      Those 250 amp and 175 amp breakers we have used for many many
      years now<br>
      have an AIC of 50,000 amps at 125 volts and if you look at the
      curve, at 48 volts<br>
      they are around 100,000 amps.  I think that this information is on
      the label<br>
      of the breaker.<br>
      <br>
      How many problems have you had with the Carlings or any other type
      of<br>
      those large breakers ?<br>
      <br>
      boB<br>
      <br>
      <br>
      On 4/9/2013 10:40 AM, Michael Welch wrote:<br>
    </div>
    <blockquote
      cite="mid:946180.52584.bm@smtp107.sbc.mail.ne1.yahoo.com"
      type="cite">
      If anyone would like an Acrobat version of this article, you can
      find it
      here:<br>
      <br>
      <a moz-do-not-send="true"
        href="ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf"
        eudora="autourl">
        ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf<br>
        <br>
      </a>William Dorsett wrote at 07:00 AM 4/9/2013:<br>
       <br>
      <blockquote type="cite" class="cite" cite="">This topic comes up
        often enough
        that we ought to mention a yellowed article in Home Power, (1992
        Issue
        27, pg 26). Christopher Freitas wrote <i>Overcurrent Protection
          for
          Battery-Powered Systems </i>where he describes experiments he
        did back
        when he was with Ananda. He put a 2000 A Big Switch to initiate
        a short
        (4/0 cable) between the terminals on a set of four golf cart
        batteries (2
        strings @ 12V). In series, he put in a 500A Shunt so he could
        measure
        current passing and various fuses and breakers. “For comparison,
        we
        decided to directly short the battery…the meter read 6960 amps
        peak
        current (three seconds) …during each test the 4/0 cable lifted
        off the
        ground 4 inches into the air by the forces generated by the
        extremely
        high current..” They videoed the 250 A ANN buss fuses arc and
        smoke; the
        200A Heinemann Series AM breakers (paralleled ones that maybe
        Roy
        mentioned) went 3 seconds without breaking and the video showed
        a flash
        and blue smoke. <br>
        175A ITE breaker with 42,000 AIC “simply tripped…but still
        allowed a peak
        current of 2960 amps<br>
        200A Class T Littlefuse “opened promptly with no external signs
        of
        stress…1920 amps peak current”<br>
        Christopher’s recommendations: <br>
        “Every AE system must have overcurrent protection able to
        interrupt the
        maximum current available from the batteries. For most systems,
        the main
        protection should use current limiting high AIC fuses, such as a
        Class T
        or Class R. A disconnect switch which allows the fuse to be
        safely
        changed should be included. A lower cost alternative is to mount
        the fuse
        in a fuse holder without a disconnect. Although the fuse would
        always be
        electrically hot,  it normally would not be changed during the
        life
        of the system. The fuse holder should be mounted outside the
        battery
        enclosure. Fuses should not be bolted directly onto the battery
        terminal,
        as they are not designed to handle the physical stresses that
        can occur
        without the protection of a fuse holder.<br>
         <br>
        Fuses which have exposed elements, such as ANN fuses, should not
        be used
        because they are not current limiting and have only 2500 amps
        AIC. They
        also may be a significant hazard when installed near batteries.
        <br>
         <br>
        High AIC breakers, like the Heinemann Series CF (25,000 Amps AIC
        @ 65VDC)
        can provide overcurrent protection for individual items. They
        cannot be
        used to protect lower AIC breakers. This eliminates their use as
        a main
        disconnect in most systems. <br>
         <br>
        Low AIC breakers, like the Heinemann Series AM (5000A AIC @65
        VDC) or the
        Square-D QO (5000A @ 125 VDC) can be used in load distribution
        centers
        and components, but must be protected by a current limiting
        fuse. Using
        low-AIC breakers alone will not provide sufficient protection
        with a
        battery system and may be a significant hazard during short
        circuit
        situations.”<br>
         <br>
        It won’t pull up anymore on HP’s article search but probably
        Michael has
        a copy he could post for those interested.<i> <br>
        </i> <br>
        Bill  Dorsett</blockquote>