    <div class="moz-cite-prefix">My take on 250.110, is that you could
      run separate EGCs from either end to bond the metal J boxes, and
      not have the EGC run the entire length through the PVC.  <br>
      Option 2:  attach a Bobcat to one end of the PVC and rip it out of
      the ground, then use the freshly made trench to reinstall what the
      inspectors want to see (larger conduit with 2 conductors). Ugh....<br>
      <br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 11/20/2013 10:44 AM, August Goers wrote:<br>
    </div>
    <blockquote
      cite="mid:638eb5ee40402767c223b84539c36d2b@mail.gmail.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <title>National Electrical Code 2008 Edition</title>
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;}
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";
        color:black;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";}
span.EmailStyle19
        {mso-style-type:personal;
        font-family:"Arial","sans-serif";
        color:black;}
span.EmailStyle20
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:#44546A;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;
        color:black;}
span.EmailStyle23
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#44546A;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style>
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">Hi
            Allan,</span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">Per
            NEC 250.110 all equipment fastened in place with exposed
            non-current carrying metal parts likely to become energized
            needs equipment grounding. There are some conditions and
            exceptions listed in the code so you might want to check
            through that section and apply it to your situation. If you
            had used metallic conduit such as EMT then the raceway
            itself would count for equipment ground. However, since it
            sounds like you have non-metallic conduit you do indeed need
            a equipment ground wire sized per table 250.122. My general
            rule of thumb is that all metal boxes and raceways need
            equipment ground, period. We run equipment ground conductors
            even in EMT because there is a chance that fittings will
            loosen over time. </span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">Anyway,
            that’s my take.</span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">Best,</span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">August</span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
        <div>
          <div style="border:none;border-top:solid #b5c4df
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal">
              <b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
                <a moz-do-not-send="true"
                  href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
                [mailto:<a moz-do-not-send="true"
                  href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>]
                <b>On Behalf Of </b>Allan Sindelar<br>
                <b>Sent:</b> Tuesday, November 19, 2013 3:34 PM<br>
                <b>To:</b> RE-wrenches<br>
                <b>Subject:</b> Re: [RE-wrenches] A related question -
                Individual AC conductors through separate conduits</span></p>
          </div>
        </div>
        <p class="MsoNormal">
           </p>
        <div>
          <p class="MsoNormal" style="margin-bottom:12.0pt">Wrenches,<br>
            I need similar advice, please, especially a Code section
            citation.<br>
            <br>
            In 2005 we installed an Outback system for a new home in
            town that was designed and installed to be a grid-backup
            solar home. It was, in essence, a stand-alone system to run
            most of the home with the utility serving the backup
            generator's role, both to provide backup charging when
            needed and to run a few specific loads. The home was built
            with two breaker panels side by side, with the PV system
            wired between them. The meter pedestal was 150' away at the
            edge of the street. The array was small at 1.32 kW.<br>
            <br>
            Around 2007 the interconnection terms were quite good and we
            converted this system into a grid-intertied system. Doing
            this involved replacing the early Outback FX2024 with a
            GVFX3524. We also had to run an additional #4 conductor from
            the system (inverter AC interactive output) to the meter
            pedestal in order to carry interactive sell-back energy to a
            REC meter, which had to be located next to the revenue
            meter. We ran this single conductor in 1" PVC conduit with
            no other conductor. Given that all AC neutrals were properly
            bonded, that the conduit was non-conductive, and that all
            metal parts were properly bonded, we didn't run an EGC with
            this single THWN. We were permitted and and passed
            inspection.<br>
            <br>
            Now we are adding an additional 1.3 kW of PV to the system,
            which requires full permit process, of course. And in the
            ensuing years the home has been annexed into the city, with
            its reputation for toughness in regards to Code compliance.
            Our design team tells me that we must pull that #4 out and
            repull it with an EGC, simply because every current-carrying
            conductor must have a grounding conductor as well. <br>
            <br>
            My question: What Code section applies here? Is an EGC
            always required in conduit carrying a single
            current-carrying conductor? <br>
            <br>
            We're trying to have our ducks in a row before contacting
            the inspector, and have never dealt with this particular
            situation before.<br>
            Thank you,<br>
            Allan</p>
          <div>
            <p class="MsoNormal"><b>Allan Sindelar</b><br>
              <span style="font-size:10.0pt"><a moz-do-not-send="true"
                  href="mailto:Allan@positiveenergysolar.com"><span
                    style="color:#000099">Allan@positiveenergysolar.com</span></a></span><br>
              <span style="font-size:10.0pt">NABCEP Certified PV
                Installation Professional<br>
                NABCEP Certified Technical Sales Professional<br>
                New Mexico EE98J Journeyman Electrician<br>
                Founder, <b>Positive Energy, Inc.</b></span></p>
            <p class="MsoNormal">
              <span style="font-size:10.0pt">A Certified B Corporation</span><sup><span
                  style="font-size:7.5pt">TM</span></sup><span
                style="font-size:10.0pt"><br>
                3209 Richards Lane<br>
                Santa Fe, New Mexico 87507<br>
                <b>505 424-1112 office 780-2738 cell</b><br>
                <a moz-do-not-send="true"
                  href="http://www.positiveenergysolar.com/"
                  target="_blank">www.positiveenergysolar.com</a></span></p>
            <p class="MsoNormal"><span style="font-size:10.0pt"> </span></p>
          </div>
          <p class="MsoNormal">On 11/19/2013 11:22 AM, Dave Click wrote:</p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <p class="MsoNormal" style="margin-bottom:12.0pt"><b>300.3(B)
              Conductors of the Same Circuit.</b> All conductors of the
            same circuit and, where used, the grounded conductor and all
            equipment grounding conductors and bonding conductors shall
            be contained within the same raceway, auxiliary gutter,
            cable tray, cablebus assembly, trench, cable, or cord,
            unless otherwise permitted in accordance with 300.3(B)(1)
            through (B)(4) [which don't help here]. <br>
            <br>
          </p>
          <div>
            <p class="MsoNormal">On 2013/11/19, 12:38, August Goers
              wrote:</p>
          </div>
          <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">Hi
                All –</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">On
                a related note, I’ve become good friends with some of
                the inspectors in San Francisco and they called me
                yesterday with a question. Is it okay to run <u>individual</u>
                DC conductors through EMT for wire management purposes?
