<div dir="ltr"><div class="gmail_default" style="font-family:verdana,sans-serif">This is an excellent paper that I would love to share with potential customers in it's final form. I have one suggestion - there might be a caveat in your load start example where you have a single large load that comes on occasionally and for a short period. For example, if there is a piece of machinery that comes on for 15 minutes and draws 2.5kw on it's own, but only runs once per day (a well pump for example), it may be advantageous to set the load start amps a little higher even though it exceeds the "5% rule." This may be more desirable than extending the load start delay. I've run into this when lifting daily water requirements to an elevated tank. I didn't feel it was necessary to start the generator every day in this case. </div>
<div class="gmail_default" style="font-family:verdana,sans-serif"><br></div><div class="gmail_default" style="font-family:verdana,sans-serif">What I would take from this paper as a buyer is that every system is very different, which is exactly what we want to point out. The other thing is that changing load conditions require recalculation and recalibration.</div>
<div class="gmail_default" style="font-family:verdana,sans-serif"><br></div><div class="gmail_default" style="font-family:verdana,sans-serif">One thing I like to point people to is Norther Arizona Wind & Sun's Battery faq (<a href="http://www.solar-electric.com/deep-cycle-battery-faq.html" style="font-family:arial" target="_blank">http://www.solar-electric.com/deep-cycle-battery-faq.html</a>). If they are not willing to read and understand this, or don't want a pricey maintenance contract, they may not be cut out for battery backup living.</div>
<br><br><div><div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif"><div style="margin:0px 0px 8px"><p style="margin:0px"><span><span>Jason Szumlanski</span></span></p><div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">
</div><p></p><p style="margin:0px"><span><span></span></span></p><div class="gmail_default" style="font-family:verdana,sans-serif;display:inline">Fafco Solar</div><br> <p></p></div></div></div><div id="WISESTAMP_SIG_gmail_session">
<div style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif"><div style="margin:0 0 8px 0"><p style="margin:0"> </p><div style="clear:both"></div></div></div></div></div><div class="gmail_extra"><br><br><div class="gmail_quote">
On Mon, Aug 19, 2013 at 8:19 PM, William Miller <span dir="ltr"><<a href="mailto:william@millersolar.com" target="_blank">william@millersolar.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<u></u>
<div>
<div><font size="4" face="Arial">
<p align="center"></p>
<p align="center"><font size="1" face="Verdana"></font></p>
<p align="left"><font face="Verdana"><font size="1"><span> <font size="3" face="Arial">Friends:</font></span></font></font></p>
<p align="left"><font face="Verdana"><font size="1"><span></span></font></font> </p>
<p align="left"><font face="Verdana"><font size="1"><span></span><span><font size="3" face="Arial">I wrote a draft white paper to discuss the issues relevant to PV
Assist systems. If you are up for along read, please feel free. If
you have suggestions, I welcome them.</font></span></font></font></p>
<p align="left"><font face="Verdana"><font size="3" face="Arial"><span>This idea is new to me so I am learning as I
go. Also, I could not easily past the chart so I included a link to
it. Also, the table did not quite line u, but I think you canfigure it
out.</span></font></font></p>
<p align="left"><font face="Verdana"><font size="3" face="Arial"><span>Thanks,</span></font></font></p>
<p align="left"><font face="Verdana"><font size="3" face="Arial"><span>William Miller</span></font></font></p>
<p align="left"><font face="Verdana"><font size="1"><span></span></font></font> </p>
<p align="left"><font face="Verdana"><font size="1"><span></span> </font></font></p>
<p align="center"><font size="1" face="Verdana"> </font><b>GENERATOR / BATTERY WITH PV
ASSIST</b></p>
<p align="center">August 19, 2013</p>
<p align="center"></p><u>
<p align="center">DRAFT, PRINCIPLES DISCUSSED ARE UNDER RESEARCH</p></u>
<p align="center"></p><b>
<p> </p>
<p>Introduction: </p></b>Whenever we design an Off-grid Alternative Energy systems,
we usually design the system so that non-fossil battery charging sources (solar,
wind, hydro) provide a majority of the energy for battery charging. Sometimes we
come across systems that have loads that are so large that it is not practical
to rely solely on non-fossil sources. A large generator will be needed to run on
a daily basis. We call these systems Generator / Battery Systems with PV Assist,
or "PV Assist" for short. We use the term PV to describe all RE charging sources
since PV is most common in our area.
