    <div class="moz-cite-prefix">Larry, one other consideration:<br>
      My own Ecogen appears to be able to produce well over its rating.
      I have never had an amp-clamp with me when I have observed this,
      but it appears to be quite able to do so. My Magnum 4024 will
      charge at 114A (as measured on a TriMetric 2025) at 28V DC, or
      3,200 watts after efficiency losses, while at the same time
      passing through both microwave and toaster, which are both being
      run directly off of the gennie as pass-through loads, as the TM's
      amps in doesn't diminish significantly. Note that this is at
      6,700' elevation, which would suggest about a 23% derating, or
      about 4,600 watts available. I'm sorry to not be more precise - I
      really should test it.<br>
      <br>
      But the point is that you may have more headroom than you think.
      My output breaker is 50A 1P, so I assume the 240V option would be
      25A 2P. You might consider increasing this to 30A if your concern
      is nuisance tripping. Also, the QO breakers have a trip curve to
      allow minor surges.<br>
      Allan<br>
      <br>
      <div class="moz-signature">
        <meta http-equiv="Content-Type" content="text/html;
          charset=ISO-8859-1">
        <meta name="ProgId" content="Word.Document">
        <meta name="Generator" content="Microsoft Word 11">
        <meta name="Originator" content="Microsoft Word 11">
        <link rel="File-List" href="SignatureNew_files/filelist.xml">
        <o:smarttagtype
          namespaceuri="urn:schemas-microsoft-com:office:smarttags"
          name="address">
          <o:smarttagtype
            namespaceuri="urn:schemas-microsoft-com:office:smarttags"
            name="PostalCode">
            <o:smarttagtype
              namespaceuri="urn:schemas-microsoft-com:office:smarttags"
              name="State">
              <o:smarttagtype
                namespaceuri="urn:schemas-microsoft-com:office:smarttags"
                name="City">
                <o:smarttagtype
                  namespaceuri="urn:schemas-microsoft-com:office:smarttags"
                  name="Street">
                  <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:Template>Normal</o:Template>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>6</o:Revision>
  <o:TotalTime>2</o:TotalTime>
  <o:Created>2013-06-07T19:15:00Z</o:Created>
  <o:LastSaved>2013-09-23T20:34:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>69</o:Words>
  <o:Characters>394</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>3</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>462</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:UseFELayout/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]--><!--[if !mso]><object
 classid="clsid:38481807-CA0E-42D2-BF39-B33AF135CC4D" id=ieooui></object>
<style>
st1\:*{behavior:url(#ieooui) }
</style>
<![endif]-->
                  <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-alt:"\FF2D\FF33 \660E\671D";
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"MS Mincho";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.SpellE
        {mso-style-name:"";
        mso-spl-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="5122"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
                  <div class="Section1">
                    <p class="MsoNormal"><b>Allan <span class="SpellE">Sindelar</span></b><br>
                      <span style="font-size:10.0pt"><a
                          href="mailto:Allan@positiveenergysolar.com"><u><span
                              style="color:#000099">Allan@positiveenergysolar.com</span></u></a></span><br>
                      <span style="font-size:10.0pt">NABCEP Certified PV
                        Installation Professional<br>
                        NABCEP Certified Technical Sales Professional<br>
                        New Mexico EE98J Journeyman Electrician<br>
                        Founder, <b>Positive Energy, Inc.<o:p></o:p></b></span></p>
                    <p class="MsoNormal"><span style="font-size:10.0pt">A
                        Certified B <span class="SpellE">Corporation<sup><span
                              style="font-size:7.5pt">TM</span></sup></span><br>
                        <st1:address w:st="on"><st1:street w:st="on">3209
                            Richards Lane</st1:street><br>
                          <st1:city w:st="on">Santa Fe</st1:city>, <st1:state
                            w:st="on">New Mexico</st1:state> <st1:postalcode
                            w:st="on">87507</st1:postalcode></st1:address><br>
                        <b>505 424-1112 office 780-2738 cell</b><br>
                        <a href="http://www.positiveenergysolar.com/"
                          target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></p>
                    <p class="MsoNormal"><span style="font-size:10.0pt"><span
                          style="mso-spacerun:yes"> </span></span></p>
                  </div>
                </o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></div>
      On 9/30/2013 5:38 PM, Ray Walters wrote:<br>
    </div>
    <blockquote cite="mid:524A0B74.8060806@solarray.com" type="cite">3rd
      option would be to have a separate charger (IOTA) that just runs
      from the generator.   No pass through loads to the generator.
