    Wrenches,<br>
    I need a bit of help here if you have it. Since 2002 we have
    installed somewhere between 30 and 35 systems with sealed batteries
    installed in manufactured enclosures, originally Outback enclosures
    and in recent years Midnite MNBE enclosures. At least ten of these
    have been indoors in one form or another - usually a laundry or
    mechanical room. Our battery of choice is Concorde SunXtender. We
    have only added mechanical ventilation (Zephyr Power-Vent to
    outside) if the battery enclosure itself is sealed. Nearly all of
    these have been permitted and inspected systems, and we have never
    had a problem with the inspectors. Of course, we always vent flooded
    systems to the outside, nearly always using a Power Vent fan.<br>
    <br>
    Now we have. An AHJ failed a system for lack of ventilation, and our
    attempts to resolve it have not been effective. The Chief Electrical
    Inspector has weighed in, and we are right at the point of filing a
    Request for Code Interpretation with the New Mexico Electrical
    Division Technical Advisory Panel. <br>
    <br>
    I have not wanted to just add ventilation to pass inspection because
    of the precedent doing so is likely to set for future installations.
    The GC on the job supports my attempts to push back, as do the
    homeowners. The Chief Inspector thinks that the 700 square foot
    unheated room in which our system is installed is a bedroom; it's
    actually a storeroom for the homeowners' collectible book home
    business.<br>
    <br>
    My request: please send me documented work by others establishing
    that PV systems with sealed VRLA batteries are used specifically
    because they are considered safe without venting to the outside. If
    you know of good online links, I could use them too. For example,
    the AHJ asked for a document stating that the batteries or the
    enclosure were specifically approved for this use in an indoor
    location. I can't - Midnite battery enclosures are simply listed to
    UL508A, which is "industrial control panels" and there's nothing
    specific to this application in the standard.<br>
    <br>
    To me this is a common-sense issue, but common sense doesn't cut it
    when needing to prove a procedure. Can anyone help?<br>
    <br>
    For what it's worth, or for those Wrenches with too much spare time,
    below is the text of the original defense of our installation that I
    sent to the AHJ. His response was that he's not an electrical
    engineer and this would have to be taken upstairs. For what it's
    worth, I'm not an EE either... My frustration is showing, I'm sure.<br>
    <br>
    Thank you for any links, reports or other resources you may be able
    to send my way.<br>
    Allan<br>
    <div class="moz-forward-container"><br>
      <br>
      -------- Original Message --------<br>
      <br>
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      Mr. [AHJ],<br>
      I have done some research as followup to our discussion last week
      about battery venting for the [X] job. Here are several
      perspectives on the issue:<br>
      <br>
      The NEC Section 480.9(A) states only that "Provisions shall be
      made for sufficient diffusion and ventilation of the gases from
      the battery to prevent the accumulation of an explosive mixture".
      At root, you are questioning whether ventilation of the batteries
      into the storeroom at the [X] home is sufficient under worst-case
      conditions.<br>
      <br>
      The NEC Handbook entries for Section 480.9(A), which are
      considered as explanatory support documentation and are not Code
      requirements, include two paragraphs that are fundamentally
      contradictory to each other. The two read: <br>
      <blockquote> The intent of 480.9(A) is not to mandate mechanical
        ventilation. Hydrogen disperses rapidly and requires little air
        movement to prevent accumulation. Unrestricted natural air
        movement in the vicinity of the battery, together with normal
        air changes for occupied spaces or heat removal, normally is
        sufficient. If the space is confined, mechanical ventilation may
        be required in the vicinity of the battery.<br>
      </blockquote>
      This paragraph refers to batteries in general, including flooded
      batteries which release hydrogen gas as a normal part of the
      charging process. The Handbook section goes on to specifically
      identify sealed batteries as being unlikely to release explosive
      gases:<br>
      <blockquote>Although valve-regulated batteries are often referred
        to as "sealed," they actually emit very small quantities of
        hydrogen gas under normal operation and are capable of
        liberating large quantities of explosive gases if overcharged.
