    <div class="moz-cite-prefix"><font size="-1">Hi Bill,<br>
        <br>
        <font size="-1">The dreaded F3......with over 40 Grundfos
          systems out there, I've seen several of these.<br>
          <br>
          <font size="-1">The most likely cause is a bad connection and
            the most common of those <font size="-1">are the splices
              underwater.<br>
              <font size="-1">I hate to say it but it can also be a bad
                CU200<font size="-1">. I've seen the <font size="-1">inter<font
                      size="-1">nal modems go bad.<br>
                      <br>
                      <font size="-1">First test is to jumper the power
                        directly to the pump....if it runs, it's likely
                        the CU200.<br>
                        <font size="-1">If not, it's either wiring or
                          the pump.<br>
                          <br>
                          <font size="-1">If this is PV direct and the
                            weather looks iffy, bring a 36 or 48 v<font
                              size="-1">olt power source with you.<br>
                              <font size="-1">We have a standard deep
                                cycle battery box with 3- 21 AH sealed
                                batteries in series that we use.<br>
                                <br>
                                <font size="-1"><font size="-1">And when
                                    all else fails, pull the pump<font
                                      size="-1">, cut the wires on the
                                      pump side of the splice<font
                                        size="-1"> and test the pump.<br>
                                        <font size="-1">You will need a
                                          4-6" piece of PVC pipe, capped
                                          on one end and filled with
                                          water for this t<font
                                            size="-1">est because<br>
                                            <font size="-1">of the dry
                                              run sensor built into the
                                              pump wiring.</font><br>
                                          </font></font></font></font></font></font></font></font></font><br>
                          <font size="-1">This is my experience....I'm
                            curious to see what others say.<br>
                            <br>
                            <font size="-1">Good luck!</font><br>
                          </font></font></font></font></font></font></font></font></font></font></font>
      <pre class="moz-signature" cols="72">Roy Butler
NABCEP Certified Small Wind Installer®
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  <a class="moz-txt-link-abbreviated" href="http://www.four-winds-energy.com">www.four-winds-energy.com</a>

Join us at the 9th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 18 and 19, 2013 in Stevens Point, Wisconsin
<a class="moz-txt-link-abbreviated" href="http://www.smallwindconference.com">www.smallwindconference.com</a>

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                
</pre>
      On 4/27/2013 9:54 AM, frenergy wrote:<br>
    </div>
    <blockquote cite="mid:936A6A11EB074B5FAC6BCCE262F165CF@D8XG8YH1"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta content="MSHTML 6.00.2900.6357" name="GENERATOR">
      <style></style>
      <div>Wrenches,</div>
      <div> </div>
      <div>        I have been asked to repair a Grundfos SQ
        installation for our area Land Trust.  Pump is not pumping and
        the controller (CU200) is throwing a code of: F3.  The manual
        says loose wires, bad connection, failed CU200 or failed pump. 
        I'm looking for more experience than mine in these matters
        before I drive the 3 hour round trip out there for the repair
        for: most likely issues, tests to conduct, tools, spare parts
        (controller??)......</div>
      <div> </div>
      <div>Thanks in advance,</div>
      <div> </div>
      <div>Bill Battagin</div>
      <div>Feather River Solar Electric<br>
        4291 Nelson St.<br>
        Taylorsville, CA  95983<br>
        530.284.7849 / 6544 fax</div>
      <div> </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>