      <br>
      4th option would be to use a larger Kohler for backup.  My
      experience is that even if they don't think they'll need it, they
      eventually will actually use it.  Large off grid systems tend to
      creep ever larger.
      <br>
      <br>
      I'd look at all the scenarios with pricing, and pros and cons.
      You'll see what makes sense.
      <br>
      <br>
      R.Ray Walters
      <br>
      CTO, Solarray, Inc
      <br>
      Nabcep Certified PV Installer,
      <br>
      Licensed Master Electrician
      <br>
      Solar Design Engineer
      <br>
      303 505-8760
      <br>
      <br>
      On 9/30/2013 5:14 PM, William Miller wrote:
      <br>
      <blockquote type="cite">Larry:
        <br>
        <br>
        Maybe a better approach might be to use an inverter with
        "Gen-support."
        <br>
        That is unless a system already exists that does not have this
        feature.
        <br>
        <br>
        Plan B:  use the gen start signal to disable one or more of the
        larger
        <br>
        loads.
        <br>
        <br>
        I know this is not what you asked for, just trying inject some
        different
        <br>
        ideas.
        <br>
        <br>
        William
        <br>
        -----Original Message-----
        <br>
        From: <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
        <br>
        [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of
        Larry
        <br>
        Crutcher, Starlight Solar Power Systems
        <br>
        Sent: Monday, September 30, 2013 1:02 PM
        <br>
        To: RE-wrenches
        <br>
        Subject: [RE-wrenches] Generator automatic disconnect
        <br>
        <br>
        Wrenches,
        <br>
        <br>
        I want to use the Ecogen 6kW generator on a large off grid
        system. The
        <br>
        location has very few overcast or rainy days and the generator
        will rarely
        <br>
        be needed. My concerns is nuisance tripping the generator output
        breakers if
        <br>
        the household load exceeds 6kW. The power system control has a
        feature for
        <br>
        reducing the AC current used to charge the batteries but does
        not have a
        <br>
        feature for disconnecting the AC input based on input load.
        <br>
        <br>
        Does anyone have a solution for monitoring AC load from the
        generator and
        <br>
        disconnect it if overloaded? It must automatically reconnect
        after a short
        <br>
        timeout.
        <br>
        <br>
        Thank you,
        <br>
        Larry Crutcher
        <br>
        _____________
        <br>
        <br>
        _______________________________________________
        <br>
        List sponsored by Home Power magazine
        <br>
        <br>
        List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
        <br>
        <br>
        Change email address & settings:
        <br>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
        <br>
        <br>
        List-Archive:
        <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
        <br>
        <br>
        List rules & etiquette:
        <br>
        <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
        <br>
        <br>
        Check out participant bios:
        <br>
        <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
        <br>
        <br>
        <br>
      </blockquote>
      <br>
      _______________________________________________
      <br>
      List sponsored by Home Power magazine
      <br>
      <br>
      List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
      <br>
      <br>
      Change email address & settings:
      <br>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
      <br>
      <br>
      List-Archive:
      <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
      <br>
      <br>
      List rules & etiquette:
      <br>
      <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
      <br>
      <br>
      Check out participant bios:
      <br>
      <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
      <br>
      <br>
      <br>
    </blockquote>
    <br>
  </body>
</html>