        These batteries therefore require the same amount of ventilation
        as their vented counterparts."<br>
      </blockquote>
      Well, no, not exactly. Valve-regulated batteries may indeed
      require the same amount of ventilation, but not for the same
      purpose or under the same conditions. <br>
      <br>
      Flooded batteries release hydrogen gas as a normal part of every
      charge cycle. While it is unlikely that the hydrogen gas could
      accumulate to the 4% concentration to become combustible, given
      its natural dispersion, the hydrogen sulfide released with the
      hydrogen gas is an unpleasant irritant and is potentially toxic
      with prolonged exposure at high concentrations. Because of the
      normal gassing during the charge cycle, we always provide
      ventilation of these gases to the outside. With sealed batteries,
      the purpose and intent of ventilation is not to ensure ventilation
      during the normal charge cycle, but rather to ensure the safety of
      the dwelling and its occupants in the event of a catastrophic
      failure resulting in the "worst-case scenario" of unregulated
      overcharge. In actual experience, the charge regulator (from the
      PV array) and the inverter/charger (from a backup generator in an
      off grid home) are the bottlenecks through which all charge
      current must pass, and failures invariably occur in an "open
      circuit" mode, rather than in a "closed circuit without charge
      regulation" mode.<br>
      <br>
      Nevertheless, we must accommodate the most hazardous potential
      outcome, which would be <i>unregulated overcharge</i> of an <i>already


        full battery</i> during periods of <i>high insolation</i> (or
      the equivalent input from an engine generator). In order to
      determine the expected amount of hydrogen gassing under worst-case
      conditions, I contacted my Concorde distibutor<font face="Times
        New Roman, Times, serif">,<span style="font-size: 11pt; color:
          black;"> Marc Kurth of</span><span style="font-size: 11pt;
          color: black;"> Centex Batteries, LLC in</span><span
          style="font-size: 11pt; color: black;"></span><span
          style="font-size: 11pt; color: black;"> Bastrop, TX, </span><span
          style="font-size: 11pt; color: black;">512 308-9002. He in
          turn spoke with </span>th</font>e engineering department at
      Concorde Battery, the manufacturer of the batteries used in the
      [X] PV installation. Their analysis of calculated gassing and
      airflow rates is in the attached pdf document which they provided
      to us. The batteries in the [X] PV system are Concorde SunXtender
      PVX-9150T, rated 915 amp-hours at the C/24 rate. There are 12
      cells in a single series string of 24 Vnom.<br>
      <br>
      The storeroom in which the PV system is located has interior
      dimensions of 19' by 37' by an average of 10' tall, or
      approximately 7,000 cubic feet. It's a large open space. The room
      has four Pella double-hung windows, each rated by the manufacturer
      at 0.3 cfm fenestration, or 1.2 cfm for all four. Each exterior
      door (the third door to the interior living space is excluded as a
      conservative calculation but also adds to overall ventilation) is
      rated at 0.6 cfm, for a total of 1.2 cfm for the two doors and 2.4
      cfm for the building, assuming no other openings of any sort, such
      as for wires or for natural convective losses due to any other air
      leakage or roof ventilation. <br>
      <br>
      The 2,000 watt PV array will provide at most about 65 peak amperes
      of DC current into the batteries, for the equivalent of a
      cumulative daily total of around seven hours in summer. (The
      inverter/charger is capable of feeding 105 amperes into the
      batteries from a generator, but by the specific stated preference
      of the homeowners, the home does not have a backup generator and
      does not include the ability to accept generator AC input.)
      Assuming the worst case of 75 amperes flowing unregulated into
      this 900 ampere-hour battery, this C/12 charge rate is capable of
      raising the batteries to 30 V DC, or 2.50 volts per cell (vpc).
