    <div class="moz-cite-prefix">Chris Freitas is my hero; that was true
      wrenching,  even better that his mad scientist's experiment is
      still relevant 20 years later.  Here's a link to the full article
      I stumbled on to last night:
<a class="moz-txt-link-freetext" href="http://www.ibiblio.org/london/alternative-energy/homepower-magazine/archives/27/27p26.txt">http://www.ibiblio.org/london/alternative-energy/homepower-magazine/archives/27/27p26.txt</a><br>
      Very cool that William was pulling it from his vault this morning,
      too.<br>
      Chris encased the batteries in concrete or safety, but apparently
      nothing happened to them.<br>
      Just one note Chris mentioned on the smaller breakers, they would
      not see as high a fault current, since they would be wired with #6
      or smaller wire.  This added wire resistance would reduce the
      current at the breaker.  I'm not saying that we depend on that,
      just that a real world short is not going to have 4/0 cables
      protected by a QO breaker.<br>
      Also, I found that higher amp class T fuses (601 to 1200 amps)
      have an AIC of 100,000 amps DC.  SO throwing some of those inline
      on big systems might make sense.  Now if we could just get an acid
      proof fuse holder for them.<br>
      I know 240.21H allows OCPDs in the battery box, but I still don't
      believe the fuses and holders are listed for the corrosive
      environment.<br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 4/9/2013 10:54 AM, <a class="moz-txt-link-abbreviated" href="mailto:toddcory@finestplanet.com">toddcory@finestplanet.com</a> wrote:<br>
    </div>
    <blockquote cite="mid:1365526469.330121242@webmail.finestplanet.com"
      type="cite"><font face="arial" size="3">
        <p style="margin:0;padding:0;">when i hear of current flows like
          this i cant help but wonder is there a risk of batteries
          exploding during these kinds of tests?</p>
        <p style="margin:0;padding:0;"> </p>
        <p style="margin:0;padding:0;">todd</p>
        <p style="margin:0;padding:0;"> </p>
        <p style="margin:0;padding:0;"> </p>
        <p style="margin:0;padding:0;"> </p>
        <p style="margin:0;padding:0;">On Tuesday, April 9, 2013 7:00am,
          "William Dorsett" <a class="moz-txt-link-rfc2396E" href="mailto:wmdorsett@sbcglobal.net"><wmdorsett@sbcglobal.net></a> said:<br>
          <br>
        </p>
        <div id="SafeStyles1365526247">
          <style><!--
  #SafeStyles1365526247 @font-face
         {font-family:Wingdings;
        panose-1:5 0 0 0 0 0 0 0 0 0;}
  #SafeStyles1365526247 @font-face
         {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
  #SafeStyles1365526247 @font-face
         {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
  #SafeStyles1365526247 @font-face
         {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
  #SafeStyles1365526247 @font-face
         {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
  #SafeStyles1365526247 @font-face
         {font-family:Webdings;
        panose-1:5 3 1 2 1 5 9 6 7 3;}

  #SafeStyles1365526247 p.MsoNormal, #SafeStyles1365526247  li.MsoNormal, #SafeStyles1365526247  div.MsoNormal
         {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
  #SafeStyles1365526247 a:link, #SafeStyles1365526247  span.MsoHyperlink
         {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
  #SafeStyles1365526247 a:visited, #SafeStyles1365526247  span.MsoHyperlinkFollowed
         {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
  #SafeStyles1365526247 pre
         {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
  #SafeStyles1365526247 p.MsoAcetate, #SafeStyles1365526247  li.MsoAcetate, #SafeStyles1365526247  div.MsoAcetate
         {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";
        color:black;}
  #SafeStyles1365526247 span.HTMLPreformattedChar
         {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;
        color:black;}
  #SafeStyles1365526247 span.EmailStyle19
         {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
  #SafeStyles1365526247 span.BalloonTextChar
         {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";
        color:black;}
  #SafeStyles1365526247 span.EmailStyle22
         {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
  #SafeStyles1365526247 .MsoChpDefault
         {mso-style-type:export-only;
        font-size:10.0pt;}
  #SafeStyles1365526247 @page WordSection1
         {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
  #SafeStyles1365526247 div.WordSection1
         {page:WordSection1;}
--></style>
          <div class="WordSection1">
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">This topic comes up often enough that we ought
                to mention a yellowed article in Home Power, (1992 Issue
                27, pg 26). Christopher Freitas wrote <em>Overcurrent
                  Protection for Battery-Powered Systems </em>where he
                describes experiments he did back when he was with
                Ananda. He put a 2000 A Big Switch to initiate a short
                (4/0 cable) between the terminals on a set of four golf
                cart batteries (2 strings @ 12V). In series, he put in a
                500A Shunt so he could measure current passing and
                various fuses and breakers. “For comparison, we decided
                to directly short the battery…the meter read 6960 amps
                peak current (three seconds) …during each test the 4/0
                cable lifted off the ground 4 inches into the air by the
                forces generated by the extremely high current..” They
