<br><font size=2 face="sans-serif">Hi Allan,</font>
<br>
<br><font size=2 face="sans-serif">The C-series behaves in the same way
as if you were to connect the module directly to the battery, </font>
<br><font size=2 face="sans-serif">then watch a DC volt meter and disconnect/reconnect
when the bulk voltage is reached to "hold" the battery </font>
<br><font size=2 face="sans-serif">at that level. It will hold at the bulk
level for 1 hour, then transition to float.</font>
<br><font size=2 face="sans-serif">If left connected without disconnecting,
the voltage would eventually climb to Voc (approx 36VDC). So, while it
is not </font>
<br><font size=2 face="sans-serif">going to be as efficient as the MPPT
controller in the bulk/absorption stages, once the PWM controller transitions
to float, </font>
<br><font size=2 face="sans-serif">it will operate right about the sweet
spot (Vmp). The question was making a single 24V module work with a 24V
battery.</font>
<br><font size=2 face="sans-serif"> PWM is the only way to do it,
as the MPPT requires a higher PV voltage due to the use of a buck transformer.</font>
<br><font size=2 face="sans-serif"> I will certainly pass on any recommendations
for improvement to our engineering team, and </font>
<br><font size=2 face="sans-serif">I appreciate the feedback.</font>
<br>
<br><font size=2 face="sans-serif">Eric Bentsen</font>
<br><font size=2 face="sans-serif"><br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Eric Bentsen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Solar
Business</b>  |   <b>UNITED STATES</b>  |   <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001#  |   <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
 |   <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
<br>
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_115F1F4C115F1B0400655D0C88257B80></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">From:</font>
<td><font size=1 face="sans-serif">Allan Sindelar <allan@positiveenergysolar.com></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font>
<td><font size=1 face="sans-serif">RE-wrenches <re-wrenches@lists.re-wrenches.org></font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font>
<td><font size=1 face="sans-serif">06/04/2013 10:35 AM</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font>
<td><font size=1 face="sans-serif">Re: [RE-wrenches] 24V charging with
60 cell modules</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font>
<td><font size=1 face="sans-serif">re-wrenches-bounces@lists.re-wrenches.org</font></table>
<br>
<hr noshade>
<br>
<br>
<br><font size=3>Eric,<br>
Please explain further, as what you wrote makes no sense to me. Mac didn't
indicate whether he wanted to charge a flooded battery (~29.2V) or sealed
(~28.4V). The C-series of PWM controllers has a fixed two-hour absorption,
which it only counts down once the bulk voltage is reached. If the bulk
voltage setpoint is above the MPP of the module, as it is in this case,
how can it ever reach float, as you suggest?<br>
<br>
And further, this is spec-sheet calculation. In all but the coldest winter
weather, the Vmp of the module will be lower still as the module temperature
rises above 25ºC, and is likely to be even below the float voltage in
hot weather. And in the winter, if the battery is also cold, it will need
a higher voltage still to get fully charged.<br>
<br>
So I'm with Bob-O on this one. You can't charge a 24V battery with a 20V
module. Please tell us how I'm wrong.<br>
Thanks, Allan<br>
<br>
P.S. - And while I'm on a virtual roll, please tell your engineering folks
to build a charge controller with a higher voltage input window. I don't
mean 600 volts at $1,500 or whatever it is; just higher than 150V. On a
48V system, we're stuck with series strings of three modules if we use
the lowest-cost-per-watt 60-cell modules. That means that systems have
to be designed with arrays in ~750-watt increments. Give us another 50-100V
or so of headroom, so we can design with strings in multiples of 3, 4,
or 5. Outback, are you listening too? The Midnite Classic does this for
us... Thanks.<br>
</font>
<br><font size=3 face="Times New Roman"><b>Allan Sindelar</b></font><font size=2 color=blue><u><br>
</u></font><a href=mailto:Allan@positiveenergysolar.com><font size=2 color=#0000a1 face="Times New Roman"><u>Allan@positiveenergysolar.com</u></font></a><font size=2 face="Times New Roman"><br>
NABCEP Certified Photovoltaic Installer<br>
NABCEP Certified Technical Sales Professional<br>
New Mexico EE98J Journeyman Electrician<br>
Founder and Chief Technology Officer<b><br>
Positive Energy, Inc.</b><br>
3209 Richards Lane (note new address)<br>
Santa Fe, New Mexico 87507<b><br>
505 424-1112</b></font><font size=2 color=blue face="Times New Roman"><u><br>
</u></font><a href=http://www.positiveenergysolar.com/ target=_blank><font size=2 color=blue face="Times New Roman"><u>www.positiveenergysolar.com</u></font></a><font size=3>
</font>
<p>
<p>
<br><font size=3>On 6/4/2013 10:43 AM, </font><a href="mailto:Eric.Bentsen@schneider-electric.com"><font size=3 color=blue><u>Eric.Bentsen@schneider-electric.com</u></font></a><font size=3>
wrote:</font>
<br><font size=2 face="sans-serif"><br>
Hi Mac,</font><font size=3> <br>
</font><font size=2 face="sans-serif"><br>
A PWM charge controller, such as the C35, will work in this application,
because it will <br>
act like a switch that connects the panel to the battery. While the bulk
voltage will likely be slightly</font><font size=3> </font><font size=2 face="sans-serif"><br>
higher than Vmp, once the controller transitions to float, which is approx
27V for most battery types,</font><font size=3> </font><font size=2 face="sans-serif"><br>
