<html><body><span style="font-family:Verdana; color:#000000; font-size:10pt;"><div>I'm with Ray.. 10 yrs in service.. showing multiple signs of failure.. the writings on the wall.. You're kicking  on a lame horse dude.. SW always did seem to sparkle when the relays twitched. I wouldn't get nervous till I started seeing errors.<br></div><div><br></div><div>db<br></div><div><br>Dan Brown<br>Foxfire Energy Corp.<br>Renewable Energy Systems<br>(802)-483-2564<br><a href="http://www.Foxfire-Energy.com">www.Foxfire-Energy.com</a><br>NABCEP #092907-44</div><div><br><br></div>
<blockquote id="replyBlockquote" webmail="1" style="border-left: 2px solid blue; margin-left: 8px; padding-left: 8px; font-size:10pt; color:black; font-family:verdana;">
<div id="wmQuoteWrapper">
-------- Original Message --------<br>
Subject: Re: [RE-wrenches] SW4024 relay spark issue<br>
From: Ray Walters <<a href="mailto:ray@solarray.com">ray@solarray.com</a>><br>
Date: Mon, November 18, 2013 8:59 pm<br>
To: <a href="mailto:Allan@positiveenergysolar.com">Allan@positiveenergysolar.com</a>,  RE-wrenches<br>
<<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
<br>
     <div class="moz-cite-prefix">I've not had good luck on Surrette 5000s actually.  We had a set that was really problematic early on with battery voltage temporarily dropping below the inverter lo volt shut off, when a well pump was started.  They have amp hours rated at the 100 hr rate, and they seem to behave as expected when the discharge rates are kept to the hundred hour rate. (19 amps from a 1900ah @ 100 hr rate)<br> For the problem set, I added another 6 v, and actually created a 54 v nominal battery bank.  That solved the problem for about 5 years, but then the lo volt problem crept back up, and they replaced the whole set at about 6 years as I recall.  This was seriously embarrassing for us, as it was an expensive battery bank that I had touted as being able to go 15 years under normal conditions.<br> They're rated to 1500 cycles at 80% DOD, but again, I only think that's true at lower discharge rates.  I just never could figure out the Surrette 5000s, and heard enough other folks having trouble, that we moved away from them.  At 10 years, I'd say all bets are off that it's a good bank.  I just had an aging set of L16s with remarkably even cell voltages, that seemed to perform well under load testing, totally crash, less than 6 months later.<br> <divre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre> On 11/18/2013 6:31 PM, Allan Sindelar wrote:<br> </div> <blockquote cite="mid:528ABF6A.2080204@positiveenergysolar.com" type="cite">  <div class="moz-cite-prefix">Ray,<br> Yes, I know...<br> <br> Doesn't ten years seem a bit weak on a set of Surrette's best? And the other ten cells are remarkably even. If replacement (which is already being arranged by Surrette in a good way) gives 3-5 more years, even with keeping a close eye on cell variations, we have accomplished a reasonable objective.<br> <br> Re a loose connection: this is why I posted the questions: to look for other possible explanations. Did you see Nick's response: "I used to see that arc flash all the time from the SW series relays, even on new SW Series inverters.  That always happened when the contact switched under load." I'd consider this before pulling the cover off to look for the source of the flash.<br> <br> Re the single-string issue, Steve Higgins replied very promptly (as did James Surrette, to whom I had written before posting here), saying "<br> <p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">What you can do to save some fuel is pull the two cells out and reduce charge voltage per cell… this means if your absorbing at 28.8, then you adjust the voltage down 2.4vpc to 24vdc… <o:p></o:p></span></div> <span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">If you do this you may also want to adjust the LBCO as low as possible.   If you leave the dead cells in it’s just going to consume more fuel to keep charged."</span><br> <br> But we agreed that the new cells would be in place soon enough to not justify this course of action. I have done the one-string-from-two temporary solution many times over the years.<br> <br> Thank you,<br> Allan<br> <br> <div class="moz-signature">      <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="address"> <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="PostalCode"> <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="State"> <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="City"> <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="Street"> <!--[if !mso]> <style>
 #wmQuoteWrapper st1\:* {behavior:url(#ieooui) }

