<DIV><FONT size=2 face=Arial>Hey Wrenches & Nick Soleil (with whom 
I worked at APS for a time I believe...),</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>I'm not familiar with Enphase commercial 
applications and am currently working through a commercial design. Enphase, on 
their M215 datasheets claim up to 25 micros per branch, at 1.0A each, with 
each branch terminating at a 20A breaker. By my calculations, 25 micros at 1.0A 
each (25A*1.25=31.25A) need to terminate at a 40A breaker. Anyone know what I'm 
missing or know how the 20A breaker design gets past the 
AHJ?</FONT></DIV>