<div dir="ltr">Before I spent any money, I would hire a PE with solar experience to give you an option. I doubt solar iinverters, which are current limited, would be a fault current issue. Usually fault current rating is a factor of the internal resistance of the secondary winding of a high voltage transformer. Solar inverters can't produce those kind of short circuit currents and are not a factor.</div>
<div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Mar 27, 2014 at 2:05 PM, Karl Jaeger <span dir="ltr"><<a href="mailto:kjaeger@lightwavesolar.com" target="_blank">kjaeger@lightwavesolar.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">





<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="color:#1f497d">Esteemed Wrenches,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">We’ve recently run into an issue with a local distributor citing network fault current on a split-phase service as a reason to prevent interconnection of our customer’s solar array. They’ve given us the options
 of reducing our system size from 36.5kW-DC to 15kW-DC, or having the customer upgrade to 3-phase at a soft price of $20-30K. We’re looking at 32kW of inverters on a 167kVA transformer.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">Does anyone have experience on circumventing the issue of network fault current? Any experience with Fault Current Limiters?<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">Much appreciated,<u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><b>Karl Jaeger<u></u><u></u></b></p>
<p class="MsoNormal"><b>Design/Build Engineer<u></u><u></u></b></p>
<p class="MsoNormal"><b>LightWave Solar Electric LLC<u></u><u></u></b></p>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>

<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div><div>
Cell: 264.235.5670</div><div>Skype: netconcepts</div>
</div>