<div class="moz-cite-prefix">Todd,<br>
The SQF runs on 30V or more, but is happiest above 90V according
to Grundfos, and I have never heard anything suggesting a
disadvantage to the higher voltages.<br>
<br>
I think the 1400 watts is a theoretical maximum, and the pump will
vary its operation and output according to the available wattage (<i>not</i>
the available current). Most SQFs effectively max out at around
800-900 watts. In fact, my pump curves on the 11SQF-2 max out at
900 watts at 300' of head. <br>
<br>
You'd probably do just fine with a single series string of 10-12
modules.<br>
<br>
What I don't know is to what degree you need to worry about low
temperature VOC limits; I'd be careful about getting too close to
300V.<br>
Allan<br>
<br>
<div class="moz-signature">
<meta http-equiv="content-type" content="text/html;
charset=ISO-8859-1">
<title></title>
<font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
<small><a href="mailto:Allan@positiveenergysolar.com"><font
color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
face="Times New Roman, Times, serif"><br>
<span style="font-size: 10pt;">NABCEP Certified Photovoltaic
Installer<br>
NABCEP Certified Technical Sales Professional<br>
New Mexico EE98J Journeyman Electrician<br>
Founder and Chief Technology Officer<br>
<b>Positive Energy, Inc.</b><br>
3209 Richards Lane (note new address)<br>
Santa Fe, New Mexico 87507<br>
<b>505 424-1112</b><br>
<a href="http://www.positiveenergysolar.com/"
target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
<p class="MsoNormal" style="margin-right: 722.25pt;"><span
style="font-size: 10pt;"><font face="Times New Roman, Times,
serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
style=""><br>
</b></span></p>
<span style="font-size: 10pt;"><br>
</span> </div>
On 5/30/2013 4:29 PM, Todd Cory wrote:<br>
</div>
<blockquote cite="mid:51A7D2D3.8000302@finestplanet.com" type="cite">
<meta http-equiv="content-type" content="text/html;
charset=ISO-8859-1">
<font size="+1"><font face="Arial">this question is part 2 about
the customer with the used astropower 75 watt modules -<br>
<br>
he has a grundfos 11sqf-2 already set by the well driller. the
input specifications for the cu200 pump & controller are
30 to 300 vdc, 1400 watts, 8 amps. <br>
<br>
this will initially be running array direct and i am trying to
figure out the wire loss from the modules to the cu200
controller. to do that i need voltage and current numbers. im
assuming the higher the voltage the lower the running current?
<br>
from the specs above: 1400 watts divided by 8 amps = 175
volts... so if i feed this with closer to 300 volts would that
mean the running current would drop to around 4.6 amps?<br>
<br>
thanks for the help,<br>
<br>
todd<br>
<br>
<br>
</font></font> <br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
</body>
</html>