<br><font size=2 face="sans-serif">Hi Kevin,</font>
<br><font size=2 face="sans-serif">We have found that network (Cat5) cables
shorter than 2m (6.5 ft) causes network reflections that contribute to
network instability in multi-unit </font>
<br><font size=2 face="sans-serif">XW systems. Do not rule out a bad or
intermittent network cable either. Also, confirm the inverters have the
same firmware and the latest.</font>
<br><font size=2 face="sans-serif">It is not necessary to have the controllers
in-network, but it allows Enhanced Grid operation, which does a better
job of keeping batteries full when </font>
<br><font size=2 face="sans-serif">selling. For off grid, they can be in
a separate network if you want to monitor them with a dedicated SCP, but
you will need to supply network power </font>
<br><font size=2 face="sans-serif">for Xanbus (AUX port can be used for
this).</font>
<br>
<br><font size=2 face="sans-serif">Rgds,<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Solar
Business</b>  |   <b>UNITED STATES</b>  |   <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001#  |   <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
 |   <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_0CDFEC700CDFE840004F708088257BD3></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">"Kevin Pegg" <kpegg@energyalternatives.ca></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">"RE-wrenches" <re-wrenches@lists.re-wrenches.org></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">08/22/2013 10:18 AM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] Xantrex XW system stability</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><tt><font size=2>Hello Wrenches, <br>
<br>
Curious how others are finding the stability of larger Xantrex XW deployments?
We have an installation with 12 Xanbus devices (4 x XW6048, 6 x XW-MPPT60,
1 x AGS, 1 x SCP) and it keeps crashing. Power cycle the whole system and
it's fine for a few weeks and then it crashes again. <br>
<br>
I find with smaller deployments under 5 Xanbus devices the stability is
much better, but still get the occasional customer call with a system gone
haywire and a power cycle fixes. <br>
<br>
This particular installation is in the high arctic darn near the north
pole and sending a tech up there next week to resolve. Needless to say,
it's an expensive ordeal to get up there. <br>
<br>
Kevin<br>
<br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
<br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________<br>
</font></tt>
<br>
<br>