                videoed the 250 A ANN buss fuses arc and smoke; the 200A
                Heinemann Series AM breakers (paralleled ones that maybe
                Roy mentioned) went 3 seconds without breaking and the
                video showed a flash and blue smoke. </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">175A ITE breaker with 42,000 AIC “simply
                tripped…but still allowed a peak current of 2960 amps</span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">200A Class T Littlefuse “opened promptly with
                no external signs of stress…1920 amps peak current”</span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">Christopher’s recommendations: </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">“Every AE system must have overcurrent
                protection able to interrupt the maximum current
                available from the batteries. For most systems, the main
                protection should use current limiting high AIC fuses,
                such as a Class T or Class R. A disconnect switch which
                allows the fuse to be safely changed should be included.
                A lower cost alternative is to mount the fuse in a fuse
                holder without a disconnect. Although the fuse would
                always be electrically hot,  it normally would not be
                changed during the life of the system. The fuse holder
                should be mounted outside the battery enclosure. Fuses
                should not be bolted directly onto the battery terminal,
                as they are not designed to handle the physical stresses
                that can occur without the protection of a fuse holder.</span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;"> </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">Fuses which have exposed elements, such as ANN
                fuses, should not be used because they are not current
                limiting and have only 2500 amps AIC. They also may be a
                significant hazard when installed near batteries. </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;"> </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">High AIC breakers, like the Heinemann Series
                CF (25,000 Amps AIC @ 65VDC) can provide overcurrent
                protection for individual items. They cannot be used to
                protect lower AIC breakers. This eliminates their use as
                a main disconnect in most systems. </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;"> </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">Low AIC breakers, like the Heinemann Series AM
                (5000A AIC @65 VDC) or the Square-D QO (5000A @ 125 VDC)
                can be used in load distribution centers and components,
                but must be protected by a current limiting fuse. Using
                low-AIC breakers alone will not provide sufficient
                protection with a battery system and may be a
                significant hazard during short circuit situations.”</span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;"> </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">It won’t pull up anymore on HP’s article
                search but probably Michael has a copy he could post for
                those interested.<em> </em></span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;"> </span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">Bill  Dorsett</span></p>
            <p class="MsoNormal" style="margin:0;padding:0;"><span
                style="font-size: 11.0pt; font-family:
                "Calibri","sans-serif"; color:
                #1f497d;">Manhattan, KS</span></p>
            <div>
              <div style="border: none; border-top: solid #B5C4DF 1.0pt;
                padding: 3.0pt 0in 0in 0in;">
                <p class="MsoNormal" style="margin:0;padding:0;"><strong><span
                      style="font-size: 10.0pt; font-family:
                      "Tahoma","sans-serif"; color:
                      windowtext;">From:</span></strong><span
                    style="font-size: 10.0pt; font-family:
                    "Tahoma","sans-serif"; color:
                    windowtext;">
                    <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
                    [<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <strong>On
                      Behalf Of </strong>John Berdner<br>
                    <strong>Sent:</strong> Monday, April 08, 2013 7:25
                    PM<br>
                    <strong>To:</strong> <a class="moz-txt-link-abbreviated" href="mailto:Allan@positiveenergysolar.com">Allan@positiveenergysolar.com</a>;
                    RE-wrenches<br>
                    <strong>Subject:</strong> Re: [RE-wrenches] Fuse
                    sizing in battery circuits</span></p>
              </div>
            </div>
            <p class="MsoNormal" style="margin:0;padding:0;"> </p>
            <div>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">Allan:</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;"> </span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">A pretty accurate retention of the Grass
                  Valley / Nevada County through 2000.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">You only missed the Trace to Xantrex
                  “acquisition” that was the start of the divorce </span><span
                  style="font-size: 11.0pt; font-family: Wingdings;
                  color: #1f497d;">J</span><span style="font-size:
                  11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;"> </span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;"> </span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">Class T fuses provide better protection for
