<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <div class="moz-cite-prefix">Funny the timing of the Wrenches list,
      just Saturday I added some Enphase inverters to an existing GTB 
      Outback system.  The Enphase are not AC coupled to the Outbacks,
      as I didn't want to get into the battery charging issues, and the
      customer has plenty of PV relative to the battery size.  However,
      we're having a communication issue as well.  I'm guessing that the
      Envoy can't be on the Outback side of the system with the Enphase
      inverters being on the grid side.  So, is there an elegant
      solution besides putting the Envoy on the grid side of the system 
      (which is out in the garage)  The whole house is on back up, so no
      grid direct circuits are available there, and the wiring is such
      that it would not be easy to change that either.<br>
      I was actually going to add a transfer switch to the Enphase
      circuit, so that in an extended outage, the customer could have
      the option of bringing in the Enphase inverters.  I have the
      Enphase breaker in the Outback Flex 500 box already, so at least
      that would be simple.<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 4/14/2014 12:49 PM, Nick Soleil wrote:<br>
    </div>
    <blockquote
cite="mid:CAAV1817skT0rdJWxeL8fnQH2Ztw2K-RPb73bDgwdpiLjhGZxhg@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>Hi Benn,<br>
          <br>
        </div>
        You can remove the microinverters from an Envoy, but it requires
        a laptop and a network cable.  Call me and we can talk.  We have
        a lot of big projects with home builders, and I am more than
        happy to share our best practices with you.  My cell number is
        707-321-2937.<br>
      </div>
      <div class="gmail_extra"><br>
        <br>
        <div class="gmail_quote">On Mon, Apr 14, 2014 at 11:42 AM, Benn
          Kilburn <span dir="ltr"><<a moz-do-not-send="true"
              href="mailto:benn@skyfireenergy.com" target="_blank">benn@skyfireenergy.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div dir="ltr">
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">August,</div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">
                I'm being told that "we" (as opposed to "Enhpase")
                cannot delete or remove rogue inverters from the Array
                Builder.  Enphase has to do this step.   And if you just
                don't include the rogue inverters in the Array Builder
                you are building for a particular system, you will still
                receive the production data from the rogues.  (2nd hand
                info, so......?)</div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif"><br>
              </div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">Louis,</div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">
                Since some of these are home builder's 'show homes' and
                new home builds, there is the possibility that internet
                has not always been set up yet, so in some of these
                cases the inverters may not have been dedicated to a
                particular Envoy yet.</div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif"><br>
              </div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">If "we" cannot remove rogue inverters
                from a particular Envoy, then we will likely just send
                the serial numbers of the Envoy and respective inverters
                to Enphase and let them sort it out.</div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif"><br>
              </div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">We may consider the Array Gun scanner
                option. </div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif"><br>
              </div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">Anyone else have any feedback on this
                option?</div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif"><br>
              </div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif"><br>
              </div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">
                Cheers,</div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif">Benn</div>
              <div class="gmail_default" style="font-family:'trebuchet
                ms',sans-serif"><br>
              </div>
            </div>
            <div class="HOEnZb">
              <div class="h5">
                <div class="gmail_extra"><br>
                  <br>
                  <div class="gmail_quote">On Mon, Apr 14, 2014 at 12:21
                    PM, Louis Woofenden <span dir="ltr"><<a
                        moz-do-not-send="true"
                        href="mailto:louis@woofenden.net"
                        target="_blank">louis@woofenden.net</a>></span>
                    wrote:<br>
                    <blockquote class="gmail_quote" style="margin:0 0 0
                      .8ex;border-left:1px #ccc solid;padding-left:1ex">
                      <div bgcolor="#FFFFFF" text="#000000">
                        <div><br>
                          Hi Benn,<br>
                          <br>
                          We've run into these problems when
                          simultaneously commissioning systems in
                          adjacent units of a housing development where
                          we did PV systems on all homes, and 2-3 homes
                          are on one utility transformer. I'm a little
                          surprised that the Envoy picked up inverters
                          from an existing system, unless those
                          microinverters were never associated with
                          another Envoy. My understanding from Enphase
                          is that once they are "bound" to one Envoy,
                          they won't be easily picked up in a device
                          scan. But maybe I'm missing something, or got
                          bad info from tech support.<br>
                          <br>
                          We've definitely had to work with Enphase tech
                          support on a couple of systems to remove
                          inverters from one Envoy, then do a device
                          scan on another Envoy, as August suggested.