      The cell voltage will not rise about this level because the
      internal resistance of the battery, which increases as the voltage
      increases, prevents it. Note also that 75 amperes is a peak
      current that could only be maintained at midday during conditions
      of cold, dry air when the solar insolation intensity is well above
      standard test conditions (STC) of 1,000 watts/square meter, when
      the sun is perpendicular to the array. As the sun passes across
      the sky, the available output current drops substantially. At a
      reduced input current, the maximum vpc drops to around 2.40 vpc
      (and continues to drop thereafter) and the maximum temperature
      also drops, in which case gassing reduces by a factor of about 20
      below the rate at 2.50 vpc.<br>
      <br>
      As an additional factor in our calculations, note that all modern
      charge controllers are designed to receive PV input at a higher
      voltage and lower current than the nominal battery voltage,
      converting this to higher current at the lower actual battery
      voltage. The Midnite Classic charge controller in this application
      works this way. In a closed-circuit failure of the charge
      controller's functions, the higher array voltage and lower current
      would pass through to the batteries. As long as the input voltage
      is higher than the battery voltage, the batteries will accept
      current, but additional voltage does not increase the current into
      the batteries or the amount of hydrogen released. Rather, in this
      case the PV modules, which are wired as four strings of two
      modules each, will not exceed the rated short-circuit of the
      modules x 1.25 (per NEC for PV source circuits. With four strings,
      this is (8.61 x 4 x 1.25 =) 43.05 amperes. This is less than half
      of the maximum input current used to calculate worst-case input
      (as shown in the following paragraphs), and as such is unlikely to
      be sufficient to raise the cell voltage to even the level
      calculated.<br>
      <br>
      Per the attached engineering analysis by Concorde, assuming that
      at a sustained 2.50 vpc the temperature of the batteries rises to
      50ºC (122ºF), the amount of hydrogen released at a constant
      current at 30V DC, or 2.50 vpc, at 50ºC is 5.6 cc/hour/Ah/cell.
      This converts to (5.6 x 915 x 12 =) 61,488 cc of hydrogen released
      per hour. Converting cubic centimeters to the more useful cubic
      feet, 61,488/21,317 cc/cuft = 2.17 cubic feet per hour of gas
      released. This amount is less than the total fenestration of that
      room (not including the door to the living space) of 2.4 cubic
      feet per minute, or (2.4 x 60 =) 144 cubic feet per hour of
      natural leakage to the outside through closed windows and doors. <br>
      <br>
      To take this one step further, 2.17 cubic feet is 0.031% of the
      volume of the storeroom. It would take 30 times this concentration
      to exceed 1% by volume in an airtight container. 4.1%
      concentration is the threshold at which hydrogen gas becomes
      combustible.<br>
      <br>
      Also at 2.50 vpc, at 50ºC, the airflow required to keep hydrogen
      accumulation below 1% is 0.0093 liter/minute/Ah/cell, or [(0.0093
      x 915 x 12)/28.32 liters/cubic foot =] 3.6 cfm, or 216 cubic
      feet/hour. While this exceeds the default window and door
      fenestration of 144 cubic feet per hour, it is sufficient to
      disperse hydrogen. Note that these batteries are not in a confined
      space; the batteries are located in a space of 7,000 cubic feet.
      Note also that is the threshold for staying below 1% hydrogen
      concentration; 4.1% is the threshold at which hydrogen becomes
      explosive.<br>
      <br>
      I reviewed our records pertaining to the use of sealed batteries
      in residential off grid PV systems and in grid-tied PV systems
      with battery backup. We have installed more than thirty such
      systems, although the great majority have been installed since
      2005. Of those, I have identified at least nine permitted and
      inspected systems in which the batteries have been located in what
      may be considered enclosed spaces without ventilation between the
      interior space and the outside air. Indeed, several of these are
      in spaces much smaller that the Shutt storeroom. This is the first
      time in which an AHJ has expressed concern about adequate
      ventilation of sealed batteries.<br>
      <br>
      In two of these thirty-plus confined interior installations, the
      sealed batteries were installed in custom-made sealed enclosures
      which were wrapped in sheet plywood with controlled intake
      ventilation. In both of these we purposely installed Power Vent
      battery fans (as we install in all of our systems with flooded
      lead-acid batteries) ducted to the outside as a safety feature to
      prevent the possibility of accumulation of gases within the
      battery enclosure itself. However, in all of the remaining systems
      we have used manufactured steel battery enclosures Listed to
      UL508A. Ventilation from the cabinet into the room where it can