<p>We have found that battery charging in PV Assist systems using traditional
settings may cause premature failure in battery arrays for reasons described
below. We want everyone to enjoy the longest battery life possible so we have
developed some alternative settings for battery charging that will hopefully
achieve longer battery life.</p>
<p>It has always been the goal of solar technicians to minimize generator run
time. In retrospect, this may not be the best idea in PV Assist systems. The
consequence may be reduced battery life.</p>
<p>Batteries wear out when they are "cycled". A cycle is defined as a discharge
and charge. Normally, an off-grid system will charge batteries during the day
and discharge them at night, resulting in one cycle per day. In the case of a PV
Assist, the batteries may cycle multiple times per day. Your battery bank is
rated for a finite number of cycles. If they cycle 4 times per day, they wear
out 4 times faster than if they cycled once per day.</p>
<p>In an attempt to preserve the longevity of a battery bank in a PV Assist
system, we are experimenting with alternative generator auto start and inverter
/ charge battery charge settings. In general, we suggest that if batteries are
going to be cycled multiple times per day, that they be cycled less "deeply." In
other words, do not discharged the batteries to as low a voltage as one would
normally.</p>
<p>In order to achieve this goal, the generator will run more frequently than in
a traditional hybrid off-grid system. In these systems it is already a given
that generator run time will occur every day, even multiple times per day. We
are essentially embracing generator run time to preserve battery life. We are
trading off greater "wear-and-tear" on the generator for less wear-and-tear on
the batteries. The decision to do this belongs with the system owner.</p><b>
<p>Battery DOD versus life span:</p></b> See figure 1 below that compares the depth
of discharge (DOD) of a battery to battery life. Note that the maximum expected
cycles is 4,000. If you cycle 4 times per day at this DOD, expect 1,000 days of
life, or three years. If you cycle to 80% you can expect 1000 cycles, or 250
days. This is a very short life span and this scenario needs to be avoided. The
sweet spot is to be determined for each unique situation, but for discussion we
are assuming we want 3000 cycles, or about 2 years. This is not long for a
battery bank, but keep in mind this design assumes we have undersized the
battery bank significantly. Essentially you are buying two or three small
battery banks in the span of time one properly sized battery bank would
last.
<p>To achieve 3,000 cycles, the DOD must be limited to about 70%. The lowest we
can allow the battery bank voltage to get, when measured at rest, is about 49.0
volts. Keep in mind that batteries being discharged will exhibit a voltage lower
than the at-rest voltage. Also keep in mind that surge loads will cause the
battery voltage to temporarily sag. The above described logic drives our
suggested system settings below.</p>
<p><a href="http://www.trojanbatteryre.com/PDF/datasheets/L16REB_TrojanRE_Data_Sheets.pdf" target="_blank">http://www.trojanbatteryre.com/PDF/datasheets/L16REB_TrojanRE_Data_Sheets.pdf</a></p>
<p><b>Generator Auto Start: </b>We will require that generators in a PV Assist
system be able to start automatically based on both battery voltage and load.
Most common inverter/charger systems are capable of this. The two conditions for
auto start are described below.</p><b>
<p>Battery start: </p></b>In the case of a battery start condition, the master
inverter monitors the battery voltage. Generally, if the voltage becomes
slightly low for 24 hours, or the voltage becomes moderately low for 2 hours or
extremely low for 15 minutes, the generator will start. When the generator
starts in these conditions, the system will complete a full three stage charge
cycle. An explanation of a three stage charge cycle is beyond the scope of this
paper.
<p>If we are assuming that the generator will start more than once per day,
there is reason to desire a short run time. Charge settings will be modified to
allow for a shorter battery charge cycle. One must be cautious to be sure that
if loads decrease, settings are modified to reflect this reduction. If this is
not done, there is a risk that the batteries will never recharge adequately. It
is also required that system operators manually equalize the batteries every 30
days. This normally only applies to flooded batteries but we will present
modified EQ settings for sealed (VRLA) batteries. In the case of VRLA batteries,
this is not to actually equalize the batteries but to ensure a full absorption
cycle.</p><b>
<p>Load Start: </p></b>For load start settings, the system senses how high the loads
are (current draw on the system). If the loads exceed a programmed amount for a
programmed time, the generator will run until the loads decrease below a lower
programmed value for a programmed time delay. We will use this feature
extensively for PV Assist systems.<b>
<p>Load Start Levels:</p></b> For this program, we are assuming that we do not want
to subject a battery bank to any draw that would deplete it in less than 10
hours. If the draw exceeds this amount, the generator should start. Calculations
show that if the draw exceeds 5% of the battery watt hours, the bank will
deplete in 10 hours or less. Example: If a 48 volt battery bank has an amp/hour
rating of 1,000, the watt/hour rating is 48,000. The generator should start if
the load exceeds 2.4 KW. These calculations are based on an available amp/hour
capacity 50% of name-plate.<b>
<p>Load Start Delay:</p></b> The excess load must be present for a programmable
period of time before the generator will auto-start. If this load occurs for
long enough the battery voltage will decline and the generator will auto-start
for voltage reasons. This will cause a charge cycle, which is usually not
necessary. Therefore we need to find a proper delay time that will start the
generator if the excess load is expected from more than a short duration. It is
up to the system designer to anticipate load values and load durations. Some
examples are included below.<b>
<p>Load Stop / Load Stop Delay:</p></b> Load stop is the value below which the load
must drop before the generator will auto-stop. The generator must fall below
this value for a programmed period of time before the generator will stop. These
values are difficult to predict unless the particulars of a system are known.