                  battery based inverters – always been that way.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">The move to breakers was a cost reduction
                  issues when Trace introduced the DC-250.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">I still contend that the way the DC-250 did
                  it was a Code violation when used with PV in the box
                  (current from all sources issue) but that is history.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;"> </span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">For high current applications the Boltswitch
                  Pull outs (the ones we used in the Power Centers) came
                  in 100A, 200A and 400 A sizes and 1, 2, and 3 pole
                  versions. </span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">I think they are still made today.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">Still the best way to do currents above 250
                  Amps.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">You can do a Eaton / GJ1P breaker up to 750
                  Amps but they are Spin Dee.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;"> </span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">As you noted you can use a single pull out
                  to do up to 3 battery strings.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">You make a copper “comb” to parallel
                  separate fused inputs to a single inverter. </span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">If you have more than one inverter you can
                  have “back to back” fuse blocks with an H-H-H shaped
                  bus bar set up.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">The biggest one I recall we did was a 12 400
                  A battery/PV  inputs going to 8 SW inverters.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;">You size the copper bus bars for 1000 A /
                  square inch of cross section and you are good to go
                  (this is from the UL 508 design guide).</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;"> </span></p>
              <div>
                <p class="MsoNormal" style="margin:0;padding:0;"><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;">Best Regards,</span></p>
                <p class="MsoNormal" style="margin:0;padding:0;"><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;"> </span></p>
                <p class="MsoNormal" style="margin:0;padding:0;"><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;">John Berdner</span></p>
                <p class="MsoNormal" style="margin:0;padding:0;"><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;">General Manager, North America</span></p>
                <p class="MsoNormal" style="margin:0;padding:0;"><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;"> </span></p>
                <p class="MsoNormal" style="margin:0;padding:0;"><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;">SolarEdge Technologies, Inc.</span></p>
                <p class="MsoNormal" style="margin:0;padding:0;"><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;">3347 Gateway Boulevard, Fremont CA 94538
                    USA </span><strong><em><span style="font-size:
                        11.0pt; font-family:
                        "Calibri","sans-serif";
                        color: #c00000;">(*Please note of our new
                        address.)</span></em></strong><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;"><br>
                    T: 510.498.3200, X 747</span></p>
                <p class="MsoNormal" style="margin:0;padding:0;"><span
                    style="font-size: 11.0pt; font-family:
                    "Calibri","sans-serif"; color:
                    #1f497d;">M: 530.277.4894 </span></p>
              </div>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 11.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  #1f497d;"> </span></p>
              <div>
                <div style="border: none; border-top: solid #B5C4DF
                  1.0pt; padding: 3.0pt 0in 0in 0in;">
                  <p class="MsoNormal" style="margin:0;padding:0;"><strong><span
                        style="font-size: 10.0pt; font-family:
                        "Tahoma","sans-serif";
                        color: windowtext;">From:</span></strong><span
                      style="font-size: 10.0pt; font-family:
                      "Tahoma","sans-serif"; color:
                      windowtext;"> <a moz-do-not-send="true"
                        href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
                      [<a moz-do-not-send="true"
                        href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
                      <strong>On Behalf Of </strong>Allan Sindelar<br>
                      <strong>Sent:</strong> Friday, April 05, 2013 9:00
                      PM<br>
                      <strong>To:</strong> RE-wrenches<br>
                      <strong>Subject:</strong> Re: [RE-wrenches] Fuse
                      sizing in battery circuits</span></p>
                </div>
              </div>
              <p class="MsoNormal" style="margin:0;padding:0;"> </p>
              <div>
                <p class="MsoNormal"
                  style="margin:0;padding:0;margin-bottom: 12.0pt;">William,<br>
                  For this I went deep into the catacombs of our
                  hardware file cabinet, and quickly found a 1996 spec
                  sheet from an Ananda Power Technologies SafeT-Block.
