<div dir="ltr"><div>Sole connection indicates that a GEC is connected to only one type of grounding electrode. This term is easily mis- understood. For example, a GEC can be connected to more than one grounding electrode—say, two ground rods—and still be considered to have a sole connection. Similarly, multiple GECs connected to the same grounding electrode are each considered to have a sole connection. When GECs have a sole connection, their maximum size is limited per NEC Sections 250.66 for an ac system and 250.166 for a dc system.  The 2014 NEC adds some clarification on this.</div>
<div><br></div><div class="gmail_extra"><div><div dir="ltr"><div>Brian Mehalic <br>NABCEP Certified Solar PV Installation Professional™ R031508-59<div>IREC ISPQ Certified Affiliated Instructor/PV US-0132<br><div><br></div>
<div>PV Curriculum Developer and Instructor<div>Solar Energy International<br><a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div></div></div>
<br><br><div class="gmail_quote">On Wed, Sep 18, 2013 at 4:52 PM, Aladdin Solar <span dir="ltr"><<a href="mailto:cpickard@aladdinsolar.com" target="_blank">cpickard@aladdinsolar.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<u></u>





<div lang="EN-US" link="blue" bgcolor="#ffffff" vlink="purple">
<div><font face="Arial">Yes, Jay, this is a TenKSolar system 
-- they certainly do have a habit of taking the 'thinking outside the 
box' approach!</font></div>
<div><font face="Arial"></font> </div>
<div><font face="Arial">The microinverter manufacturer states in their 
installation manual, "Connect the grounding electrode conductor to the 
microinverter ground clamp" so it's quite clear we are dealing with GEC 
rules.</font></div>
<div><font face="Arial"></font> </div>
<div><font face="Arial">Thanks for all your comments and the reminder of 
the NEC 250.166(C) exception which I hadn't really connected with before. 
</font></div>
<div><font face="Arial"></font> </div>
<div><font face="Arial">I'm having difficulty understanding what the 
requirement in that paragraph actually means. When it states "that portion of 
the grounding electrode conductor that is the sole connection to the grounding 
electrode shall not be required to be larger than 6AWG..." -- what does "that 
portion" and "sole connection" mean? If we have a number of GEC branches from 
that are irreversably spliced to a single 6AWG conductor bonded to the 
grounding electrode, do those various GECs affect the "that portion" and "sole 
connection" at all?</font></div><div class="im">
<div><font face="Arial"></font> </div>
<div><font face="Arial">Charlie Pickard<br>NABCEP Certified PV Installation 
Professional ™<br>Aladdin Solar, LLC</font></div>
<div><font face="Arial"> </font></div>
<div><font face="Arial"></font> </div>
</div><blockquote style="BORDER-LEFT:#000000 2px solid;PADDING-LEFT:5px;PADDING-RIGHT:0px;MARGIN-LEFT:5px;MARGIN-RIGHT:0px"><div><div class="h5">
  <div style="FONT:10pt arial">----- Original Message ----- </div>
  <div style="FONT:10pt arial;BACKGROUND:#e4e4e4"><b>From:</b> 
  <a title="billbrooks7@yahoo.com" href="mailto:billbrooks7@yahoo.com" target="_blank">Bill 
  Brooks</a> </div>
  <div style="FONT:10pt arial"><b>To:</b> <a title="re-wrenches@lists.re-wrenches.org" href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">'RE-wrenches'</a> </div>
  <div style="FONT:10pt arial"><b>Sent:</b> Wednesday, September 18, 2013 2:42 
  PM</div>
  <div style="FONT:10pt arial"><b>Subject:</b> Re: [RE-wrenches] GEC sizing for 
  a high amp,low voltage PV system with microinverters</div>
  <div><br></div>
  <div>
  <p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt">Nick,<u></u><u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u> <u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt">Thanks 
  for the clarification—it is a mysterious threaded hole….<u></u><u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u> <u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt">Bill.<u></u><u></u></span></p>
  <p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u> <u></u></span></p>
  <p class="MsoNormal"><b><span style="FONT-FAMILY:'Calibri','sans-serif';FONT-SIZE:11pt">From:</span></b><span style="FONT-FAMILY:'Calibri','sans-serif';FONT-SIZE:11pt"> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a> 
  [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Nick 
  Soleil<br><b>Sent:</b> Wednesday, September 18, 2013 10:19 AM<br><b>To:</b> 
  RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches] GEC sizing for a high amp, 
  low voltage PV system with microinverters<u></u><u></u></span></p>
  <p class="MsoNormal"><u></u> <u></u></p>
  <div>
  <div>
  <p style="MARGIN-BOTTOM:12pt" class="MsoNormal">Hi Bill and 
  wrenches,<u></u><u></u></p></div>
  <p class="MsoNormal">To clarify, our new Enphase M250 microinverter does not 
  have a grounding terminal.  The grounding of the M250 will be provided 
  through the Engage cable.  We only have a hole in the lid, in the rare 
  case that a lug will be desired or required by the AHJ, but we do not provide 
  the grounding clip with the microinverter.  A grounding terminal can be 
  added to the microinverter.  We have an application note on alternate 
  grounding methods for the M250, if needed.<u></u><u></u></p></div>
  <div>
  <p style="MARGIN-BOTTOM:12pt" class="MsoNormal"><u></u> <u></u></p></div><pre><u></u> <u></u></pre></div><br><br></div></div>__________ Information from ESET 
  NOD32 Antivirus, version of virus signature database 8815 (20130918) 
  __________<div class="im"><br><br>The message was checked by ESET NOD32 Antivirus.<br><br><a href="http://www.eset.com" target="_blank">http://www.eset.com</a><br>
  </div><p></p><div class="im">
  <hr>

  <p></p>_______________________________________________<br>List sponsored by 
  Home Power magazine<br><br>List Address: 
  <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change email address & 
  settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: 
  <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List 
  rules & etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out 
  participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br><br><br><br><br></div>__________ 
  Information from ESET NOD32 Antivirus, version of virus signature database 
  8815 (20130918) __________<div class="im"><br><br>The message was checked by ESET NOD32 
  Antivirus.<br><br><a href="http://www.eset.com" target="_blank">http://www.eset.com</a><br><br></div><p></p></blockquote><br>
<br>
__________ Information from ESET NOD32 Antivirus, version of virus signature database 8817 (20130918) __________<div class="im"><br>
<br>
The message was checked by ESET NOD32 Antivirus.<br>
<br>
<a href="http://www.eset.com" target="_blank">http://www.eset.com</a><br>


</div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div></div>