<br><font size=2 face="sans-serif">Hi Lee,</font>
<br><font size=2 face="sans-serif">The MC version is similar to the standard
SW, but does not have grid usage menu (no sell/lbx), and does not give
AC1 priority (assuming both inputs are present). It will support the generator
with battery power whenever the load exceeds the AC2 Amps setting in Menu
11.</font>
<br><font size=2 face="sans-serif">Eric<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Solar
Business</b>  |   <b>UNITED STATES</b>  |   <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001#  |   <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
 |   <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_06FD283406FD2404005C088888257B91></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">"info@solarplexus1.com" <info@solarplexus1.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches@lists.re-wrenches.org</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">06/21/2013 07:29 AM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] generator support mode</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><tt><font size=2><br>
                
I have a project using an SW4024 inverter that uses the generator support
mode with a smaller hydro AC generator.   Worked well, but one of
the to inverters died. There are plenty of new SWs on the internet, but
all the new ones are SW4024MC2.   Apparently the SELL mode does not
exist in the MC2 version and Auto Gen Start is an option.   Does anyone
know if the good old generator support is available in the MC2 version,
or has it been scrapped along with the SELL mode. <br>
<br>
                
Generator support mode--where some inverter AC output can be added to the
generator AC input to meet a load larger than the generator could otherwise
handle.  Not just where the inverter backs off the battery charger
enough to use full generator input for the load.<br>
<br>
                
Any insight on the MC2 version would be helpful.  <br>
<br>
Lee Tavenner<br>
Solar Plexus<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
<br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________<br>
</font></tt>
<br>
<br>