    <div class="moz-cite-prefix">Hi Troy;<br>
      <br>
      Many moons ago, I looked at the curves as you did, and special
      ordered some 350 amp T fuses, but then I quit making extra work
      for myself.  In a dead short, the 350 is really not going to blow
      that much faster, while the 400 amp blows much faster than a lower
      rated breaker will trip.<br>
      There are several reasons why we use 400s with 4/0 cable.  First
      and foremost is that that is (or was) the fuse and cable size
      recommended by Trace back when we used a lot of class Ts.  If you
      stick with the manufacturer's recommendations, you are doing your
      job by the NEC.   <br>
      "110.3(B) INSTALLATION AND USE:  Listed or labeled equipment shall
      be installed and used in accordance with any instructions included
      in the listing or labeling."<br>
      The 2nd point, is that cables within NEC are designed for
      continuous use 3 hrs or more.  An inverter is not going to exceed
      the cable rating for more than a few seconds during a surge. If
      something is wrong, it will almost always be a higher current
      short, and the fuse will still blow.  The idea of a  short circuit
      situation with an inverter in which a 350 amp fuse would blow, but
      not a 400 amp is just going to be rare.  What CAN happen though is
      a normal surge that could nuisance trip a very expensive and hard
      to replace 350 amp fuse.<br>
      Third, I'm using class T fuses to protect battery cables that are
      never over 10 ft long.  They usually run in conduit for less than
      24 in, so it is considered a nipple, and most of the fill and temp
      adjustment factors don't apply: 310.15 (B)3.  Also, since its for
      short runs and most of the circuit is not in conduit, you can use
      the free air rating of the cables. 310.15(A)2 exception.  At least
      that is how it was explained to me.  I never argued this last
      point with an AHJ, so others could debunk me on that, but I simply
      would show the AHJ the sizing reference in the inverter manual,
      and we're done.<br>
      Finally,  Outback still lists the class T fuse 400 amp for 4/0
      cable but they add a note (for mobile only) since these days class
      T fuses are mostly used in non UL listed fuse holders with no
      disconnects.  Bolt switch still makes UL listed class T
      disconnects, though.  BTW, I'm not advocating for going back to
      the 90s as Robin mentioned and using class T fuse exclusively.  I
      thought the original thread was about adding supplemental
      protection at the battery terminals or for each string, in
      addition to regular breakers.  In that case you can put in larger
      fuses too, because you're really after the interrupt rating more
      than the regular fuse rating.  The Midnite breaker still takes
      care of the primary OCPD requirements. <br>
      <br>
      I'm sure I missed something, so hopefully others might join in as
      well.   (motor circuit fusing?)<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 4/22/2013 4:58 PM, Troy Harvey wrote:<br>
    </div>
    <blockquote
      cite="mid:0DE206DA-633D-41B9-B025-551D6CE24691@heliocentric.org"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      Ray,
      <div><br>
      </div>
      <div>One thing I didn't understand is how you can pair a 400 amp
        class-T fuse with a 4/0 cable. The 400 fuse curve looks like the
        continuous rating is 350A in the graph supplied by Allan. Which
        is well above the 4/0 ampacity of 250A (copper). Anyone want to
        explain?</div>
      <div><br>
        <div apple-content-edited="true">
          <span class="Apple-style-span" style="border-collapse:
            separate; color: rgb(0, 0, 0); font-variant: normal;
            letter-spacing: normal; line-height: normal; orphans: 2;
            text-align: -webkit-auto; text-indent: 0px; text-transform:
            none; white-space: normal; widows: 2; word-spacing: 0px;
            border-spacing: 0px; -webkit-text-decorations-in-effect:
            none; -webkit-text-size-adjust: auto;
            -webkit-text-stroke-width: 0px; ">
            <div style="word-wrap: break-word; -webkit-nbsp-mode: space;
              -webkit-line-break: after-white-space; "><span
                style="font-size: 11px; ">thanks,<br>
                <br>
                Troy Harvey<br>
                ---------------------<br>
                Principal Engineer<br>
                Heliocentric<br>
                801-453-9434<br>
                <a moz-do-not-send="true"
                  href="mailto:taharvey@heliocentric.org">taharvey@heliocentric.org</a><br>
              </span><br>
              <br>
            </div>
          </span>
        </div>
        <br>
        <div>
          <div>On Apr 5, 2013, at 10:12 PM, Ray Walters <<a
              moz-do-not-send="true" href="mailto:ray@solarray.com">ray@solarray.com</a>>
            wrote:</div>
          <br class="Apple-interchange-newline">
          <blockquote type="cite">
            <meta content="text/html; charset=ISO-8859-1"
              http-equiv="Content-Type">
            <div text="#000000" bgcolor="#FFFFFF">
              <div class="moz-cite-prefix">I just finished a rewire and
                we kept the Ananda power center, Allan <span
                  class="moz-smiley-s1"> :-) </span><br>
                Back when we used class T fuses more they were always
                over sized relative to Heinemann breakers.<br>
                400 amp class T fuse = 250 amp breaker= 4/0 cable<br>
                200 amp class T fuse = 175 amp breaker= 2/0 cable<br>
                <br>
                I still think class T fuses are superior in some ways to
                breakers: they have better interrupt capacity and trip
                faster in a short circuit condition.<br>
                <br>
