider XW inverter BOS box comes with arctic ultra flex wire with
ferrules)

Jay

Peltz power


</pre>
            <blockquote type="cite">
              <pre wrap="">On Apr 29, 2014, at 10:48 PM, Ray Walters <a moz-do-not-send="true" class="moz-txt-link-rfc2396E" href="mailto:ray@solarray.com"><ray@solarray.com></a> wrote:

Hi All;

In order to avoid any of my work showing up in someone's slideshow of
</pre>
            </blockquote>
            <pre wrap="">horrors, I'm trying to find the correct way to wire 3 Sunny Islands with
Cobra X flex cable.
</pre>
            <blockquote type="cite">
              <pre wrap="">While it doesn't actually mention it in the SMA manual, a call to SMA tech
</pre>
            </blockquote>
            <pre wrap="">support confirmed my suspicions: the DC lugs in the inverter are NOT rated
for flex or fine stranded cable.
</pre>
            <blockquote type="cite">
              <pre wrap="">Both SMA and CED recommended I try Grainger's for crimp on adapters.
</pre>
            </blockquote>
            <pre wrap="">Grainger had no clue, and nothing came up in searches there.
</pre>
            <blockquote type="cite">
              <pre wrap="">From a trade show, I have an ILSCO lug book, that shows a crimp on 
pigtail adapter.  It does not mention whether its flex rated though on the
</pre>
            </blockquote>
            <pre wrap="">crimp side of the adapter, as the adapter is used primarily to land over
sized cables into smaller lugs.  (2/0 to #1, for instance) The best I've
found so far, is NSI, which makes sleeves, that are installed around the
wire, right in the connection:
</pre>
            <blockquote type="cite">
              <pre wrap=""><a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.nsiindustries.com/products/electrical/connectors/compressio">http://www.nsiindustries.com/products/electrical/connectors/compressio</a>
n-connectors/copper-compression/fsflex-cable-sleeve.aspx
I also found a Schneider white paper recommending sleeves with their lugs:
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://static.schneider-electric.us/docs/Circuit%20Protection/0515DB03">http://static.schneider-electric.us/docs/Circuit%20Protection/0515DB03</a>
01.pdf

So who has used these sleeves, and where do I get them?
The sleeves seem like a decent compromise, whilst the ILSCO pigtail 
adapters are coming in at $40/ ea...... (ouch)

On the internet, I'm seeing several examples of X flex used directly (no
</pre>
            </blockquote>
            <pre wrap="">adapters) with the Sunny Islands, so are folks just blowing off articles
690.31(F) and 110.14, that specify the connector be rated for flex cable?
</pre>
            <blockquote type="cite">
              <pre wrap="">And finally, couldn't SMA use a lug that was flex rated?
For example, Marathon makes Class K rated mechanical Lugs: 
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.marathonsp.com/NewRatings.html">http://www.marathonsp.com/NewRatings.html</a>
I'd use THHN, but I really don't feel good about wiring the Heineman
</pre>
            </blockquote>
            <pre wrap="">breakers with that stiff a wire.  I've cracked breaker cases
before......that's why the X flex is industry standard for off grid DC.
</pre>
            <blockquote type="cite">
              <pre wrap="">Thanks for your help,

--
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

_______________________________________________

</pre>
            </blockquote>
            <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
            <br>
            <fieldset class="mimeAttachmentHeader"></fieldset>
            <br>
            <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
          </blockquote>
          <br>
        </div>
      </blockquote>
      <blockquote type="cite">
        <div><span>_______________________________________________</span><br>
          <span>List sponsored by Home Power magazine</span><br>
          <span></span><br>
          <span>List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
          <span></span><br>
          <span>Change email address & settings:</span><br>
          <span><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List rules & etiquette:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
          <span></span><br>
          <span>Check out participant bios:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
          <span></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>