                  For the young'uns, Ananda was a quality company, the
                  originator of the listed Powercenter - the breaker and
                  terminal block hardware that is part of every
                  batttery-based system nowadays. Ananda became APT,
                  then Pulse, then part of Trace (the PC250 and PC500)
                  as part of a short-lived marriage followed by a messy
                  divorce, the results of which led, as an act of
                  revenge insurrection, to the introduction into the
                  U.S. market of the Sunny Boy and AC-coupled systems,
                  and the rest is even more wacky history. But I
                  digress, after a run-on sentence bad enough that my
                  high school English teacher is rolling over in her
                  grave...<br>
                  <br>
                  I have attached a scan of page two of the spec sheet.
                  In the upper left corner is a chart of current vs.
                  time for a Class T fuse. Once I understood this chart
                  I never again worried about nuisance tripping, as
                  whether described as fast-acting or not, Class T fuses
                  have an inherent surge capacity of about 2 1/2 times
                  their rating, and thus can handle surges.<br>
                  <br>
                  If you put them on individual battery strings, the
                  point is to prevent overcurrent on one string, which
                  is only likely to occur when either 1) a terminal is
                  corroded sufficiently that one string fails to carry
                  its share of the load or charge (we have seen this) or
                  2) one string fails when the batteries reach
                  end-of-life. When the Class T fuses blows in that
                  situation it has done its job.<br>
                  Allan</p>
                <div>
                  <p class="MsoNormal" style="margin:0;padding:0;"><strong>Allan
                      Sindelar</strong><br>
                    <span style="font-size: 10.0pt;"><a
                        moz-do-not-send="true"
                        href="mailto:Allan@positiveenergysolar.com"><span
                          style="color: #000099;">Allan@positiveenergysolar.com</span></a></span><br>
                    <span style="font-size: 10.0pt;">NABCEP Certified
                      Photovoltaic Installer<br>
                      NABCEP Certified Technical Sales Professional<br>
                      New Mexico EE98J Journeyman Electrician<br>
                      Founder and Chief Technology Officer<br>
                      <strong>Positive Energy, Inc.</strong><br>
                      3209 Richards Lane (note new address)<br>
                      Santa Fe, New Mexico 87507<br>
                      <strong>505 424-1112</strong><br>
                      <a moz-do-not-send="true"
                        href="http://www.positiveenergysolar.com/"
                        target="_blank">www.positiveenergysolar.com</a></span></p>
                  <p class="MsoNormal"
                    style="margin:0;padding:0;mso-margin-top-alt: auto;
                    margin-right: 722.25pt; mso-margin-bottom-alt:
                    auto;"><br>
                    <img moz-do-not-send="true"
                      src="cid:image001.png@1365526469.1842"
                      alt="image001.png"></p>
                  <p class="MsoNormal" style="margin:0;padding:0;"> </p>
                </div>
                <p class="MsoNormal" style="margin:0;padding:0;">On
                  4/5/2013 8:29 PM, William Miller wrote:</p>
              </div>
              <blockquote style="margin-top: 5.0pt; margin-bottom:
                5.0pt;">
                <p class="MsoNormal"
                  style="margin:0;padding:0;margin-bottom: 12.0pt;">Friends:<br>
                  <br>
                  Good topic.  Some questions:<br>
                  <br>
                  1. Most manufacturer's present an installation guide
                  that shows one OCPD in the battery circuit and that is
                  in the BOS cabinet.  This means the battery leads are
                  unprotected.  Do we need an OPCD at the battery
                  terminals?<br>
                  <br>
                  2. Class T fuses are generally recommended for this
                  application.  The data shows them as "fast acting." 
