<div dir="ltr"><div class="gmail_default" style="font-family:verdana,sans-serif">Both the bus and conductors need to be rated for 217 amps minimum. As you mentioned, the bus is not a problem. The way I interpret it, the conductor size required would be after derate factors are applied. The rating of the conductor is ultimately dependent on the derate factors.</div>

<div class="gmail_default" style="font-family:verdana,sans-serif"><br></div><div class="gmail_default" style="font-family:verdana,sans-serif">If you can locate your subpanel adjacent to the main distribution panel, you may be able to use Exception #3 to 310.15(B)(2) by connecting the panels with a short nipple. I assume you are just looking at a number of conductor derate and not an ambient temperature derate.</div>

<br><div id="WISESTAMP_SIG_gmail_session"><div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif"><div style="margin:0 0 8px 0"><p style="margin:0"><span><span>Jason Szumlanski</span></span></p><p style="margin:0">

</p><div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">Fafco Solar</div><br> <p></p><div style="clear:both"></div></div><img src="https://wisestamp.appspot.com/pixview.gif?p=chrome&v=3.31.0&t=1393961350220&u=ce9344a8140ce271" width="1" height="1"></div>

</div><div class="gmail_extra"><br><br><div class="gmail_quote">On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander <span dir="ltr"><<a href="mailto:kirk@vtsolar.com" target="_blank">kirk@vtsolar.com</a>></span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="font-size:14.0pt">Hello,<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:14.0pt">I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker. My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 = 270 amps. That’s less than the sum of the two breakers of 260 amps, so no issue there. The conductors between sub and main panel have to be rated for at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after derating the conductor?<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:14.0pt"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">Kirk Herander<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:14.0pt">VT Solar, LLC<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">dba Vermont Solar Engineering<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">NABCEP<sup>TM </sup>Certified Inaugural Certificant<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:14.0pt">NYSERDA-eligible Installer<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">VT RE Incentive Program Partner<u></u><u></u></span></p><p class="MsoNormal">

<span style="font-size:14.0pt"><a href="tel:802.863.1202" value="+18028631202" target="_blank">802.863.1202</a><u></u><u></u></span></p><p class="MsoNormal"><u></u> <u></u></p></div></div></blockquote></div><br></div></div>