The suggested starting point for Load Stop is 2.5% of bank watt hours (a 20 hour
depletion). The stop delay is determined by factors discussed below.<b>
<p>Quiet Time: </p></b>Most modern inverter / chargers have a quiet time setting.
When this is invoked the generator will not battery start for the 24 or 2 hours
volt settings described above. We use this not only to allow for reduced
generator run at night, but to disallow battery starting in the morning of a
sunny day where the PV charge might prevent a generator start. We will embrace
quiet time as valuable in PV Assist systems.<b>
<p>PV Charging:</p></b> We recommend that PV and other RE charging sources be set at
traditional values. This will differ from the suggested settings below only in
absorption duration. This value should be a minimum of 2 hours, or a taper
setting that provides a similar absorption period.<b>
<p>Settings: </p></b>Below are suggested settings for three stage charging systems
and for generator auto-start systems. These settings are for nominal 48 volt
systems and can be interpolated for other nominal system voltages. These
settings apply to flooded lead-acid and VRLA (sealed) batteries:
<p><b>Parameter <span>
</span>FLA <span>
</span>VRLA</b></p>
<p><span>A</span>bsorb volts: <span> </span>57.6 <span> </span>56.8</p>
<p>Absorb time: <span>
</span>0.5 hours 0.5 hours</p>
<p>EQ Volts <span>
</span>61.0 <span>
</span>56.8</p>
<p>EQ Time: <span> </span>2.0
hours 2.0 hours</p>
<p>24 hour start:<span>
</span>48.8 <span>
</span>48.8</p>
<p>2 hour start: <span>
</span>47.8 <span>
</span>47.8</p>
<p>15 minute start: <span>
</span>47.0 <span>
</span>47.0</p>
<p>Load Start: <span>
</span>5% of battery array watt/hours</p>
<p>Load Start delay: <span>
</span>Minimum setting</p>
<p>Load Stop: <span>
</span>1% of battery array watt/hours</p>
<p>Load Stop delay: <span>
</span>Determined by load profile, see below</p><b>
<p>Load profile:</p></b> We need to determine the number of cycles of loads that
exceed 5% of battery array watt hours. This is the number of times the generator
will start on a daily basis.
<p>There should be a finite number of times a generator starts each day to avoid
excess wear on the generator starting mechanism. If the load cycle number
exceeds the desired generator starts per day, then the load cycle needs to be
reduced or the delay time will need to be extended to exceed the off cycle of
the 5% load.</p>
<p>For example if the excess load comes on every two hours, the generator will
start 12 times per day. If this is acceptable, then use a minimum Load Stop
setting. The generator can shut down soon after the loading stops.</p>
<p>If this number of generator starts is excessive, the load cycle count needs
to be reduced or generator load start settings adjusted. For example, if the
excess load is an appliance, the user needs to be instructed to use the
appliance less often. Or, the load stop time needs to be increased so that the
generator stays on for several cycles of the load. For example, if the uses of
the appliance can be grouped so that most of the times it is used there is no
more than 20 minutes between uses, set the stop delay for >20 minutes and the
generator will remain on until the grouped use cycle is complete.</p>
<p>An example might be a water heater that is used in the morning and evening,
but not the rest of the day. The heater might come on three times in the morning
and three times in the evening, cycling off for 30 minutes. In this case the
load stop delay can be set at >30 minutes and the generator will run for a
few hours morning and evening. The consumer should be encouraged to group other
loading to occur during those hours. The cooking, laundry and workshop
activities could occur during those hours, making use of the generator
run.</p><b>
<p>Summary: </p></b>This program is still under development and we welcome your
feedback on the results you achieve using these settings.
<p>End of paper.</p></font></div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>