    <font face="Helvetica, Arial, sans-serif">Belated thanks for the
      replies on this, Jason et al. Sorry for my lack of a clear
      explanation- Jason interpreted me correctly. Apparently this
      Lennox unit was installed without a neutral- I'm awaiting more
      info from the PE.</font><br>
    <br>
    <div class="moz-cite-prefix">On 2013/7/5 19:25, Jason Szumlanski
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAJJtG3pa9PQWfufUuFeU78jU6DWp7dWQioNTEdeb8DfrF6hX-g@mail.gmail.com"
      type="cite">
      <p>I think what Dave is saying is that the enphase cable neutral
        is connected to the EGC in the roof mounted j-box, and no
        neutral is run to the Lennox panel or disconnect. While the
        neutral should not carry line current under normal operation,
        Enphase calls it a neutral - look up the NEC definition of
        neutral. I can see an AHJ having reservations about this,
        whether the "combined Neutral/EGC/GEC" is bare or insulated. </p>
      <p>I would not waste time trying to argue this with the AHJ. I
        would bring three current carrying conductors plus a combined
        EGC/GEC to the main distribution panel, just like every other
        Enphase job we do. </p>
      <p>I spend a fair amount of time explaining how this solar powered
        air conditioner is nothing revolutionary, except for the
        creative marketing. Anyone out there try to team up with a HVAC
        company to market any A/C unit as solar powered?</p>
      <p>Jason Szumlanski<br>
        Fafco Solar</p>
      <div class="gmail_quote">On Jul 5, 2013 5:14 PM, "August Goers"
        <<a moz-do-not-send="true" href="mailto:august@luminalt.com">august@luminalt.com</a>>
        wrote:<br type="attribution">
        <blockquote class="gmail_quote" style="margin:0 0 0
          .8ex;border-left:1px #ccc solid;padding-left:1ex">
          Hi Dave,<br>
          <br>
          I'm not sure I'm understanding your scenario clearly but I'll
          take a crack<br>
          at it. The Enphase system should have a bare #6 GEC for each
          micro and can<br>
          then transition to a #8 green GEC once in conduit and run all
          the way back<br>
          to the main ground electrode system. The #6 and #8 should be
          irreversibly<br>
          crimped together since the GEC needs to be continuous.
          Certainly it is not<br>
          okay for the neutral in the Lennox panel to be bare unless it
          is somehow a<br>
          main panel. You could run the DC GEC along with the other
          conductors and<br>
          it can serve as a dual purpose GEC and equipment grounding
          conductor per<br>
          2011 NEC 690.47(C)(3).<br>
          <br>
          Best,<br>
          <br>
          August<br>
          -----Original Message-----<br>
          From: <a moz-do-not-send="true"
            href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a><br>
          [mailto:<a moz-do-not-send="true"
            href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>]
          On Behalf Of Dave Click<br>
          Sent: Wednesday, July 03, 2013 6:26 AM<br>
          To: RE-wrenches<br>
          Subject: [RE-wrenches] EGC for Enphases<br>
          <br>
          All,<br>
          <br>
          I was just looking at small 4-module Andalay (Enphase 190)
          system tying<br>
          into one of the Lennox solar-ready air conditioners. The
          engineer had<br>
          specified the 690.47(C) GEC be run directly from the array
          down to the<br>
          existing electrode. Running from the inverters is a 2+G wire
          to the Lennox<br>
          panel; they are using the uninsulated ground as the circuit
          neutral. It<br>
          seems to me that this violates 200.7 (grounded conductor
          marked white or<br>
          grey). Also, 250.134(B) (EGC run with circuit conductors),
          about which the<br>
          engineer states "I have been studying the NEC on this and I
          believe that<br>
          the intent is to permit the ground to be carried with the
          current carrying<br>
          conductors, not require."<br>
          <br>
          Am I missing something?<br>
          <br>
          Thanks,<br>
          Dave<br>
          _______________________________________________<br>
          List sponsored by Home Power magazine<br>
          <br>
          List Address: <a moz-do-not-send="true"
            href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change email address & settings:<br>
          <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          List-Archive:<br>
          <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
            target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          <br>
          List rules & etiquette:<br>
          <a moz-do-not-send="true"
            href="http://www.re-wrenches.org/etiquette.htm"
            target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out participant bios:<br>
          <a moz-do-not-send="true"
            href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
          _______________________________________________<br>
          List sponsored by Home Power magazine<br>
          <br>
          List Address: <a moz-do-not-send="true"
            href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change email address & settings:<br>
          <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
            target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          <br>
          List rules & etiquette:<br>
          <a moz-do-not-send="true"
            href="http://www.re-wrenches.org/etiquette.htm"
            target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out participant bios:<br>
          <a moz-do-not-send="true"
            href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>