<br><font size=2 face="sans-serif">A PWM charge controller, such as the
C35, will work in this application, because it will </font>
<br><font size=2 face="sans-serif">act like a switch that connects the
panel to the battery. While the bulk voltage will likely be slightly</font>
<br><font size=2 face="sans-serif">higher than Vmp, once the controller
transitions to float, which is approx 27V for most battery types,</font>
<br><font size=2 face="sans-serif">it should allow the module to operate
very close to Vmp. </font>
<br><font size=2 face="sans-serif">Typically, MPPT controllers require
a higher Vmp than the target charge voltage.</font>
<br>
<br><font size=2 face="sans-serif">Eric Bentsen<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Solar
Business</b>  |   <b>UNITED STATES</b>  |   <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001#  |   <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
 |   <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_0D9356A40D95A428005B765C88257B80></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Mac Lewis <maclewis1@gmail.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches <re-wrenches@lists.re-wrenches.org></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">06/04/2013 08:05 AM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">[RE-wrenches] 24V charging with 60 cell
modules</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=3>Hello wrenches,</font>
<br>
<br><font size=3>Is there a good method to charge 24V battery bank with
single 60 cell modules?  Ideally, I'd like to charge a 24 V bank with
a Kyocera 245GX-LFB.  However, at NOTC the Vmp is 26.8V.  Any
good way to do this?</font>
<br>
<br><font size=3>Thanks in advance.<br>
-- </font>
<br>
<br>
<br>
<br><font size=3>Mac Lewis<br>
</font>
<p><font size=2 color=#37605e>"Yo solo sé que no sé nada." </font><font size=2 color=#5f5f5f>-Sócrates</font>
<p><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<p>
<p>