                However, If you spend too much time thinking about and
                looking at the trip curves, you'll break your brain and
                special order some weird fuses and breakers.  (anybody
                need a 350 amp class T fuse?)<br>
                 Just follow the inverter manufacturer's recommendations
                and all will be well.<br>
                On the other hand, William has brought up a topic I have
                harped on for years:  Having the OCPD in the cabinet
                doesn't protect the majority of the circuit.  Class T
                fuses at the battery terminals do, but they're not rated
                for the corrosive environment.  I have thrown a few
                class T fuses away that had acid eating away at the
                ends.<br>
                I don't have the solution, but I will continue to point
                out that this is a real problem. Dropping a wrench
                across the battery terminals can lead to a spectacular
                failure that not only can cause a fire, but might even
                cause a battery explosion, yet NEC offers no
                protection.  <br>
                We use insulated wrenches from experience, and hope for
                the best.  <br>
                <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
                On 4/5/2013 8:29 PM, William Miller wrote:<br>
              </div>
              <blockquote
                cite="mid:6.0.1.1.2.20130405192312.03083f90@millersolar.com"
                type="cite"> Friends:<br>
                <br>
                Good topic.  Some questions:<br>
                <br>
                1. Most manufacturer's present an installation guide
                that shows one OCPD in the battery circuit and that is
                in the BOS cabinet.  This means the battery leads are
                unprotected.  Do we need an OPCD at the battery
                terminals?<br>
                <br>
                2. Class T fuses are generally recommended for this
                application.  The data shows them as "fast acting."  Is
                this a problem?  Will they act too fast and open during
                normal surge loads?<br>
                <br>
                Thanks in advance!<br>
                <br>
                William Miller<br>
                <br>
                <br>
                <br>
                <br>
                <br>
                <blockquote type="cite" class="cite"
                  cite="x-msg://1311/">Troy,<br>
                   <br>
                  Overcurrent device size is matched to the conductor
                  size. The inverse time constant nature of an
                  overcurrent device can typically handle the surge
                  currents as long as conductor sizing has truly been
                  done correctly for the conductor. Circuit breakers are
                  preferred to fuses because they can be reset. <br>
                   <br>
                  There has been volumes written on this issue. The
                  constant current at lowest battery voltage should be
                  used, plus the ac ripple content on the battery
                  circuit. This is usually a much larger conductor than
                  your average designer will plan for. The best thing is
                  to look at Midnight, Outback, and Schneider and see
                  what size overcurrent devices they require for their
                  products. That will give you a good clue as to how to
                  size the conductor and overcurrent device.<br>
                   <br>
                  Bill.<br>
                   <br>
                  <b>From:</b> <a moz-do-not-send="true"
                    class="moz-txt-link-abbreviated"
                    href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
                  [<a moz-do-not-send="true"
                    href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                    eudora="autourl">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
                  <b>On Behalf Of </b>Troy Harvey<br>
                  <b>Sent:</b> Friday, April 05, 2013 3:38 PM<br>
                  <b>To:</b> RE-wrenches<br>
                  <b>Subject:</b> [RE-wrenches] Fuse sizing in battery
                  circuits<br>
                   <br>
                  I've got a question about battery string fusing.
                  Typically we size the wire from the batteries to the
                  inverter based on continuous rating procedures (max
                  power/efficiency)*125%. <br>
                   <br>
                  However a 6kW inverter, can peak at 12kW for 5-10
                  seconds, doubling the source current. That is no big
                  deal for the wire, because it is a short time frame...
                  little heat will be generated. However, in fusing the
                  sub-strings, you need to account for that peak surge
                  current so you don't blow fuses all the time. But if
                  you put a 500-1000 amp fuse on a 4/0 wire, above the
                  max surge draw of the inverter, the wire will be
                  under-protected for its ampacity rating. Any thoughts
                  on the catch-22?<br>
                   </blockquote>
                <br>
                <fieldset class="mimeAttachmentHeader"></fieldset>
                <br>
                <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org/">www.members.re-wrenches.org</a>

</pre>
              </blockquote>
              <br>
            </div>
            _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change email address & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive:
            <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules & etiquette:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>