                  Is this a problem?  Will they act too fast and open
                  during normal surge loads?<br>
                  <br>
                  Thanks in advance!<br>
                  <br>
                  William Miller<br>
                  <br>
                  <br>
                  <br>
                  <br>
                  <br>
                </p>
                <p class="MsoNormal" style="margin:0;padding:0;">Troy,<br>
                  <br>
                  Overcurrent device size is matched to the conductor
                  size. The inverse time constant nature of an
                  overcurrent device can typically handle the surge
                  currents as long as conductor sizing has truly been
                  done correctly for the conductor. Circuit breakers are
                  preferred to fuses because they can be reset. <br>
                  <br>
                  There has been volumes written on this issue. The
                  constant current at lowest battery voltage should be
                  used, plus the ac ripple content on the battery
                  circuit. This is usually a much larger conductor than
                  your average designer will plan for. The best thing is
                  to look at Midnight, Outback, and Schneider and see
                  what size overcurrent devices they require for their
                  products. That will give you a good clue as to how to
                  size the conductor and overcurrent device.<br>
                  <br>
                  Bill.<br>
                  <br>
                  <strong>From:</strong> <a moz-do-not-send="true"
                    href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
                  [<a moz-do-not-send="true"
                    href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
                  <strong>On Behalf Of </strong>Troy Harvey<br>
                  <strong>Sent:</strong> Friday, April 05, 2013 3:38 PM<br>
                  <strong>To:</strong> RE-wrenches<br>
                  <strong>Subject:</strong> [RE-wrenches] Fuse sizing in
                  battery circuits<br>
                  <br>
                  I've got a question about battery string fusing.
                  Typically we size the wire from the batteries to the
                  inverter based on continuous rating procedures (max
                  power/efficiency)*125%. <br>
                  <br>
                  However a 6kW inverter, can peak at 12kW for 5-10
                  seconds, doubling the source current. That is no big
                  deal for the wire, because it is a short time frame...
                  little heat will be generated. However, in fusing the
                  sub-strings, you need to account for that peak surge
                  current so you don't blow fuses all the time. But if
                  you put a 500-1000 amp fuse on a 4/0 wire, above the
                  max surge draw of the inverter, the wire will be
                  under-protected for its ampacity rating. Any thoughts
                  on the catch-22?</p>
                <p class="MsoNormal"
                  style="margin:0;padding:0;margin-bottom: 12.0pt;"><br>
                  <br>
                </p>
                <p style="margin:0;padding:0;">_______________________________________________
                </p>
                <p style="margin:0;padding:0;">List sponsored by Home
                  Power magazine
                </p>
                <p style="margin:0;padding:0;"> 
                </p>
                <p style="margin:0;padding:0;">List Address: <a
                    moz-do-not-send="true"
                    href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
                </p>
                <p style="margin:0;padding:0;"> 
                </p>
                <p style="margin:0;padding:0;">Change email address
                  & settings:
                </p>
                <p style="margin:0;padding:0;"><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
                </p>
                <p style="margin:0;padding:0;"> 
                </p>
                <p style="margin:0;padding:0;">List-Archive: <a
                    moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
                </p>
                <p style="margin:0;padding:0;"> 
                </p>
                <p style="margin:0;padding:0;">List rules &
                  etiquette:
                </p>
                <p style="margin:0;padding:0;"><a moz-do-not-send="true"
                    href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
                </p>
                <p style="margin:0;padding:0;"> 
                </p>
                <p style="margin:0;padding:0;">Check out participant
                  bios:
                </p>
                <p style="margin:0;padding:0;"><a moz-do-not-send="true"
                    href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
                </p>
                <p style="margin:0;padding:0;"> 
                </p>
              </blockquote>
              <p class="MsoNormal" style="margin:0;padding:0;"> </p>
            </div>
            <div>
              <p class="MsoNormal" style="margin:0;padding:0;"><span
                  style="font-size: 10.0pt; font-family:
                  "Calibri","sans-serif"; color:
                  navy;">CONFIDENTIALITY NOTICE: This e-mail and its
                  attachments are intended only for the use of the
                  individual or entity who is the intended recipient and
                  may contain information that is privileged,
                  confidential and exempt from disclosure or any type of
                  use under applicable law. If the reader of this e-mail
                  is not the intended recipient, or the employee, agent,
                  or representative responsible for delivering the
                  e-mail to the intended recipient, you are hereby
                  notified that any dissemination, distribution,
                  copying, or other use of this e-mail is strictly
                  prohibited. If you have received this e-mail in error,
                  please reply immediately to the sender.</span></p>
              <p class="MsoNormal" style="margin:0;padding:0;"><strong><span
                    style="font-size: 13.5pt; font-family: Webdings;
                    color: green;" lang="DE">P</span></strong><span
                  style="font-size: 10.0pt; color: green;"> Please think
                  of the environment before printing this email</span></p>
            </div>
          </div>
        </div>
      </font><br>
      <br>
      <br>
      Sent from Finest Planet WebMail.<br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>