    <div class="moz-cite-prefix">Drake:<br>
      <br>
      Generac released a Service Bulletin # <u>SIB13-09-EcoGen</u> in
      July about this issue.<br>
      <br>
      Regards,<br>
      <br>
      Gary Willett<br>
      Icarus Solar<br>
      <br>
      <br>
      On 9/24/13 9:34 AM, Drake wrote:<br>
    </div>
    <blockquote
      cite="mid:20130924143422.DF7B32E805C@homiemail-a51.g.dreamhost.com"
      type="cite">
      Wrenches,<br>
      <br>
      An unknown quantity of Generac EcoGens went out of the factory
      with
      incorrectly connected oil lines. We are working with Generac now,
      concerning a new unit that destroyed itself on its first run.<br>
      <br>
      After we hooked the machine up and left, the customer manually
      started
      the machine the following day. We were not able to do the startup
      because
      we did not have <u>all the information</u> needed for Generac to
      provide
      us with the access code needed to start the unit. The
      representative told
      me she would give me the code, but that it would void the
      warranty! 
      Beware of the many EcoGen warranty loopholes!<br>
      <br>
      After providing the necessary information to Generac and receiving
      the
      access code, my client started the unit and watched happily as the
      machine ran quietly and charged the batteries at twice the rate of
      her
      old unit. She went about her chores, and 2 hours later noticed
      that the
      yard had a tremendous amount of smoke in it. The generator was
      pouring
      out smoke. The lid of the enclosure was too hot to touch. <br>
      <br>
      The machine was seriously damaged. Much of the oil was blown out.<u>
        Neither the over-temperature nor the low engine oil shutdown
        functioned
        to protect the unit</u>.<br>
      <br>
      We are asking Generac to provide a new unit, not repair the flawed
      one,
      as the amount of overheating could have damaged unknown
      components. We
      understand that Generac would prefer to repair instead of
      replace.<br>
      <br>
      Under the circumstances, it would be wise to monitor a new EcoGen
      for
      much longer than would normally be required after startup. How
      long?  I don't know. I'd wait two hours to feel safe.<br>
      <br>
      Best,<br>
      <br>
      Drake <br>
      <br>
      <a moz-do-not-send="true" name="_MailAutoSig"></a>Drake Chamberlin<br>
      <i>Athens Electric LLC<br>
        OH License 44810<br>
        CO License 3773<br>
        NABCEP Certified Solar PV Installer<br>
        740-448-7328<br>
      </i><a moz-do-not-send="true" href="http://athens-electric.com/">http://athens-electric.com/</a>
      <br>
       <br>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>