    <div class="moz-cite-prefix">Charlie:<br>
      <br>
      The answer depends on whether the "system" (modules and
      micro-inverters) is "grounded" or "ungrounded". I think you are
      describing a "grounded" system, but it's not totally clear based
      on your issue description.<br>
      <br>
      If the micro-inverter is "transformer-less" the conductors are not
      isolated between the DC-in and the AC-out. This requires the
      micro-inverter to have no DC-side system ground. The
      micro-inverter AC-side always requires an EGC.<br>
      <br>
      I am assuming that the PV modules are in close proximity to the
      micro-inverters, and the 300' home-run is for the AC outputs of
      the micro-inverters.<br>
      <br>
      Is either DC bus (PV+ or PV-) a grounded conductor, or are both
      busses ungrounded? If the DC-side combiners and re-combiners have
      OCPDs and disconnecting means for both PV+ and PV-, then your
      system is considered to be "floating" or "ungrounded".<br>
      <br>
      If the system is "ungrounded", a GEC is not required on the
      DC-side of the micro-inverter, and only an AC-EGC sized per NEC
      690.45 is required.<br>
      <br>
      If the DC-side combiners and re-combiners have OCPDs and
      disconnecting means for only one conductor (PV+ or PV-), then your
      PV system is considered to be "grounded". If the system is
      "grounded", the combined DC-GEC and AC-EGC sizing requirements in
      NEC 690.47(C)(3) apply. The larger of the EGC (Table 250.122) and
      GEC [250.166(B)] sizes will be required.<br>
      <br>
      More specifics on the PV module Vmpp and micro-inverter you're
      dealing with would be helpful.<br>
      <br>
      Regards,<br>
      <br>
      Gary Willett<br>
      Icarus Solar<br>
      <br>
      <br>
      On 9/17/13 8:37 PM, Aladdin Solar wrote:<br>
    </div>
    <blockquote cite="mid:54C54C15539D48F99FDAC11C109C088F@Dell530"
      type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <meta name="GENERATOR" content="MSHTML 8.00.6001.23520">
      <style></style>
      <div><font face="Arial" size="2">We will be installing a 40KW
          grid-tied PV system that uses PV modules wired in parallel as
          per the module manufacturer -- so it's a high amperage, low
          voltage system on the DC side. 2 branches of about 3KW of
          parallel wired modules each come together onto a DC bus. The
          DC branch conductors are sized as 2AWG.</font></div>
      <div> </div>
      <div><font face="Arial" size="2">The inverter system provided by
          the manufacturer consists of a number of UL1741 single phase
          microinverters that all are powered off of the low voltage DC
          bus. So there's a bunch of microinverters in parallel,
          combined output is single phase power.</font></div>
      <div> </div>
      <div><font face="Arial" size="2">Those microinverters have a
          ground lug labeled "GEC". You know where this is going...</font></div>
      <div> </div>
      <div><font face="Arial" size="2">Assuming we are following NEC
          690.47(C)(3), we'll be treating this ground as GEC and
          following all the GEC rules. My understanding is that because
          the DC conductors within the array are 2AWG (NEC 250.166(B),
          we will need to connect all 12 branches and 6 DC buses with
          continuous 2AWG and bring it all the way back 300' to where
          the AC GEC bond is located. We're getting a lot of pushback
          from the electrical sub and even some disagreement from the
          module manufacturer on this--no one's ever seen a grounding
          conductor of this size being required for this application.</font></div>
      <div> </div>
      <div><font face="Arial" size="2">Please don't get too bogged down
          with understanding the low voltage, parallel module spec and
          the massive number of microinverters involved. What I'm
          looking for is confirmation that I am properly
          understanding how the NEC GEC requirements apply, especially
          to the GEC size.</font></div>
      <div> </div>
      <div><font face="Arial" size="2">Charlie Pickard<br>
          NABCEP Certified PV Installation Professional ™<br>
          Aladdin Solar, LLC<br>
        </font></div>
      <br>
      <br>
      __________ Information from ESET NOD32 Antivirus, version of virus
      signature database 8813 (20130917) __________<br>
      <br>
      The message was checked by ESET NOD32 Antivirus.<br>
      <br>
      <a moz-do-not-send="true" href="http://www.eset.com">http://www.eset.com</a><br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>