<html>
<head>
<meta content="text/html; charset=ISO-8859-1"
http-equiv="Content-Type">
</head>
<body text="#000000" bgcolor="#FFFFFF">
<div class="moz-cite-prefix">Dick,<br>
No, I stand by what I wrote, but I'll clarify.<br>
<br>
If the gennie has a GFI, it will often have trouble feeding an
inverter, as the GFI will sense the ground loop and trip. The
ground loop is caused by bonds in both gennie and the first point
of AC disconnect on the inverter's output (a.k.a. the AC bond
point in the E-Panel or equivalent). You won't ever want to remove
the neutral-ground bond in the E-Panel, as then you'd only have a
bond when plugged into the gennie. This is why inverters designed
for RV's are listed to UL 458 rather than 1741 - they have an
internal relay to make/break the neutral/ground bond. When
boondocking it's made, but when plugged into shore power it's
open, allowing the utility hookup to bond at the meter.<br>
<br>
I asked Wiles about this years ago, as there's no fully
Code-compliant way to deal with this issue, in an off grid system
with a contractor's special gennie with an unbreakable bond. He
said the least unsafe approach is to leave the ground loop in
place and allow the grounding conductor of the gennie cord to
carry some of the neutral current (which implicitly means
bypassing any GFI). But in this case, the ground loop may in
itself be the source of the appliance's failure to run off of the
inverter. It's thus worth trying this approach. If it works with
the grounding conductor open, then that's the likely cause. The
move the gennie far enough from any building with inverted AC,
treat it like a "separate structure" per NEC, ground the bonded
chassis to its own rod(s), and you've done all you can.<br>
<br>
If there's a ground fault in the coffee maker, no problemo, as the
cofeemaker metal is grounded through the bond in the E-Panel. It's
just the gennie that's not bonded to the main system ground.<br>
<br>
High quality commercial and industrial generators allow the bond
to be either bonded or floated, but homeowner units often can't be
floated. Therein's the problem(o).<br>
<br>
Clear as mud?<br>
Allan<br>
<br>
<div class="moz-signature">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="ProgId" content="Word.Document">
<meta name="Generator" content="Microsoft Word 11">
<meta name="Originator" content="Microsoft Word 11">
<link rel="File-List" href="SignatureNew_files/filelist.xml">
<!--[if gte mso 9]><xml>
<o:DocumentProperties>
<o:Author>pe</o:Author>
<o:Template>Normal</o:Template>
<o:LastAuthor>pe</o:LastAuthor>
<o:Revision>2</o:Revision>
<o:TotalTime>1</o:TotalTime>
<o:Created>2013-06-07T19:15:00Z</o:Created>
<o:LastSaved>2013-06-07T19:16:00Z</o:LastSaved>
<o:Pages>1</o:Pages>
<o:Words>73</o:Words>
<o:Characters>418</o:Characters>
<o:Company>pe</o:Company>
<o:Lines>3</o:Lines>
<o:Paragraphs>1</o:Paragraphs>
<o:CharactersWithSpaces>490</o:CharactersWithSpaces>
<o:Version>11.9999</o:Version>
</o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
<w:WordDocument>
<w:SpellingState>Clean</w:SpellingState>
<w:GrammarState>Clean</w:GrammarState>
<w:ValidateAgainstSchemas/>
<w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
<w:IgnoreMixedContent>false</w:IgnoreMixedContent>
<w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
<w:Compatibility>
<w:UseFELayout/>
</w:Compatibility>
<w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
</w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
<w:LatentStyles DefLockedState="false" LatentStyleCount="156">
</w:LatentStyles>
</xml><![endif]-->
<style>
<!--
/* Font Definitions */
@font-face
{font-family:"MS Mincho";
panose-1:2 2 6 9 4 2 5 8 3 4;
mso-font-alt:"\FF2D\FF33 \660E\671D";
mso-font-charset:128;
mso-generic-font-family:modern;
mso-font-pitch:fixed;
mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
@font-face
{font-family:"\@MS Mincho";
panose-1:2 2 6 9 4 2 5 8 3 4;
mso-font-charset:128;
mso-generic-font-family:modern;
mso-font-pitch:fixed;
mso-font-signature:-1610612033 1757936891 16 0 131231 0;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{mso-style-parent:"";
margin:0in;
margin-bottom:.0001pt;
mso-pagination:widow-orphan;
font-size:12.0pt;
font-family:"Times New Roman";
mso-fareast-font-family:"MS Mincho";
color:black;}
a:link, span.MsoHyperlink
{color:blue;}
a:visited, span.MsoHyperlinkFollowed
{color:blue;}
span.SpellE
{mso-style-name:"";
mso-spl-e:yes;}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.25in 1.0in 1.25in;
mso-header-margin:.5in;
mso-footer-margin:.5in;
mso-paper-source:0;}
div.Section1
{page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
/* Style Definitions */
table.MsoNormalTable
{mso-style-name:"Table Normal";
mso-tstyle-rowband-size:0;
mso-tstyle-colband-size:0;
mso-style-noshow:yes;
mso-style-parent:"";
mso-padding-alt:0in 5.4pt 0in 5.4pt;
mso-para-margin:0in;
mso-para-margin-bottom:.0001pt;
mso-pagination:widow-orphan;
font-size:10.0pt;
font-family:"Times New Roman";
mso-fareast-font-family:"Times New Roman";
mso-ansi-language:#0400;
mso-fareast-language:#0400;
mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="2050"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1"/>
</o:shapelayout></xml><![endif]-->
<div class="Section1">
