<div class="moz-cite-prefix">200.6 allows 3 continuous white
stripes to identify the grounded conductor on wires smaller than
#6, so All cable's marking would qualify, we just can't field tape
it. (which makes sense: if the white tape falls off, and you're
left with 2 black wires, you're in for trouble...) <br>
Second, we are allowed to tape wires all we want for our own
purposes (like DC polarity, or circuit ID) I love my 3M and Brady
wire label makers. I could even put a label on a white wire that
said: "DC negative, grounded conductor"<br>
We just can't use tape all by itself to identify the grounded
conductor.<br>
<br>
<pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
On 9/24/2013 6:05 PM, Chris Mason wrote:<br>
</div>
<blockquote
cite="mid:CAG6C1q=4Xv1RbNF9NG6FU2wJZzQMZzJ0yHFD0=wacVuyCfWa+Q@mail.gmail.com"
type="cite">
<div dir="ltr">Just brought it up with AEESolar and they can
supply red and black PV Wire.
<div>In reference to marking the conductor polarity with tape,
wouldn't that fall foul of the NEC rule that only allows wire
colouring on conductors larger than #6?</div>
</div>
<div class="gmail_extra"><br>
<br>
<div class="gmail_quote">On Tue, Sep 24, 2013 at 2:17 AM, Ray
Walters <span dir="ltr"><<a moz-do-not-send="true"
href="mailto:ray@solarray.com" target="_blank">ray@solarray.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0
.8ex;border-left:1px #ccc solid;padding-left:1ex">
<div text="#000000" bgcolor="#FFFFFF">
<div>All Cable and probably other companies can add
striping and marking to any wire you need.
<div class="im"><br>
<pre cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
<a moz-do-not-send="true" href="tel:303%20505-8760" value="+13035058760" target="_blank">303 505-8760</a></pre>
</div>
<div>
<div class="h5"> On 9/23/2013 10:57 PM, <a
moz-do-not-send="true"
href="mailto:don@energysolarnow.com"
target="_blank">don@energysolarnow.com</a> wrote:<br>
</div>
</div>
</div>
<blockquote type="cite">
<div>
<div class="h5"><span
style="font-size:10pt;font-family:Verdana">
<div>Marco- You should not transition to THHN wire
at all for the DC run. The PV wire is double
insulated for a good reason- the transformerless
inverters are such suckers for a ground fault
that they need the extra protection. That's why
the NEC specifies PV wire. </div>
<div>I recently did an installation like you
wrote, with a transition at the j-box. This
developed an intermittent ground fault when wet,
and when the P1 inverter failed it was deemed
out of warranty. Learn from my mistake-- use PV
wire all the way to the inverter. </div>
<div><br>
</div>
<div>That said, does anyone know where to get 1000
volt PV wire in colors other than red, black,
and white?</div>
<div>It would be nice to color code the positive
runs like is possible with colors of THHN.</div>
<div>I'm thinking of buying spools of white and
spraying plastic paint on them for a striped
color coding.<br>
</div>
<div><br>
</div>
<div>Don Barch</div>
<div>Energy Solar</div>
<div><br>
</div>
<div><br>
</div>
<blockquote
style="padding-left:8px;font-size:10pt;margin-left:8px;font-family:verdana;border-left:2px
solid blue">
<div> Message: 3<br>
Date: Mon, 23 Sep 2013 09:27:30 -1000<br>
From: "Marco Mangelsdorf" <<a
moz-do-not-send="true"
href="mailto:marco@pvthawaii.com"
target="_blank">marco@pvthawaii.com</a>><br>
To: "'RE-wrenches'" <<a
moz-do-not-send="true"
href="mailto:re-wrenches@lists.re-wrenches.org"
target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
Subject: [RE-wrenches] transformerless
inverters and conductor colors<br>
Message-ID:
<000001ceb892$f3e41470$dbac3d50$@com><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Hi all,<br>
<br>
We're doing more and more installs with TL
inverters (SMA and P1).<br>
<br>
I'm using double-insulated wire from the array
string to the first<br>
enclosure, as in j-box, and then transitioning
to standard THHN/THWN wire.<br>
<br>
--------------------------------------------<br>
</div>
</blockquote>
</span> <br>
<fieldset></fieldset>
<br>
</div>
</div>
<div class="im">
<pre>_______________________________________________
List sponsored by Home Power magazine
List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a moz-do-not-send="true" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a moz-do-not-send="true" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>
</pre>
</div>
</blockquote>
<br>
</div>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a moz-do-not-send="true"
href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a moz-do-not-send="true"
href="http://www.re-wrenches.org/etiquette.htm"
target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a moz-do-not-send="true"
href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br>
</blockquote>
</div>
<br>
<br clear="all">
<div><br>
</div>
-- <br>
Chris Mason
<div>President, Comet Systems Ltd</div>
<div><a moz-do-not-send="true"
href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div>
<div>
Cell: 264.235.5670</div>
<div>Skype: netconcepts</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
</body>
</html>