<div dir="ltr">That's total nonsense. Most of our installs involve a generator, as generators are very common here due to intermittent electrical supply and hurricanes. We also sell and install generators and I am a tech.<div>
A decent heavy generator will produce electricity that will fall within the IEEE 1547 specifications for grid tied interconnections. Additionally, in our area, we alter those settings to widen the windows as the electricity supply on an island is not as stable as a large grid.</div>
<div><br></div><div>My rule of thumb is that no lockout is required if there is no risk of backfeeding the generator, that is, if the load will always exceed the solar output by a reasonable factor. We have customers that have constant loads in the 40 to 80KW range, and so 20KW of PV will never cause a problem. Residential is the larger issue, as there is often no load. </div>
<div>A generator's output is controlled by the Automatic Voltage Regulator or AVR. It senses the voltage at the terminals of the alternator and changes the excitation to keep the voltage constant. </div><div>Usually the generator's controller has voltage sensing and will stop the generator if the voltage exceeds limits.</div>
<div>If the solar inverter is making power and there is no load, it will increase the voltage until it finds enough load, or trips. If the generator sees the increased voltage and the AVR cannot reduce the excitation enough to control it, the controller MAY shut down the generator.</div>
<div>A generator's controller and AVR presumes it is the only source of power on the electrical system. The inverter presumes it is connected to an infinitely large grid system that can absorb all power generated.</div>
<div><br></div><div>Our usual solution is to put a contactor in front of the inverter controlled by voltage from the generator, or ideally by a contact on the transfer switch. </div><div><br></div><div>It may be possible to program the generator to run faster or slower so as to keep the frequency outside the inverter limits, but you run the risk that a future tech will adjust the inverter or generator.</div>
<div><br></div><div><br></div><div><br></div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Sat, Feb 8, 2014 at 11:32 AM, Kirk Herander <span dir="ltr"><<a href="mailto:kirk@vtsolar.com" target="_blank">kirk@vtsolar.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="font-size:14.0pt">Hello,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:14.0pt"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">I recently posed the question to Solaredge tech support, wondering if their inverter, in this case a 20kw 480 3-phase, would have any issues if it were connected to an AC panel backed up by a generator. They told me no problem, for the inverter’s anti-islanding will work if it sees the “generator frequency” and therefore will not try to push PV power to the panel. But isn’t 60 hz, 60hz regardless of origin? There’s got to be more to it than that. I question this because I asked the same to SMA several years ago and they were hard-set against connecting Sunnyboys to a panel with generator backup, so I always would establish the point of interconnection upstream of the generator feed. Comments? Thanks.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:14.0pt"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">Kirk Herander<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">VT Solar, LLC<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:14.0pt">dba Vermont Solar Engineering<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">NABCEP<sup>TM </sup>Certified Inaugural Certificant<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:14.0pt">NYSERDA-eligible Installer<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:14.0pt">VT RE Incentive Program Partner<u></u><u></u></span></p><p class="MsoNormal">
<span style="font-size:14.0pt"><a href="tel:802.863.1202" value="+18028631202" target="_blank">802.863.1202</a><u></u><u></u></span></p><p class="MsoNormal"><u></u> <u></u></p></div></div><br>_______________________________________________<br>

List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div><div>
Cell: 264.235.5670</div><div>Skype: netconcepts</div>
</div>