<p dir="ltr">Generac also makes a 20kw.</p>
<p dir="ltr">Chris Mason<br>
Comet Systems<br>
Anguilla (264) 235-5670<br>
St. Kitts  (869) 662-5670<br>
skype netconcepts</p>
<p dir="ltr">NABCEP Certified Solar PV Installer™<br>
Renewable Energy Systems professional<br>
Generac Generators Factory technician</p>
<div class="gmail_quote">On Oct 1, 2013 11:16 AM, "Ray Walters" <<a href="mailto:ray@solarray.com">ray@solarray.com</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Sounds like they need a 20 Kw Kohler. Hot Tub in the future?  They'll love their Kohler.  The Generac is just way too small to even consider IMHO.<br>
<br>
R.Ray Walters<br>
CTO, Solarray, Inc<br>
Nabcep Certified PV Installer,<br>
Licensed Master Electrician<br>
Solar Design Engineer<br>
<a href="tel:303%20505-8760" value="+13035058760" target="_blank">303 505-8760</a><br>
<br>
On 10/1/2013 8:11 AM, Larry Crutcher, Starlight Solar Power Systems wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
William, Chris, Ray, Allan, et al.<br>
<br>
Gen support would be ideal but this inverter setup will be a quad pack of Magnum 4024PAE (120/240 split; 16kW). Their New MSH inverter is single phase only and can not be stacked.<br>
<br>
While disabling load(s) is the antithesis of the desired outcome, I'll review this possibility further.<br>
<br>
Using a separate charger could work but it would need to be about 200A @ 32V which would add quite a bit of cost and be hard to sell since the Magnum inverters already have 4 high quality charges included.<br>
<br>
A larger generator might be necessary if the customer won't agree to load shedding. Their plans are to expand the loads over time, operate a business, install a hot tube and more. Of course I have pushed the concept that conservation is paramount. The PV array and inverters are being oversized now for the future growth.<br>

<br>
My ideal solution...Since Magnum inverters monitor the AC input and control it based on quality of power, it seems to me that there could be a setting for disconnecting the AC input if loads exceed a setpoint. Change in control software would be great.<br>

<br>
<br>
Thank you,<br>
Larry<br>
<br>
<br>
<br>
On Sep 30, 2013, at 4:14 PM, William Miller <<a href="mailto:william@millersolar.com" target="_blank">william@millersolar.com</a>> wrote:<br>
<br>
Larry:<br>
<br>
Maybe a better approach might be to use an inverter with "Gen-support."<br>
That is unless a system already exists that does not have this feature.<br>
<br>
Plan B:  use the gen start signal to disable one or more of the larger<br>
loads.<br>
<br>
I know this is not what you asked for, just trying inject some different<br>
ideas.<br>
<br>
William<br>
-----Original Message-----<br>
From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-<u></u>wrenches.org</a><br>
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@<u></u>lists.re-wrenches.org</a>] On Behalf Of Larry<br>
Crutcher, Starlight Solar Power Systems<br>
Sent: Monday, September 30, 2013 1:02 PM<br>
To: RE-wrenches<br>
Subject: [RE-wrenches] Generator automatic disconnect<br>
<br>
Wrenches,<br>
<br>
I want to use the Ecogen 6kW generator on a large off grid system. The<br>
location has very few overcast or rainy days and the generator will rarely<br>
be needed. My concerns is nuisance tripping the generator output breakers if<br>
the household load exceeds 6kW. The power system control has a feature for<br>
reducing the AC current used to charge the batteries but does not have a<br>
feature for disconnecting the AC input based on input load.<br>
<br>
Does anyone have a solution for monitoring AC load from the generator and<br>
disconnect it if overloaded? It must automatically reconnect after a short<br>
timeout.<br>
<br>
Thank you,<br>
Larry Crutcher<br>
______________________________<u></u>_________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<u></u>org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>pipermail/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br>
</blockquote>
<br>
______________________________<u></u>_________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<u></u>org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>options.cgi/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/<u></u>pipermail/re-wrenches-re-<u></u>wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<u></u>htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>