    <div class="moz-cite-prefix">We'd need more info to figure this out.<br>
      1) Wire Size<br>
      2)  Type of charge controller C 60 or new MPPT model<br>
      3) use a clamp on meter to measure actual current<br>
      4) measure voltage drop across the breaker.<br>
      <br>
      This very well could just be a loose connection at the breaker
      either the cable side of the breaker, or where it snaps on to the
      buss bar.<br>
      I've had QOs not work at higher voltage DC.  (over 50 v) I'd have
      to wiggle the breaker to get good contact on the buss, and it
      would start working again.  Given the age of the system, there's
      probably some corrosion and dust on the contact points.  Might
      just need some sanding/ filing.  <br>
      The heat described fits with a loose/ high resistance connection.
      <br>
      Switching to a Midnite/ Outback breaker would be the only real way
      to reliably make sure it doesn't keep happening though.  On old
      systems, our job is to exorcise the ghosts from the machine. <br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 7/9/2013 9:10 AM, jay peltz wrote:<br>
    </div>
    <blockquote cite="mid:09ADFA12-C61A-4D50-9DA1-ED61824CFF54@asis.com"
      type="cite">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <div>Hi Dan</div>
      <div>I'm guessing the wire can handle the 100 amp if they are
        already running 60a. </div>
      <div>I've had QO breakers go bad, even ones not tortured like that
        one. </div>
      <div><br>
      </div>
      <div>The derate is interesting as it has to do with less atoms of
        air per volume. Less air, equals less cooling</div>
      <div><br>
      </div>
      <div>Jay</div>
      <div>Peltz power<br>
        <br>
        Sent from my iPad</div>
      <div><br>
        On Jul 8, 2013, at 10:07 PM, Dan Fink <<a
          moz-do-not-send="true" href="mailto:danbob88@gmail.com">danbob88@gmail.com</a>>
        wrote:<br>
        <br>
      </div>
      <blockquote type="cite">
        <div>
          <div dir="ltr">Esteemed Wrenches;
            <div><br>
            </div>
            <div style="">A weird troubleshooting call today for my
              business partner DanB. I wish I had been along if only for
              shock and awe and lessons learned.</div>
            <div style=""><br>
            </div>
            <div style="">
              A nicely installed vintage 12VDC PV system that someone
              else designed and installed over 10 years ago, we replaced
              a dead/frozen battery bank a month ago. DanB went back
              today because customer reported low battery bank voltage.</div>
            <div style=""><br>
            </div>
            <div style="">He found the PV input breaker tripped, a
              Square D QO 2-pole 60 amp. About 600 watts of PV 12vdc
              nominal on the roof. Reset the breaker, and a few minutes
              later it was too hot to touch.</div>
            <div style=""><br>
            </div>
            <div style="">So our working theory -- the 60a QO on *DC*
              has a 1.2x ampacity derate, which puts 600w PV right at 60
              amps instead of 50. There's also a bit of a high altitude
              derate, which I don't understand at all. And during the
              battery disaster last year bank voltage was certainly
              11vdc or less, and was a bit over 11vdc on DanB's arrival
              since the PV had not been charging. That puts us at
              possibly 65.5 amps. The breaker was maybe just doing its
              job correctly, though the heat was disturbing I am told.Or
              maybe it got damaged during the battery disaster......both
              + and - were connected thru the 2 poles.</div>
            <div style=""><br>
            </div>
            <div style="">In any case, our question --- due to my fuzzy
              memory and poor shopping skills, we have a 100 amp QO 2
              pole breaker in stock that needs a home, and it'll plug
              right in. I have a nice tech bulletin from Schneider
              Electric about DC ratings of their breakers that doesn't
              show that a 100a QO 2 pole even exists, and a Schneider
              FAQ that says it'll work fine:</div>
            <div style=""><a moz-do-not-send="true"
href="http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US&lang=en&id=FA125383&redirect=true">http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US&lang=en&id=FA125383&redirect=true</a><br>
            </div>
            <div style=""><br>
            </div>
            <div style="">Any advice on this? We'd sure love to just
              drop by and pop in the new 100a amp QO breaker instead of
              installing a whole new DC rated Midnite box. But we don't
              want to leave a fire hazard either. With 15 years service
              on our local volunteer fire department, It would be
               rather embarrassing if a "fix" we made to this old
              off-grid system caused a fire. ;-) We are aware of the 5k
              AIR issue with these breakers, but the battery bank is
              small enough I don't think it's quite up there, and
              information on AIR interruption from battery manufacturers
              is hard to find......and of course it's a weird curve.</div>
            <div><br>
            </div>
            <div>Thanks in advance;</div>
            <div><br clear="all">
              <div>Dan Fink,<br>
                Executive Director;<br>
                Otherpower<br>
                Buckville Energy Consulting<br>
                Buckville Publications LLC<br>
                NABCEP / IREC accredited Continuing Education Providers<br>
                970.672.4342<br>
                <br>
                 </div>
            </div>
          </div>
        </div>
      </blockquote>
      <blockquote type="cite">
        <div><span>_______________________________________________</span><br>
          <span>List sponsored by Home Power magazine</span><br>
          <span></span><br>
          <span>List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
          <span></span><br>
          <span>Change email address & settings:</span><br>
          <span><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List rules & etiquette:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
          <span></span><br>
          <span>Check out participant bios:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
          <span></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>