                We have always run paired positive and negative
                conductors in conduit so the question had never occurred
                to me. Obviously, you have to bond both ends of the
                conduit if it is over 250 v. I know that AC would have
                induction issues with running individual conductors but
                I’m not sure with DC.</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">Thanks,</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">August</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">August
                Goers</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">Principal</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">Luminalt
                Energy Corporation</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">o:
                415.641.4000</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a">m:
                415.559.1525</span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"><a
                  moz-do-not-send="true" href="http://www.luminalt.com">www.luminalt.com</a></span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#44546a"> </span></p>
            <div>
              <div style="border:none;border-top:solid #b5c4df
                1.0pt;padding:3.0pt 0in 0in 0in">
                <p class="MsoNormal">
                  <b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
                    <a moz-do-not-send="true"
                      href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
                    [mailto:<a moz-do-not-send="true"
                      href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>]
                    <b>On Behalf Of </b>William Miller<br>
                    <b>Sent:</b> Monday, November 18, 2013 11:33 PM<br>
                    <b>To:</b> 'RE-wrenches'<br>
                    <b>Subject:</b> Re: [RE-wrenches] PV Wiring methods</span></p>
              </div>
            </div>
            <p class="MsoNormal"> </p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif"">Bill:</span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif""> </span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif"">There
                is no need to stuff MC4 cables into standard conduit. 
                You can either slot the pipe using our easy method or
                install bulkhead type connectors.  The connectors are
                readily available.  I get them from PV Cables in
                Northern California..</span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif""> </span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif"">Wire
                routing problems and some solutions can be found on our
                web-site:</span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif""> </span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif""><a
                  moz-do-not-send="true"
href="http://millersolar.com/MillerSolar/practices/PV_wiring/_PV_Wiring2.html">http://millersolar.com/MillerSolar/practices/PV_wiring/_PV_Wiring2.html</a></span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif""> </span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif"">Since
                the industry won’t provide wire management solutions, we
                are making our own.  Questions:  Just write or call.</span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif""> </span></p>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif"">William
                Miller</span></p>
            <p class="MsoNormal">
              <span
                style="font-family:"Arial","sans-serif""> </span></p>
            <div>
              <div style="border:none;border-top:solid #b5c4df
                1.0pt;padding:3.0pt 0in 0in 0in">
                <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
                    <a moz-do-not-send="true"
                      href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
                    [<a moz-do-not-send="true"
                      href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
                    <b>On Behalf Of </b>frenergy<br>
                    <b>Sent:</b> Thursday, November 14, 2013 7:46 AM<br>
                    <b>To:</b> RE-wrenches<br>
                    <b>Subject:</b> Re: [RE-wrenches] PV Wiring methods</span></p>
              </div>
            </div>
            <p class="MsoNormal"> </p>
            <div>
              <p class="MsoNormal">William, Bill....from another Bill,</p>
            </div>
            <div>
              <p class="MsoNormal"> </p>
            </div>
            <div>
              <p class="MsoNormal">        Two things:  For the rest of
                us (maybe it's just me?!) that's still trying to figure
                out how (or why) to stuff a MC4 connector into conduit
                and my hesitation in using SS wire ties for fear of the
                sharp edges cutting or chaffing into cables, I'm open
                for advice. Any wire I use on the roof is rated for that
                type of service and I have some off-grid systems that
                have been in the sun for some 25 years where the wire
                still looks nearly new even when flexing it to look for
                checking/cracks.  It seems the wire/insulation can take
                it, thus it seems like the key to "wire management is to
                keep the wire from moving and off the roof, secured to
                the racking, thus not compromising the insulation. </p>
            </div>
            <div>
              <p class="MsoNormal"> </p>
            </div>
            <p class="MsoNormal"><br>
              <br>
              <br>
            </p>
            <pre>_______________________________________________</pre>
            <pre>List sponsored by Home Power magazine</pre>
            <pre> </pre>
            <pre>List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></pre>
            <pre> </pre>
            <pre>Change email address & settings:</pre>
            <pre><a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></pre>
            <pre> </pre>
            <pre>List-Archive: <a moz-do-not-send="true" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></pre>
            <pre> </pre>
            <pre>List rules & etiquette:</pre>
            <pre><a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></pre>
            <pre> </pre>
            <pre>Check out participant bios:</pre>
            <pre><a moz-do-not-send="true" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></pre>
            <pre> </pre>
          </blockquote>
          <p class="MsoNormal"><br>
            <br>
            <br>
            <br>
          </p>
          <pre>_______________________________________________</pre>
          <pre>List sponsored by Home Power magazine</pre>
          <pre> </pre>
          <pre>List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></pre>
          <pre> </pre>
          <pre>Change email address & settings:</pre>
          <pre><a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></pre>
          <pre> </pre>
          <pre>List-Archive: <a moz-do-not-send="true" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></pre>
          <pre> </pre>
          <pre>List rules & etiquette:</pre>
          <pre><a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></pre>
          <pre> </pre>
          <pre>Check out participant bios:</pre>
          <pre><a moz-do-not-send="true" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></pre>
          <pre> </pre>
        </blockquote>
        <p class="MsoNormal"> </p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>