</style> <![endif]--> <style>
 #wmQuoteWrapper /* Font Definitions */ @font-face  {font-family:"MS Mincho"; panose-1:2 2 6 9 4 2 5 8 3 4; mso-font-alt:"\FF2D\FF33 \660E\671D"; mso-font-charset:128; mso-generic-font-family:modern; mso-font-pitch:fixed; mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 #wmQuoteWrapper @font-face  {font-family:"\@MS Mincho"; panose-1:2 2 6 9 4 2 5 8 3 4; mso-font-charset:128; mso-generic-font-family:modern; mso-font-pitch:fixed; mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 #wmQuoteWrapper /* Style Definitions */ p.MsoNormal, #wmQuoteWrapper li.MsoNormal, #wmQuoteWrapper div.MsoNormal  {mso-style-parent:""; margin:0in; margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:12.0pt; font-family:"Times New Roman"; mso-fareast-font-family:"MS Mincho"; color:black;}
 #wmQuoteWrapper a:link, #wmQuoteWrapper span.MsoHyperlink  {color:blue;}
 #wmQuoteWrapper a:visited, #wmQuoteWrapper span.MsoHyperlinkFollowed  {color:blue;}
 #wmQuoteWrapper span.SpellE  {mso-style-name:""; mso-spl-e:yes;}
 #wmQuoteWrapper @page Section1  {size:8.5in 11.0in; margin:1.0in 1.25in 1.0in 1.25in; mso-header-margin:.5in; mso-footer-margin:.5in; mso-paper-source:0;}
 #wmQuoteWrapper div.Section1  {page:Section1;}

</style><!--[if gte mso 10]> <style>
 #wmQuoteWrapper /* Style Definitions */ table.MsoNormalTable  {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-fareast-font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;}

</style> <![endif]--> <div class="Section1"> <div class="MsoNormal" style="font-size:12pt;"><b>Allan <span class="SpellE">Sindelar</span></b><br> <span style="font-size:10.0pt"><a target="_blank" moz-do-not-send="true" href="mailto:Allan@positiveenergysolar.com"><u><span style="color:#000099">Allan@positiveenergysolar.com</span></u></a></span><br> <span style="font-size:10.0pt">NABCEP Certified PV Installation Professional<br> NABCEP Certified Technical Sales Professional<br> New Mexico EE98J Journeyman Electrician<br> Founder, <b>Positive Energy, Inc.<o:p></o:p></b></span></div> <div class="MsoNormal" style="font-size:12pt;"><span style="font-size:10.0pt">A Certified B <span class="SpellE">Corporation<sup><span style="font-size:7.5pt">TM</span></sup></span><br> <st1:address w:st="on"><st1:street w:st="on">3209 Richards Lane</st1:street><br> <st1:city w:st="on">Santa Fe</st1:city>, <st1:state w:st="on">New Mexico</st1:state> <st1:postalcode w:st="on">87507</st1:postalcode></st1:address><br> <b>505 424-1112 office 780-2738 cell</b><br> <a moz-do-not-send="true" href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></div> <div class="MsoNormal" style="font-size:12pt;"><span style="font-size:10.0pt"><span style="mso-spacerun:yes"> </span></span></div> </div> </o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></div> On 11/18/2013 6:13 PM, Ray Walters wrote:<br> </div> <blockquote cite="mid:528ABB3E.20108@solarray.com" type="cite">  <div class="moz-cite-prefix">I thought the relays on the SWs were sealed, so visible arcing sounds bad.  Are you sure its not a loose connection?<br> Also on the batteries, anytime I've ever seen someone replace just a couple of cells in a bank that old, it never ended well.  It was like that gopher stomping game, and you hit one problem, and then another pops up right after.....<br> We need some kind of financing program for battery replacements, so that people can get what they really need: a whole new set.<br> That very situation, is why I quit doing as many single series strings: one or two cells fail, and the whole system goes.  <br> In this same situation with 2 strings, you create a single string of your strongest cells to limp the customer along, until they can afford to replace the set. As cells go down, you keep pulling in replacements from the retired string. This would be a great time to take a few of the best used cells from another aging set  on another system that is getting replaced.<br> <divre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre> On 11/18/2013 5:01 PM, Allan Sindelar wrote:<br> </div> <blockquote cite="mid:528AAA57.5090206@positiveenergysolar.com" type="cite">  Wrenches,<br> A longtime off grid customer with a 1997-era Trace SW4024 and a Kohler 8.5RMY backup generator (with 1,800 hours over 16 years) has never had an inverter failure, but requested my assistance with a recent development. His generator has been set up on automatic operation using standard Trace voltage, quiet time and load-start program parameters. When it was called to run, it would charge to 29.6 V with a one-hour absorption, then shut off. This has worked well until recently. The automatic operation includes a cool-down and the modest absorption means that the AC input current at shutdown is going to be pretty low.<br> <br> Recently he called me because his generator was starting more frequently and running for longer duration. Of course, I immediately suspected the batteries, which are ten-year old 5000 series Surrette 4KS-25PS cells. Upon checking I found two weak cells, which would explain the inability of the batteries to reach full voltage and shut off after absorption. I will be replacing these two cells, which fortunately are both within the same red polypropylene case, as our only option, as the homeowner's budget won't allow replacement of the whole set. As a single string, the two new cells should play reasonably well with the old cells for a few more years.<br> <br> Because of this, the homeowner had recently shut off the generator at night using the buttons on the inverter, and when he did this he saw a spark flash from inside the inverter on the AC end. I was able to duplicate the flash, which I assume to be the AC2 input relay. The AC2 In setpoint is set to maximum 35A AC. Until the failed cells are replaced, I have advised the homeowner to manually control the generator at the generator, using its AC output breaker to disconnect the current to the inverter before the 108V AC default input voltage threshold causes the inverter AC input relay to unlatch under load. While the SW latches while unloaded and then ramps up input current, I don't believe that it can reduce input current to zero before unlatching when shutting down. <br> <br> My guess is that after 15 years of flawless performance, the relay contacts have pitted enough to cause arcing at disconnect, and if not addressed, the relay on the AC board will eventually fail. As AC relay boards these days are likely made out of unobtanium, I'd rather avoid this failure.<br> <br> So my questions, please: <br> 1. Have I likely correctly identified the AC input relay as the most likely cause of the visible arcing when the generator is turned off at the inverter?<br> 2. Should manual control be a permanent solution?<br> 3. Any other suggestions for this customer?<br> <br> Thank you,<br> Allan<br> <div class="moz-signature">-- <br>      <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="address"> <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="PostalCode"> <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="State"> <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="City"> <o:smarttagtype namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="Street"> <!--[if !mso]> <style>
 #wmQuoteWrapper st1\:* {behavior:url(#ieooui) }

