<div dir="ltr"><div><div><div><div>Hi Benn,<br><br></div>Our customer service team can help you resolve this issue, and I am also happy to speak with you about this.  <br><br></div>That
 is a somewhat unusual scenario, because once an array of microinverters
 has been communicating with one Envoy (EMU was the original product 
name,) then those microinverters should be associated with that Envoy.  
For the scenario that you described to occur, the older site's Envoy 
must have been removed or not communicating with it's microinverters.  
Since those older microinverters have not been communicating with any 
other EMU or Envoy for a while, they reported all of their production 
data to the new Envoy when you plugged it in.  The situation you 
described can also occur when the Envoy or EMU had been previously 
installed at another system and already was holding that data in it.<br>


<br></div><div>If you want to remove the other devices from the Envoy, 
you can connect the Envoy to a laptop or to a network, and access the 
local host page of the Envoy by entering the IP Address that is 
displayed on the Envoy's LCD screen into you browser's address bar.  
Once you've accessed the Envoy's local host page, you can delete the 
extra devices from the device menu.  To access that menu, you will need 
to enter 'admin' for the user name and 'admin' for the password.<br>

<br></div><div>If the Envoy has reported those erroneous devices from 
the Envoy to the web, then those devices must also be removed from 
Enlighten, as August mentioned.<br></div><div>
<br></div><div>This scenario you described, with two arrays reporting to
 a single Envoy, can only occur when the separate residences share a 
common utility transformer.  If you are developing a large project with 
many homes or apartments on the same transformer,  then we have some 
best practices that we recommend, to ensure a trouble free 
commissioning.  You can view our Multitenant Application Note online. <br>


<br></div><div>I would say that Line Communication Filters are not 
necessary for this application.  LCFs are really designed for commercial
 scale projects.  We have evaluated a number of smaller, 20A to 60A 
filters that are available for filtering:powerline communications in 
single phase applications, but they are likely not needed in your 
scenario.  That technical brief, Filters for Single Phase Applications, 
is available on our website.<br>


<br></div><div>For commercial scale applications, some of these same 
design parameters can come into play.  Our Envoy is limited to 600 
microinverters, so a large system may need to use powerline filters or 
transformers to isolate the separate Envoy's communication domains.  You
 can read more about that in our Commercial Design Guide online.<br>


</div><div><br></div>All of our US downloads are available at: <a href="http://enphase.com/global/resources/geo_us/" target="_blank">http://enphase.com/global/resources/geo_us/</a>  The docs discussed are primarily located under our tech briefs.<br>

</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Mon, Apr 14, 2014 at 11:21 AM, Louis Woofenden <span dir="ltr"><<a href="mailto:louis@woofenden.net" target="_blank">louis@woofenden.net</a>></span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <div><br>
      Hi Benn,<br>
      <br>
      We've run into these problems when simultaneously commissioning
      systems in adjacent units of a housing development where we did PV
      systems on all homes, and 2-3 homes are on one utility
      transformer. I'm a little surprised that the Envoy picked up
      inverters from an existing system, unless those microinverters
      were never associated with another Envoy. My understanding from
      Enphase is that once they are "bound" to one Envoy, they won't be
      easily picked up in a device scan. But maybe I'm missing
      something, or got bad info from tech support.<br>
      <br>
      We've definitely had to work with Enphase tech support on a couple
      of systems to remove inverters from one Envoy, then do a device
      scan on another Envoy, as August suggested. Another option is to
      spend the money for the Array Gun scanner (SocketMobile CHS7xi
      scanner), and use the iOS Enphase Installer Toolkit app to build
      arrays and "provision" the Envoy, sending the inverter serial
      numbers directly to the Envoy, without need for a device scan. Not
      sure if this is worth it at the $450 retail price for the scanner,
      but if you can find one used, it might be. I recently was able to
      pick one up for about $250 used.<br>
      <br>
      Haven't yet had issues serious enough to require LCFs on
      residential systems. Crossing my fingers on that one.<br>
      <br>
      Best,<br>
      <br>
      Louis Woofenden<br>
      <br>
      Net Zero Solar, Tucson, AZ<div><div class="h5"><br>
      <br>
      On 4/14/14, 9:08 AM, Benn Kilburn wrote:<br>
    </div></div></div>
    <blockquote type="cite"><div><div class="h5">
      <div dir="ltr">
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">Wrenches,</div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">I'm sure i read a thread on this list about
          dealing with this, i've searched but cannot find it.  If
          anyone recalls the subject line, please let me know.</div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif"><br>
        </div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">We are dealing with setting up Enphase
          monitoring in neighborhoods with other Enphase systems nearby
          and these 'other' systems are being picked up by the EMU.</div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif"><br>
        </div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">A few weeks ago we finished a 14 module (3.5kW)
          install and i plugged in the EMU to search for the inverters.
           As it was picking up the first few inverters, it was showing
          several hundred kWh already produced???  Not bad for a 14
          module system being in operation for 10 min!!!  (yes the
          inverters were new, out of the box)</div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif"><br>
        </div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">After 30-40 min, the EMU had picked up 28
          inverters in total.  There were 14 on the system we had just
          installed, and 14 on a house across the street that we had
          installed back in Nov'13.  I'm pretty sure it had picked up
          the 14 across the street before picking up the ones we just
          installed.<br>
          Funny that we can sometimes have communication issues btwn the
          inverters and EMU in some houses, and here we have EMU's
          picking up inverters across the street!?!</div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">
          <br>
        </div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">Anywho... has anyone dealt with this and
          streamlined a process with Enphase to remedy this issue?</div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">
          <br>
        </div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">Cheers,</div>
        <div class="gmail_default" style="font-family:trebuchet ms,sans-serif">Benn</div>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      </div></div><div class=""><pre>_______________________________________________
List sponsored by Home Power magazine