                          Another option is to spend the money for the
                          Array Gun scanner (SocketMobile CHS7xi
                          scanner), and use the iOS Enphase Installer
                          Toolkit app to build arrays and "provision"
                          the Envoy, sending the inverter serial numbers
                          directly to the Envoy, without need for a
                          device scan. Not sure if this is worth it at
                          the $450 retail price for the scanner, but if
                          you can find one used, it might be. I recently
                          was able to pick one up for about $250 used.<br>
                          <br>
                          Haven't yet had issues serious enough to
                          require LCFs on residential systems. Crossing
                          my fingers on that one.<br>
                          <br>
                          Best,<br>
                          <br>
                          Louis Woofenden<br>
                          <br>
                          Net Zero Solar, Tucson, AZ
                          <div>
                            <div><br>
                              <br>
                              On 4/14/14, 9:08 AM, Benn Kilburn wrote:<br>
                            </div>
                          </div>
                        </div>
                        <blockquote type="cite">
                          <div>
                            <div>
                              <div dir="ltr">
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif">Wrenches,</div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif">I'm sure i read a
                                  thread on this list about dealing with
                                  this, i've searched but cannot find
                                  it.  If anyone recalls the subject
                                  line, please let me know.</div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif"><br>
                                </div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif">We are dealing with
                                  setting up Enphase monitoring in
                                  neighborhoods with other Enphase
                                  systems nearby and these 'other'
                                  systems are being picked up by the
                                  EMU.</div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif"><br>
                                </div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif">A few weeks ago we
                                  finished a 14 module (3.5kW) install
                                  and i plugged in the EMU to search for
                                  the inverters.  As it was picking up
                                  the first few inverters, it was
                                  showing several hundred kWh already
                                  produced???  Not bad for a 14 module
                                  system being in operation for 10
                                  min!!!  (yes the inverters were new,
                                  out of the box)</div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif"><br>
                                </div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif">After 30-40 min, the
                                  EMU had picked up 28 inverters in
                                  total.  There were 14 on the system we
                                  had just installed, and 14 on a house
                                  across the street that we had
                                  installed back in Nov'13.  I'm pretty
                                  sure it had picked up the 14 across
                                  the street before picking up the ones
                                  we just installed.<br>
                                  Funny that we can sometimes have
                                  communication issues btwn the
                                  inverters and EMU in some houses, and
                                  here we have EMU's picking up
                                  inverters across the street!?!</div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif"> <br>
                                </div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif">Anywho... has anyone
                                  dealt with this and streamlined a
                                  process with Enphase to remedy this
                                  issue?</div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif"> <br>
                                </div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif">Cheers,</div>
                                <div class="gmail_default"
                                  style="font-family:trebuchet
                                  ms,sans-serif">Benn</div>
                              </div>
                              <br>
                              <fieldset></fieldset>
                              <br>
                            </div>
                          </div>
                          <div>
                            <pre>_______________________________________________
List sponsored by Home Power magazine

List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a moz-do-not-send="true" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a moz-do-not-send="true" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