</style> <![endif]--> <style>
 #wmQuoteWrapper /* Font Definitions */ @font-face  {font-family:"MS Mincho"; panose-1:2 2 6 9 4 2 5 8 3 4; mso-font-alt:"\FF2D\FF33 \660E\671D"; mso-font-charset:128; mso-generic-font-family:modern; mso-font-pitch:fixed; mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 #wmQuoteWrapper @font-face  {font-family:"\@MS Mincho"; panose-1:2 2 6 9 4 2 5 8 3 4; mso-font-charset:128; mso-generic-font-family:modern; mso-font-pitch:fixed; mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 #wmQuoteWrapper /* Style Definitions */ p.MsoNormal, #wmQuoteWrapper li.MsoNormal, #wmQuoteWrapper div.MsoNormal  {mso-style-parent:""; margin:0in; margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:12.0pt; font-family:"Times New Roman"; mso-fareast-font-family:"MS Mincho"; color:black;}
 #wmQuoteWrapper a:link, #wmQuoteWrapper span.MsoHyperlink  {color:blue;}
 #wmQuoteWrapper a:visited, #wmQuoteWrapper span.MsoHyperlinkFollowed  {color:blue;}
 #wmQuoteWrapper span.SpellE  {mso-style-name:""; mso-spl-e:yes;}
 #wmQuoteWrapper @page Section1  {size:8.5in 11.0in; margin:1.0in 1.25in 1.0in 1.25in; mso-header-margin:.5in; mso-footer-margin:.5in; mso-paper-source:0;}
 #wmQuoteWrapper div.Section1  {page:Section1;}

</style><!--[if gte mso 10]> <style>
 #wmQuoteWrapper /* Style Definitions */ table.MsoNormalTable  {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-fareast-font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;}

</style> <![endif]--> <div class="Section1"> <p class="MsoNormal"><b>Allan <span class="SpellE">Sindelar</span></b><br> <span style="font-size:10.0pt"><a target="_blank" moz-do-not-send="true" href="mailto:Allan@positiveenergysolar.com"><u><span style="color:#000099">Allan@positiveenergysolar.com</span></u></a></span><br> <span style="font-size:10.0pt">NABCEP Certified PV Installation Professional<br> NABCEP Certified Technical Sales Professional<br> New Mexico EE98J Journeyman Electrician<br> Founder, <b>Positive Energy, Inc.<o:p></o:p></b></span></div> <div class="MsoNormal" style="font-size:12pt;"><span style="font-size:10.0pt">A Certified B <span class="SpellE">Corporation<sup><span style="font-size:7.5pt">TM</span></sup></span><br> <st1:address w:st="on"><st1:street w:st="on">3209 Richards Lane</st1:street><br> <st1:city w:st="on">Santa Fe</st1:city>, <st1:state w:st="on">New Mexico</st1:state> <st1:postalcode w:st="on">87507</st1:postalcode></st1:address><br> <b>505 424-1112 office 780-2738 cell</b><br> <a moz-do-not-send="true" href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></div> <div class="MsoNormal" style="font-size:12pt;"><span style="font-size:10.0pt"><span style="mso-spacerun:yes"> </span></span></div> </div> </o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></div> <br> <fieldset class="mimeAttachmentHeader"></fieldset> <br> <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a target="_blank" moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a target="_blank" moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a target="_blank" moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre> </blockquote> <br> </blockquote> <br> </blockquote> <br>   <hr>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
<br>

</div>
</blockquote></span></body></html>