      dissipate has always been considered to be adequate in these
      applications.<br>
      <br>
      I believe that I have conclusively established that in a
      worst-case scenario, the batteries cannot release enough hydrogen
      to come even close to dangerous levels. In practical terms, if a
      failure were to occur when the residents were away, the batteries
      would be permanently damaged by a failed controller, but no danger
      exists to the home. If the residents are present when the failure
      occurs, they would in short order smell the "rotten egg" smell of
      hydrogen sulfide. Following their noses, they'd find a much
      stronger smell in the storeroom, suspect that the batteries were
      the source, turn off the circuit breakers on the system (which are
      readily accessible per NEC) and open the doors or windows. <br>
      <br>
      The 2011 NEC Hanbook states, as noted above: "If the space is
      confined, mechanical ventilation may be required in the vicinity
      of the battery." The storeroom at the [X] residence is simply not
      a "confined space" as built.<br>
      <br>
      Thank you for your consideration of this defense of our
      installation practices.<br>
      Allan Sindelar<br>
      <div class="moz-signature">-- <br>
        <meta http-equiv="Content-Type" content="text/html;
          charset=ISO-8859-1">
        <meta name="ProgId" content="Word.Document">
        <meta name="Generator" content="Microsoft Word 11">
        <meta name="Originator" content="Microsoft Word 11">
        <link rel="File-List" href="SignatureNew_files/filelist.xml">
        <o:smarttagtype
          namespaceuri="urn:schemas-microsoft-com:office:smarttags"
          name="address"> <o:smarttagtype
            namespaceuri="urn:schemas-microsoft-com:office:smarttags"
            name="PostalCode"> <o:smarttagtype
              namespaceuri="urn:schemas-microsoft-com:office:smarttags"
              name="State"> <o:smarttagtype
                namespaceuri="urn:schemas-microsoft-com:office:smarttags"
                name="City"> <o:smarttagtype
                  namespaceuri="urn:schemas-microsoft-com:office:smarttags"
                  name="Street">
                  <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:Template>Normal</o:Template>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>6</o:Revision>
  <o:TotalTime>2</o:TotalTime>
  <o:Created>2013-06-07T19:15:00Z</o:Created>
  <o:LastSaved>2013-09-23T20:34:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>69</o:Words>
  <o:Characters>394</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>3</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>462</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:UseFELayout/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]--><!--[if !mso]><object
 classid="clsid:38481807-CA0E-42D2-BF39-B33AF135CC4D" id=ieooui></object>
<style>
st1\:*{behavior:url(#ieooui) }
</style>
<![endif]-->
                  <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-alt:"\FF2D\FF33 \660E\671D";
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"MS Mincho";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.SpellE
        {mso-style-name:"";
        mso-spl-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="5122"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
                  <div class="Section1">
                    <p class="MsoNormal"><b>Allan <span class="SpellE">Sindelar</span></b><br>
                      <span style="font-size:10.0pt"><a
                          moz-do-not-send="true"
                          href="mailto:Allan@positiveenergysolar.com"><u><span
                              style="color:#000099">Allan@positiveenergysolar.com</span></u></a></span><br>
                      <span style="font-size:10.0pt">NABCEP Certified PV
                        Installation Professional<br>
                        NABCEP Certified Technical Sales Professional<br>
                        New Mexico EE98J Journeyman Electrician<br>
                        Founder, <b>Positive Energy, Inc.<o:p></o:p></b></span></p>
                    <p class="MsoNormal"><span style="font-size:10.0pt">A
                        Certified B <span class="SpellE">Corporation<sup><span
                              style="font-size:7.5pt">TM</span></sup></span><br>
                        <st1:address w:st="on"><st1:street w:st="on">3209

                            Richards Lane</st1:street><br>
                          <st1:city w:st="on">Santa Fe</st1:city>, <st1:state
                            w:st="on">New Mexico</st1:state> <st1:postalcode
                            w:st="on">87507</st1:postalcode></st1:address><br>
                        <b>505 424-1112 office 780-2738 cell</b><br>
                        <a moz-do-not-send="true"
                          href="http://www.positiveenergysolar.com/"
                          target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></p>
                    <p class="MsoNormal"><span style="font-size:10.0pt"><span
                          style="mso-spacerun:yes"> </span></span></p>
                  </div>
                </o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></div>
      <br>
    </div>
    <br>
  </body>
</html>