      After 100's of thousands of  inverters having been shipped in the
      last many years<br>
      and thousands of inverters broken and shorting the battery
      terminals, there has<br>
      never been (to our knowledge) one breaker that has not tripped.<br>
      <br>
      The Midnite site lists the AIC rating of all our breakers I
      believe.<br>
      <br>
      The Carling F series of Magnetic-Hydraulic breakers poop sheet is
      here...<br>
      <br>
<a class="moz-txt-link-freetext" href="http://www.carlingtech.com/sites/default/files/documents/F-Series_Details_%26_COS_0.pdf">http://www.carlingtech.com/sites/default/files/documents/F-Series_Details_%26_COS_0.pdf</a><br>
      <br>
      I guess there isn't a graph of AIC vs. voltage on their F series
      web page but we remember<br>
      them showing us figures or a graph that says those breakers have
      an AIC of more than<br>
      100,000 amps at 48 volts.  We'll try to find that info or you may
      be able to get that<br>
      from Carling.<br>
      <br>
      I have, many times, directly connected these breakers across good
      L-16 battery strings<br>
      to demonstrate the left-hand rule to people where the 4/0 cable
      jumps apart or towards each<br>
      other when very high current passes through those wires when they
      are near each other.<br>
      <br>
      It always trips.  Never tried it at anything above a 48V battery
      banks IIRC.<br>
      <br>
      Robin would like to mention that anyone that wants to use T-Classc
      fuses.... Welcome back to the 1990's<br>
      <br>
      boB<br>
      <br>
      <br>
      On 4/9/2013 1:23 PM, Ray Walters wrote:<br>
    </div>
    <blockquote cite="mid:516478A6.80809@solarray.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <div class="moz-cite-prefix">Hey Bob;<br>
        <br>
        Can you share that AIC vs Voltage chart?<br>
        <br>
        Thanks,<br>
        <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
        On 4/9/2013 1:46 PM, boB wrote:<br>
      </div>
      <blockquote cite="mid:5164702D.2060909@midnitesolar.com"
        type="cite">
        <meta content="text/html; charset=ISO-8859-1"
          http-equiv="Content-Type">
        <div class="moz-cite-prefix"><br>
          Those 250 amp and 175 amp breakers we have used for many many
          years now<br>
          have an AIC of 50,000 amps at 125 volts and if you look at the
          curve, at 48 volts<br>
          they are around 100,000 amps.  I think that this information
          is on the label<br>
          of the breaker.<br>
          <br>
          How many problems have you had with the Carlings or any other
          type of<br>
          those large breakers ?<br>
          <br>
          boB<br>
          <br>
          <br>
          On 4/9/2013 10:40 AM, Michael Welch wrote:<br>
        </div>
        <blockquote
          cite="mid:946180.52584.bm@smtp107.sbc.mail.ne1.yahoo.com"
          type="cite"> If anyone would like an Acrobat version of this
          article, you can find it here:<br>
          <br>
          <a moz-do-not-send="true"
            href="ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf"
            eudora="autourl">
            ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf<br>
            <br>
          </a>William Dorsett wrote at 07:00 AM 4/9/2013:<br>
           <br>
          <blockquote type="cite" class="cite" cite="">This topic comes
            up often enough that we ought to mention a yellowed article
            in Home Power, (1992 Issue 27, pg 26). Christopher Freitas
            wrote <i>Overcurrent Protection for Battery-Powered Systems
            </i>where he describes experiments he did back when he was
            with Ananda. He put a 2000 A Big Switch to initiate a short
            (4/0 cable) between the terminals on a set of four golf cart
            batteries (2 strings @ 12V). In series, he put in a 500A
            Shunt so he could measure current passing and various fuses
            and breakers. “For comparison, we decided to directly short
            the battery…the meter read 6960 amps peak current (three
            seconds) …during each test the 4/0 cable lifted off the
            ground 4 inches into the air by the forces generated by the
            extremely high current..” They videoed the 250 A ANN buss
            fuses arc and smoke; the 200A Heinemann Series AM breakers
            (paralleled ones that maybe Roy mentioned) went 3 seconds
            without breaking and the video showed a flash and blue
            smoke. <br>
            175A ITE breaker with 42,000 AIC “simply tripped…but still
            allowed a peak current of 2960 amps<br>
            200A Class T Littlefuse “opened promptly with no external
            signs of stress…1920 amps peak current”<br>
            Christopher’s recommendations: <br>
            “Every AE system must have overcurrent protection able to
            interrupt the maximum current available from the batteries.
            For most systems, the main protection should use current
            limiting high AIC fuses, such as a Class T or Class R. A
            disconnect switch which allows the fuse to be safely changed
            should be included. A lower cost alternative is to mount the
            fuse in a fuse holder without a disconnect. Although the
            fuse would always be electrically hot,  it normally would
            not be changed during the life of the system. The fuse
            holder should be mounted outside the battery enclosure.
            Fuses should not be bolted directly onto the battery
            terminal, as they are not designed to handle the physical
            stresses that can occur without the protection of a fuse
            holder.<br>
             <br>
            Fuses which have exposed elements, such as ANN fuses, should
            not be used because they are not current limiting and have
            only 2500 amps AIC. They also may be a significant hazard
            when installed near batteries. <br>
             <br>
            High AIC breakers, like the Heinemann Series CF (25,000 Amps
            AIC @ 65VDC) can provide overcurrent protection for
            individual items. They cannot be used to protect lower AIC
            breakers. This eliminates their use as a main disconnect in
            most systems. <br>
             <br>
            Low AIC breakers, like the Heinemann Series AM (5000A AIC
            @65 VDC) or the Square-D QO (5000A @ 125 VDC) can be used in
            load distribution centers and components, but must be
            protected by a current limiting fuse. Using low-AIC breakers
            alone will not provide sufficient protection with a battery
            system and may be a significant hazard during short circuit
            situations.”<br>
             <br>
            It won’t pull up anymore on HP’s article search but probably
            Michael has a copy he could post for those interested.<i> <br>
            </i> <br>
            Bill  Dorsett</blockquote>
          <br>
          <fieldset class="mimeAttachmentHeader"></fieldset>
          <br>
        </blockquote>
        <br>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <br>
        <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
      </blockquote>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>