<div dir="ltr">Andrew, Daniel, August,<div><br></div><div>Thanks for your suggestions.  </div><div>Andrew, the PR valve had gone off only twice that I could tell.  When I checked it again on Saturday the pressure  was again at zero but I used the PR valve to vent some residual pressure/fluid from the system.  It seems sound.</div>


<div><br></div><div>Daniel,</div><div>On my previous visit I had also assumed a system leak and so checked connections at the collectors, at the line set transition, and there was no evidence of a leak.  The pressure tank was clearly marked with the set pressure, commissioning date, and initials of my lead installer, so I "assumed that was good".  After all the system had been in service without  issue for approximately 1 year.  Wrong!  After relieving the fluid in the system I checked the expansion tank pressure, and it was at zero.  My thought was either the bladder had ruptured or the Schrader valve had a slow leak.  When I pulled the valve out there was no fluid (thanks for the suggestion to check this August ), so I assumed a leaking valve.  I lubed and re-seated the valve and re-pressurized the tank.  I then recharged the system, bled the air,and 4 days later the pressure is rock solid after a couple of good solar days.<br>


</div><div><br></div><div>I had never had an expansion tank lose pressure before, so my take away was to add "Verify the expansion tank pressure", to the  troubleshooting/service checklist.</div><div><br></div>
<div>
Daniel,</div><div>I was unaware that the corrugated line set had capacity for expansion , but witnessed this on the recharge cycle.  As I pressurized the system, closing the drain valve, to allow pressure to build,  I noted the insulation on the return line set slide up the pipe 2 inches or so and then slide back as pressure was released.  It makes sense that the line set can expand along the length of the pipe. Good to know.</div>


<div><br></div><div>So in reviewing things last Friday evening before my service call Saturday, I went back and verified the pipe, collector, heat exchanger, and expansion tank  volume.  I was sure the exp tank was adequate but still wasn't thinking empty expansion tank.  In doing this I pulled out the Calefi idronics 3 manual and did some reading.  The appendix there offers some calcs for determining expansion tank volume (attached).  Tha calcs showed the 18 liter expansion tank to be oversized for the  system (so good to go on this front).  The appendix also offers calcs for expansion tank charging pressure.  These calcs suggest a system charging pressure of 18 PSI (rather than the 26 psi  suggested by the Schuco table I posted previously. The Calefi calcs also seem to be independent of the charging pressure, where as the Schuco table clearly correlates the two.  If anyone has any insights on this please share.</div>


<div><br></div><div>I rechecked the expansion tank pressure after filling the system.  What I found was that  the expansion tank pressure had increased from 26 psi to 35 psi, with the system pressurized to 30 psi.  My expectaion was that the expansion tank pressure would have increased to match the glycol charging pressure.  I thought at first this was a gauge offset, but on second thought I considered it might be the glycol is an incompressible fluid whereas the air is a compressible fluid.  Again, If anyone has any insights on this please share.</div>
<div><br></div><div>Thanks again for your replies,</div><div>Carl Adams</div><div>SunRock Solar</div><div class="gmail_extra"><br></div></div>