    <div class="moz-cite-prefix">Hey Bob;<br>
      <br>
      Can you share that AIC vs Voltage chart?<br>
      <br>
      Thanks,<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 4/9/2013 1:46 PM, boB wrote:<br>
    </div>
    <blockquote cite="mid:5164702D.2060909@midnitesolar.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <div class="moz-cite-prefix"><br>
        Those 250 amp and 175 amp breakers we have used for many many
        years now<br>
        have an AIC of 50,000 amps at 125 volts and if you look at the
        curve, at 48 volts<br>
        they are around 100,000 amps.  I think that this information is
        on the label<br>
        of the breaker.<br>
        <br>
        How many problems have you had with the Carlings or any other
        type of<br>
        those large breakers ?<br>
        <br>
        boB<br>
        <br>
        <br>
        On 4/9/2013 10:40 AM, Michael Welch wrote:<br>
      </div>
      <blockquote
        cite="mid:946180.52584.bm@smtp107.sbc.mail.ne1.yahoo.com"
        type="cite"> If anyone would like an Acrobat version of this
        article, you can find it here:<br>
        <br>
        <a moz-do-not-send="true"
          href="ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf"
          eudora="autourl">
          ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf<br>
          <br>
        </a>William Dorsett wrote at 07:00 AM 4/9/2013:<br>
         <br>
        <blockquote type="cite" class="cite" cite="">This topic comes up
          often enough that we ought to mention a yellowed article in
          Home Power, (1992 Issue 27, pg 26). Christopher Freitas wrote
          <i>Overcurrent Protection for Battery-Powered Systems </i>where
          he describes experiments he did back when he was with Ananda.
          He put a 2000 A Big Switch to initiate a short (4/0 cable)
          between the terminals on a set of four golf cart batteries (2
          strings @ 12V). In series, he put in a 500A Shunt so he could
          measure current passing and various fuses and breakers. “For
          comparison, we decided to directly short the battery…the meter
          read 6960 amps peak current (three seconds) …during each test
          the 4/0 cable lifted off the ground 4 inches into the air by
          the forces generated by the extremely high current..” They
          videoed the 250 A ANN buss fuses arc and smoke; the 200A
          Heinemann Series AM breakers (paralleled ones that maybe Roy
          mentioned) went 3 seconds without breaking and the video
          showed a flash and blue smoke. <br>
          175A ITE breaker with 42,000 AIC “simply tripped…but still
          allowed a peak current of 2960 amps<br>
          200A Class T Littlefuse “opened promptly with no external
          signs of stress…1920 amps peak current”<br>
          Christopher’s recommendations: <br>
          “Every AE system must have overcurrent protection able to
          interrupt the maximum current available from the batteries.
          For most systems, the main protection should use current
          limiting high AIC fuses, such as a Class T or Class R. A
          disconnect switch which allows the fuse to be safely changed
          should be included. A lower cost alternative is to mount the
          fuse in a fuse holder without a disconnect. Although the fuse
          would always be electrically hot,  it normally would not be
          changed during the life of the system. The fuse holder should
          be mounted outside the battery enclosure. Fuses should not be
          bolted directly onto the battery terminal, as they are not
          designed to handle the physical stresses that can occur
          without the protection of a fuse holder.<br>
           <br>
          Fuses which have exposed elements, such as ANN fuses, should
          not be used because they are not current limiting and have
          only 2500 amps AIC. They also may be a significant hazard when
          installed near batteries. <br>
           <br>
          High AIC breakers, like the Heinemann Series CF (25,000 Amps
          AIC @ 65VDC) can provide overcurrent protection for individual
          items. They cannot be used to protect lower AIC breakers. This
          eliminates their use as a main disconnect in most systems. <br>
           <br>
          Low AIC breakers, like the Heinemann Series AM (5000A AIC @65
          VDC) or the Square-D QO (5000A @ 125 VDC) can be used in load
          distribution centers and components, but must be protected by
          a current limiting fuse. Using low-AIC breakers alone will not
          provide sufficient protection with a battery system and may be
          a significant hazard during short circuit situations.”<br>
           <br>
          It won’t pull up anymore on HP’s article search but probably
          Michael has a copy he could post for those interested.<i> <br>
          </i> <br>
          Bill  Dorsett</blockquote>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <br>
      </blockquote>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>