                          </div>
                        </blockquote>
                        <br>
                      </div>
                      <br>
                      _______________________________________________<br>
                      List sponsored by Home Power magazine<br>
                      <br>
                      List Address: <a moz-do-not-send="true"
                        href="mailto:RE-wrenches@lists.re-wrenches.org"
                        target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      Change email address & settings:<br>
                      <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                        target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List rules & etiquette:<br>
                      <a moz-do-not-send="true"
                        href="http://www.re-wrenches.org/etiquette.htm"
                        target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                      <br>
                      Check out participant bios:<br>
                      <a moz-do-not-send="true"
                        href="http://www.members.re-wrenches.org"
                        target="_blank">www.members.re-wrenches.org</a><br>
                      <br>
                      <br>
                    </blockquote>
                  </div>
                  <br>
                </div>
              </div>
            </div>
            <br>
            _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change email address & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules & etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm"
              target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
            <br>
          </blockquote>
        </div>
        <br>
        <br clear="all">
        <br>
        -- <br>
        <div dir="ltr">
          <p style="margin:0in 0in 0.0001pt"><span
              style="font-size:14pt">Cordially,</span></p>
          <p style="margin:0in 0in 0.0001pt"><b><span
                style="font-size:14pt">Nick Soleil</span></b><span
              style="font-size:14pt"></span></p>
          <p style="margin:0in 0in 0.0001pt"><b><span>Field Applications
                Engineer<br>
              </span></b></p>
          <p style="margin:0in 0in 0.0001pt"><b><span
                style="color:rgb(227,108,10)">Enphase Energy</span></b></p>
          <p style="margin:0in 0in 0.0001pt"><span></span><span>Mobile:
              <a moz-do-not-send="true" value="+17073212937">(707)
                321-2937</a></span></p>
          <p style="margin:0in 0in 0.0001pt"><a moz-do-not-send="true"
href="http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten"
              target="_blank"><br>
            </a></p>
          <p style="margin:0in 0in 0.0001pt">
            <a moz-do-not-send="true"
href="http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten"
              target="_blank"><font color="#000000" size="4"><b>MyEnlighten
                  is Coming. </b>Get Ready</font></a><br>
            <b><span style="color:rgb(227,108,10)"></span></b></p>
          <p style="margin:0in 0in 0.0001pt"><a moz-do-not-send="true"
href="http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012"
              target="_blank"><font><span
                  style="font-family:Arial,sans-serif"><b><span
                      style="color:rgb(255,102,0)"><br>
                    </span></b></span></font></a></p>
          <p style="margin:0in 0in 0.0001pt"><span>1420 North McDowell<br>
            </span></p>
          <p style="margin:0in 0in 0.0001pt"><span>Petaluma, CA 94954</span></p>
          <p style="margin:0in 0in 0.0001pt"><span></span></p>
          <p style="margin:0in 0in 0.0001pt"><span><a
                moz-do-not-send="true"
                href="http://www.enphaseenergy.com/" target="_blank">www.enphase.com</a></span></p>
          <p style="margin:0in 0in 0.0001pt"><span>P: (707) 763-4784
              x7267</span></p>
          <p style="margin:0in 0in 0.0001pt"><span>F: (707) 763-0784</span></p>
          <p style="margin:0in 0in 0.0001pt"><span>E: <a
                moz-do-not-send="true"
                href="mailto:nsoleil@enphaseenergy.com" target="_blank">nsoleil@enphaseenergy.com</a></span></p>
          <p style="margin:0in 0in 0.0001pt"><br>
          </p>
          <p style="margin:0in 0in 0.0001pt">
            NABCEP Certified Solar PV Installer #03262011-300</p>
          <p style="margin:0in 0in 0.0001pt">California C10 Licensed
            Electrician #986315</p>
          <p style="margin:0in 0in 0.0001pt">Texas Master Electrician
            #284451<br>
          </p>
          <p style="margin:0in 0in 0.0001pt">
            <span></span></p>
          <p style="margin:0in 0in 0.0001pt"><span></span></p>
          <p style="margin:0in 0in 0.0001pt"><span></span></p>
          <span></span>
          <p>“Don’t get me wrong: I love nuclear energy! It’s just that
            I prefer fusion to fission. And it just so happens that
            there’s an enormous fusion reactor safely banked a few
            million miles from us. It delivers more than we could ever
            use in just about 8 minutes. And it’s wireless!”  <br>
          </p>
          <p>- William McDonough
            <span></span></p>
        </div>
      </div>
      <pre>
This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. 



<fieldset class="mimeAttachmentHeader"></fieldset>
<pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>

</pre>
    </blockquote>
    <br>
  </body>
</html>