<p class="MsoNormal"><b>Allan <span class="SpellE">Sindelar</span></b><br>
<span style="font-size:10.0pt"><a
href="mailto:Allan@positiveenergysolar.com"><span
style="color:#000099">Allan@positiveenergysolar.com</span></a></span><br>
<span style="font-size:10.0pt">NABCEP Certified PV
Installation Professional <br>
NABCEP Certified Technical Sales Professional<br>
New Mexico EE98J Journeyman Electrician<br>
Founder and Chief Technology Officer<br>
<b>Positive Energy, Inc.</b>, a Certified B <span
class="SpellE">Corporation<sup><span
style="font-size:7.5pt">TM</span></sup></span><br>
3209 Richards Lane<br>
Santa Fe, New Mexico 87507<br>
<b>505 424-1112 office 780-2738 cell</b><br>
<a href="http://www.positiveenergysolar.com/"
target="_blank">www.positiveenergysolar.com</a></span></p>
</div>
</div>
On 6/7/2013 4:49 PM, Richard L Ratico wrote:<br>
</div>
<blockquote cite="mid:161624337@retriever.VALLEY.NET" type="cite">
<pre wrap="">Allan,
I think most gennies bond the neutral to the chassis so the circuit breakers on
the gennie will trip in the event of a ground fault. If the neutrals weren't
bonded and the breakers didn't trip to clear it, there would be a shock hazard
on the chassis in the event of a fault. Not sure what you mean by suggesting to
disconnect the grounding conductor on the extension cord. If there's a ground
fault in the coffee maker, that might leave any metal parts of the appliance
energized and thus be an extreme shock hazard. Better to investigate the gennie
for a ground to neutral bond as well as the inverter BOS and rewire so the is
only one neutral to gound bond in the entire system, as required by code.
Apologies in advance if I have misunderstood your suggestion. Your posts are
invariably right on.
Dick Ratico
Solarwind Electric
Jeremy,
Outback may be right on, and it's worth checking.
Most portable gennies internally bond neutral to chassis, because they expect
that no typical homeowner will ground the chassis. (Inverter-generators are a
noteworthy exception to this.) Most inverter systems also have a neutral-ground
bond, if done to Code. Whe plugged into the gennie, there's thus an inherent
ground loop. Try disconnecting the grounding conductor on the extension cord.
Allan
Allan Sindelar
<a class="moz-txt-link-abbreviated" href="mailto:Allan@positiveenergysolar.com">Allan@positiveenergysolar.com</a>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
<a class="moz-txt-link-abbreviated" href="http://www.positiveenergysolar.com">www.positiveenergysolar.com</a>
On 6/7/2013 9:10 AM, All Solar, Inc. wrote:
I found out that the appliance will work fine from an extension cord with a
portable generator.
The appliance will not even work however when the backup gen is running and
transfering through the inverters.
Outback T.S. suggested to check the Neutral to ground bond so that is the next
step. Also tried to set the Power Save levels the same (stacked pair)
Jeremy
All Solar
----- Original Message -----
From: Exeltech
To: RE-wrenches
Sent: Wednesday, April 17, 2013 1:51 PM
Subject: Re: [RE-wrenches] Outback wave form
Wrenches,
While the addition of a capacitor may resolve issues associated with various
inverter/appliance/motor combinations, please make sure the capacitor(s) get
switched OUT of the circuit (disconnected) when the load itself is disconnected.
Failure to do so could under some circumstances cause the inverter control-loop
circuitry to go unstable, leading to unpredictable inverter operation, and
possible
damage/failure in the power system. Disconnecting the capacitor with the load
alleviate this possibility.
Regards to all...
Dan Lepinski
--- On Wed, 4/17/13, Larry Crutcher, Starlight Solar Power Systems
<a class="moz-txt-link-rfc2396E" href="mailto:larry@starlightsolar.com"><larry@starlightsolar.com></a> wrote:
From: Larry Crutcher, Starlight Solar Power Systems <a class="moz-txt-link-rfc2396E" href="mailto:larry@starlightsolar.com"><larry@starlightsolar.com></a>
Subject: Re: [RE-wrenches] Outback wave form
To: "RE-wrenches" <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></a>
Date: Wednesday, April 17, 2013, 2:09 PM
We experience issues like this from time to time. PF seems to be the culprit.
Have you measured it or looked at the waveform yet? How an inverter deals with
PF seems to vary broadly. For example, the Splendide XC2100 washer/dryer will
not work on a Magnum Energy and a few other sine wave inverters. However, it
will run on a low cost GoPower or Samlex sine wave inverter. Below is a scope
trace of voltage/current of the Magnum inverter & Splendide washer. Upper trace
is voltage
By adding a 50uF run capacitor inline, it somewhat tames the current phase and
the sine wave so the Magnum can operate the washer.
(Special thanks to Al for the discovery and photos)
Larry Crutcher
Starlight Solar Power Systems
On Apr 16, 2013, at 9:46 AM, All Solar <a class="moz-txt-link-rfc2396E" href="mailto:allsolar@scswifi.net"><allsolar@scswifi.net></a> wrote:
Have a client with a new coffee maker that will not run from their new dual
outback setup. Has anyone heard of this lately. We have had no problems with
appliances and sine wave inverters. What to look for?
Sent from Jeremy's IPhone. Sorry for typos and shorthand!
_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
</body>
</html>