it should allow the module to operate very close to Vmp. <br>
Typically, MPPT controllers require a higher Vmp than the target charge
voltage.</font><font size=3> <br>
</font><font size=2 face="sans-serif"><br>
Eric Bentsen</font><font size=3 color=#008000><br>
_____________________________________________________________________________________</font><font size=3>
</font><font size=1 face="Arial"><b><br>
<br>
Eric Bentsen</b>  |  </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b>  |  Solar
Business</b>  |   <b>UNITED STATES</b>  |   <b>Technical
Support Representative</b> <b><br>
Phone:</b> +(650) 351-8237 ext. 001#  |   <b><br>
Email:</b> </font><a href="mailto:eric.bentsen@schneider-electric.com"><font size=1 color=blue face="Arial"><u>eric.bentsen@schneider-electric.com</u></font></a><font size=1 face="Arial">
 |   <b>Site:</b></font><a href="http://www.schneider-electric.com/solar" target=_blank><font size=1 color=blue face="Arial"><u>
www.schneider-electric.com/solar</u></font></a><font size=1 face="Arial">
 |   <b>Address:</b> 250 South Vasco Rd., Livermore, CA 94551
</font><font size=1 color=blue face="Arial"><u><br>
</u></font><font size=3 color=blue><u><br>
</u></font><a href="www.schneider-electric.com/solar"><img src=cid:_2_0FE008C00FE254EC00655D0C88257B80></a><font size=1 color=#00a000 face="Arial"><br>
*** Please consider the environment before printing this e-mail</font><font size=1 face="Arial">
</font><font size=3><br>
<br>
<br>
</font>
<table width=100%>
<tr valign=top>
<td width=15%><font size=1 color=#5f5f5f face="sans-serif">From:</font><font size=3>
</font>
<td width=84%><font size=1 face="sans-serif">Mac Lewis </font><a href=mailto:maclewis1@gmail.com><font size=1 color=blue face="sans-serif"><u><maclewis1@gmail.com></u></font></a><font size=3>
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">To:</font><font size=3>
</font>
<td><font size=1 face="sans-serif">RE-wrenches </font><a href="mailto:re-wrenches@lists.re-wrenches.org"><font size=1 color=blue face="sans-serif"><u><re-wrenches@lists.re-wrenches.org></u></font></a><font size=3>
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Date:</font><font size=3>
</font>
<td><font size=1 face="sans-serif">06/04/2013 08:05 AM</font><font size=3>
</font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Subject:</font><font size=3>
</font>
<td><font size=1 face="sans-serif">[RE-wrenches] 24V charging with 60 cell
modules</font><font size=3> </font>
<tr valign=top>
<td><font size=1 color=#5f5f5f face="sans-serif">Sent by:</font><font size=3>
</font>
<td><a href="mailto:re-wrenches-bounces@lists.re-wrenches.org"><font size=1 color=blue face="sans-serif"><u>re-wrenches-bounces@lists.re-wrenches.org</u></font></a></table>
<br><font size=3><br>
</font>
<hr noshade><font size=3><br>
<br>
<br>
Hello wrenches, <br>
<br>
Is there a good method to charge 24V battery bank with single 60 cell modules?
 Ideally, I'd like to charge a 24 V bank with a Kyocera 245GX-LFB.
 However, at NOTC the Vmp is 26.8V.  Any good way to do this?
<br>
<br>
Thanks in advance.<br>
-- <br>
<br>
<br>
<br>
Mac Lewis</font>
<p><font size=2 color=#37605e>"Yo solo sé que no sé nada."
</font><font size=2 color=#5f5f5f>-Sócrates</font><font size=3> </font>
<p><font size=3><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font></tt><a href="mailto:RE-wrenches@lists.re-wrenches.org"><tt><font size=2 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></tt></a><tt><font size=2><br>
<br>
Change email address & settings:</font></tt><font size=3 color=blue><u><br>
</u></font><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:</font></tt><font size=3 color=blue><u><br>
</u></font><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:</font></tt><font size=3 color=blue><u><br>
</u></font><a href="www.members.re-wrenches.org"><tt><font size=2 color=blue><u>www.members.re-wrenches.org</u></font></tt></a><tt><font size=2><br>
</font></tt>
<p>
<p>
<br><tt><font size=3>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: </font></tt><a href="mailto:RE-wrenches@lists.re-wrenches.org"><tt><font size=3 color=blue><u>RE-wrenches@lists.re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
Change email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=3 color=blue><u>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=3 color=blue><u>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="http://www.re-wrenches.org/etiquette.htm"><tt><font size=3 color=blue><u>www.re-wrenches.org/etiquette.htm</u></font></tt></a><tt><font size=3><br>
<br>
Check out participant bios:<br>
</font></tt><a href="http://www.members.re-wrenches.org/"><tt><font size=3 color=blue><u>www.members.re-wrenches.org</u></font></tt></a><tt><font size=3><br>
<br>
</font></tt>
<br><font size=3><br>
<br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email Security.cloud service.<br>
______________________________________________________________________</font><tt><font size=2>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Change email address & settings:<br>
</font></tt><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List-Archive: </font></tt><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt><font size=2>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
List rules & etiquette:<br>
</font></tt><a href="www.re-wrenches.org/etiquette.htm"><tt><font size=2>www.re-wrenches.org/etiquette.htm</font></tt></a><tt><font size=2><br>
<br>
Check out participant bios:<br>
</font></tt><a href="www.members.re-wrenches.org"><tt><font size=2>www.members.re-wrenches.org</font></tt></a><tt><font size=2><br>
<br>
</font></tt>
<br>
<br>