<div dir="ltr">Thanks for the correction on that sedona fire Bill; I had only seen the incorrect fire dept report.<div>I wish there was a clearinghouse for information on RE incidents and close calls as they are all teachable moments for both RE professionals and firefighters.</div>
<div><br></div><div>I ditto the need for more NEC guidance on battery banks. In my firefighting career, I've been at about a dozen structure fires involving RE equipment. Only 4 were actually caused by the RE equipment. *All* of those originated in or near the battery bank. 1 internal battery short circuit, 1 mouse chew inside battery box, and 2 bad connection when charging with a generator.</div>
<div><br></div><div>I'd like to get involved, Bill....I have lots to say about wooden battery boxes, parallel fusing, signage, and more. What are the first steps for getting involved?</div><div><br></div><div><div class="gmail_extra">
<br clear="all"><div>Dan Fink,<br>Executive Director;<br>Otherpower<br>Buckville Energy Consulting<br>Buckville Publications LLC<br>NABCEP / IREC accredited Continuing Education Providers<br>970.672.4342<br><br> </div>
<br><br><div class="gmail_quote">On Thu, Jan 23, 2014 at 12:23 PM, Bill Brooks <span dir="ltr"><<a href="mailto:billbrooks7@yahoo.com" target="_blank">billbrooks7@yahoo.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple"><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Jeffrey and Ray,<u></u><u></u></span></p><p class="MsoNormal">
<span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Batteries can off-gas hydrogen-sulfide gas when under heavy charge or overcharge. It is the nasty rotten egg smelling gas. Definitely not to be inhaled since when it hits your lungs it turns back into sulfuric acid.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">To address Ray’s point, the new 690.12 regulation that has been getting a lot of air time on this list does, in fact, address battery circuits for PV systems. Any circuit that is part of a PV system inside a building within 5’ must be controlled to 30V, 240VA within 10 seconds. This includes all the ac output conductors from a backup PV inverter and the battery inverter input circuit as well. This provision matches the new requirement for battery systems in 690.71(H) that requires “A disconnecting means and overcurrent protection shall be provided at the energy storage device end of the circuit. Fused disconnecting means or circuit breakers shall be permitted to be used.” Ideally we try to keep our battery conductors to 5’ or less and that means that no additional disconnecting means would be necessary according to the new 690.71(H). If we have to go longer than 5’ and the conductors are inside the building, a rapid shutdown capability would need to be on that circuit and it would need to have a disconnecting means and overcurrent protection. The best way to meet this requirement would probably be to have a shunt-trip breaker, similar to what Midnite Solar provides with their birdhouse setup.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">There are definitely much more discussion going on in the NEC about energy storage now than ever before. This next code cycle will be very busy on the subject. It is likely that article 480 will soon be turned into “Energy Storage” or a new article in Chapter 6 or 7 will cover “Energy Storage Systems.” It was proposed last cycle and failed, but this time there is much more interest in the subject. The solar industry needs to be involved, so it sounds like this is your year for both of you to get involved.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Bill.<u></u><u></u></span></p>
<p class="MsoNormal"><br></p></div></blockquote></div></div></div></div>