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
    </div></blockquote>
    <br>
  </div>

<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><br>-- <br><div dir="ltr"><p style="margin:0in 0in 0.0001pt"><span style="font-size:14pt">Cordially,</span></p><p style="margin:0in 0in 0.0001pt"><b><span style="font-size:14pt">Nick Soleil</span></b><span style="font-size:14pt"></span></p>



        <p style="margin:0in 0in 0.0001pt"><b><span>Field Applications Engineer<br></span></b></p>
        <p style="margin:0in 0in 0.0001pt"><b><span style="color:rgb(227,108,10)">Enphase Energy</span></b></p><p style="margin:0in 0in 0.0001pt"><span></span><span>Mobile: <a value="+17073212937">(707) 321-2937</a></span></p>

<p style="margin:0in 0in 0.0001pt"><a href="http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten" target="_blank"><br></a></p><p style="margin:0in 0in 0.0001pt">

<a href="http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten" target="_blank"><font color="#000000" size="4"><b>MyEnlighten is Coming. </b>Get Ready</font></a><br>

<b><span style="color:rgb(227,108,10)"></span></b></p><p style="margin:0in 0in 0.0001pt"><a href="http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012" target="_blank"><font><span style="font-family:Arial,sans-serif"><b><span style="color:rgb(255,102,0)"><br>

</span></b></span></font></a></p>
        <p style="margin:0in 0in 0.0001pt"><span>1420 North McDowell<br></span></p>
        <p style="margin:0in 0in 0.0001pt"><span>Petaluma, CA
            94954</span></p><p style="margin:0in 0in 0.0001pt"><span></span></p>
        
        <p style="margin:0in 0in 0.0001pt"><span><a href="http://www.enphaseenergy.com/" target="_blank">www.enphase.com</a></span></p>
        <p style="margin:0in 0in 0.0001pt"><span>P: (707)
            763-4784 x7267</span></p>
        <p style="margin:0in 0in 0.0001pt"><span>F: (707)
            763-0784</span></p>
        <p style="margin:0in 0in 0.0001pt"><span>E: <a href="mailto:nsoleil@enphaseenergy.com" target="_blank">nsoleil@enphaseenergy.com</a></span></p><p style="margin:0in 0in 0.0001pt"><br></p><p style="margin:0in 0in 0.0001pt">

NABCEP Certified Solar PV Installer #03262011-300</p><p style="margin:0in 0in 0.0001pt">California C10 Licensed Electrician #986315</p><p style="margin:0in 0in 0.0001pt">Texas Master Electrician #284451<br></p><p style="margin:0in 0in 0.0001pt">

<span></span></p><p style="margin:0in 0in 0.0001pt"><span><a href="mailto:nsoleil@enphaseenergy.com" target="_blank"></a></span></p><p style="margin:0in 0in 0.0001pt"><span></span></p><span></span><p>“Don’t get me wrong: I love nuclear energy! It’s just that I prefer 
fusion to fission. And it just so happens that there’s an enormous 
fusion reactor safely banked a few million miles from us. It delivers 
more than we could ever use in just about 8 minutes. And it’s wireless!”  <br></p><p>- William McDonough
<span></span></p></div>
</div>

<pre>

This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message.