<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <div class="moz-cite-prefix">Ryan,<br>
      I may have found the answer to my original post, but it raises
      more questions. <br>
      <br>
      I wrote that these were MV units (MNSPD300), but I checked with my
      lead tech and learned that in both cases he used LV units
      (MNSPD115). Could this be the reason? He told me that he has used
      the LV with 120V inverters and the MV with 120/240V inverters. The
      instruction manual states that the LV units are designed to be
      used on nominal 90VAC and 115VDC circuits, and have a Maximum
      Continuous Operating Voltage of 180V. The manual states: "The
      MidNite Solar SPD voltage rating should be chosen according to the
      nominal voltage of the system. Do not install an SPD with Maximum
      Continuous Operating Voltage (MCOV) below the nominal voltage of
      the system; this will deteriorate the SPD and making it
      unavailable when you most need it." If this is true, then the LV
      (with its 180 MCOV) should be fine at 120VAC. The instructions are
      confusing: should we use an MNSPD115 or an MNSPD300 with 120VAC
      output? And in this case, could this be the cause of the
      failure-to-sleep problem?<br>
      <br>
      If we should be using the MNSPD300 with 120VAC inverter output,
      then the description on the Midnite website is confusing at best.
      It states that the MNSPD115 "is designed for both AC and DC
      systems and provides protection to service panels, load centers or
      where the SPD is directly connected to the electronic device
      requiring protection." But service panels and load centers seldom
      if ever carry AC at less than 90VAC, the nominal rating of the
      MNSPD115. Please clarify all of this!<br>
      <br>
      Thanks, Allan<br>
      <div class="moz-signature">
        <meta http-equiv="Content-Type" content="text/html;
          charset=ISO-8859-1">
        <meta name="ProgId" content="Word.Document">
        <meta name="Generator" content="Microsoft Word 11">
        <meta name="Originator" content="Microsoft Word 11">
        <link rel="File-List" href="SignatureNew_files/filelist.xml">
        <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:Template>Normal</o:Template>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>5</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2013-06-07T19:15:00Z</o:Created>
  <o:LastSaved>2013-06-10T19:03:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>73</o:Words>
  <o:Characters>420</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>3</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>492</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:UseFELayout/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]-->
        <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-alt:"\FF2D\FF33 \660E\671D";
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"MS Mincho";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.SpellE
        {mso-style-name:"";
        mso-spl-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="4098"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
        <div class="Section1">
          <p class="MsoNormal"><span style="font-size:10.0pt"><span
                style="mso-spacerun:yes"> </span></span></p>
        </div>
      </div>
      On 8/13/2013 11:28 AM, Ryan wrote:<br>
    </div>
    <blockquote cite="mid:520A6CC4.3070201@kb1uas.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      Allan<br>
      That is not expected behavior. Which model of SPD are you using?<br>
      <br>
      Ryan<br>
      <img src="cid:part1.05020906.02010702@positiveenergysolar.com"
        border="0"><br>
      <br>
      <br>
      <div class="moz-cite-prefix">On 8/13/2013 1:08 PM, Allan Sindelar
        wrote:<br>
      </div>
      <blockquote cite="mid:520A680E.1050302@positiveenergysolar.com"
        type="cite">
        <meta http-equiv="content-type" content="text/html;
          charset=ISO-8859-1">
        Wrenches,<br>
        Very seldom do inverters in off grid systems ever go to sleep
        anymore, given the increase in phantom electronic loads and
        greater customer expectations. Coupled with lower module prices,
        we usually size larger arrays and inverters remain on
        continuously. However, we also service and upgrade many existing
        systems, and some customers still want their inverters to go
        into search mode. They typically either have gotten used to a
        more energy frugal lifestyle over many years, or (to their
        credit) choose to buck the system and live with a lighter energy
        and resource footprint. <br>
        <br>
        Twice in recent months we have added Midnite MNSPD MV surge
        arrestors to the AC output of smaller systems and discovered
        that the inverters will no longer go into search mode. It
        doesn't appear to make any difference where the search watts
        threshhold is set. One system used a 24V Outback FX2524T (with
        current boards following a nearby lightning strike) and the
        other used a Magnum MS2812. In the former case, we defeated the
        search (against the customer's preference, as she liked the
        total silence once her day was done). In the latter, the
        customer rejected and we removed the surge arrestor once it
        became clear that the inverter wouldn't sleep.<br>
        <br>
        Has anyone else experienced this? Is there a fix for it? Robin,
        can you chime in here (off list if necessary; I'll carefully
        post your response)?<br>
        <br>
        Thank you,<br>
        Allan<br>
        <div class="moz-signature">-- <br>
          <meta http-equiv="Content-Type" content="text/html;
            charset=ISO-8859-1">
          <meta name="ProgId" content="Word.Document">
          <meta name="Generator" content="Microsoft Word 11">
          <meta name="Originator" content="Microsoft Word 11">
          <link rel="File-List" href="SignatureNew_files/filelist.xml">
          <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:Template>Normal</o:Template>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>5</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2013-06-07T19:15:00Z</o:Created>
  <o:LastSaved>2013-06-10T19:03:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>73</o:Words>
  <o:Characters>420</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>3</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>492</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:UseFELayout/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]-->
          <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-alt:"\FF2D\FF33 \660E\671D";
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;
        mso-font-charset:128;
        mso-generic-font-family:modern;
        mso-font-pitch:fixed;
        mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"MS Mincho";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.SpellE
        {mso-style-name:"";
        mso-spl-e:yes;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="4098"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
          <div class="Section1">
            <p class="MsoNormal"><b>Allan <span class="SpellE">Sindelar</span></b><br>
              <span style="font-size:10.0pt"><a moz-do-not-send="true"
                  href="mailto:Allan@positiveenergysolar.com"><u><span
                      style="color:#000099">Allan@positiveenergysolar.com</span></u></a></span><br>
              <span style="font-size:10.0pt">NABCEP Certified PV
                Installation Professional <br>
                NABCEP Certified Technical Sales Professional<br>
                New Mexico EE98J Journeyman Electrician<br>
                Founder and Chief Technology Officer<br>
                <b>Positive Energy, Inc.</b>, a Certified B <span
                  class="SpellE">Corporation<sup><span
                      style="font-size:7.5pt">TM</span></sup></span><br>
                3209 Richards Lane<br>
                Santa Fe, New Mexico 87507<br>
                <b>505 424-1112 office 780-2738 cell</b><br>
                <a moz-do-not-send="true"
                  href="http://www.positiveenergysolar.com/"
                  target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></p>
            <p class="MsoNormal"><span style="font-size:10.0pt"><span
                  style="mso-spacerun:yes"> </span></span></p>
          </div>
        </div>
      </blockquote>
    </blockquote>
  </body>
</html>