      <br>
      I actually used to have info from Trojan on the short circuit
      current available from the T105 and L16.  I just don't remember it
      exactly, but I recall it was around 2000 amps for the T105.  I
      agree its really shameful how lame most battery manus are at
      providing info anymore.  Its hard to even get good cycle life
      tables.<br>
      HUP does show their short circuit #s.  The 845 AH battery is 9600
      amps and for comparison,  the 2490 AH is 29,100 amps.<br>
      So yes, we could have trouble.<br>
      B&B a manufacturer of sealed deep cycle batteries shows their
      12 v 90 AH battery with a whopping short circuit current of 2300
      amps but only for 100 milliseconds.<br>
      Midnite shows their breaker AIC ratings and its 10,000 amps for
      the PV breakers up to 50,000 amps for the 175 and 250 amp
      breakers.  The class T fuses I checked are 20,000 amps AIC. 
      Remember that this is all rated at 125 to 150 vdc, so all of these
      OCPDs will have even better AIC at lower voltages.  (I wish we
      could get a chart that showed AIC relative to voltage.)  The other
      factor in our favor is that the batteries might be able to exceed
      the AIC for tenths of seconds, but it can't sustain it like the
      grid can.<br>
      Sorry that this is not enough info to do a definitive design, but
      at least it can get us all thinking about AIC ratings relative to
      bigger battery banks.<br>
      <br>
      <pre class="moz-signature" cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
      On 4/6/2013 1:21 PM, Kent Osterberg wrote:<br>
    </div>
    <blockquote cite="mid:516075A4.4030703@coveoregon.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <div class="moz-cite-prefix">Phil,<br>
        <br>
        Thanks for the code references, they are very useful and point
        out an area where I fear many installations of battery based
        inverters are deficient. You are right the manufacturers have
        not made this easy!<br>
        <br>
        First, data on the short circuit current available from most
        batteries isn't easily available, if available at all. Concorde
        publishes short circuit current numbers for the SunExtender
        batteries. Neither Trojan, Rolls/Surrette, nor Outback publishes
        short circuit current data for their batteries. Full River
        publishes an internal resistance number that can be used to
        estimate the short circuit current. Taken as a whole, battery
        manufacturer's certainly haven't made it easy to comply with
        690.71<br>
        <br>
        Second, sometimes interrupting capacity data on the breakers
        being used in BOS equipment is also missing. Take a look at
        Outback's catalog and try to find the AIC for the breakers used
        to protect the inverter wiring. Is it published anywhere else?
        Should a system designer have to buy the Outback breaker, find
        out who manufactured it, and then search for the correct ratings
        in the in the breaker manufacturer's catalog? Obviously not.  <br>
        <br>
        Third, BOS manufacturers often connect circuit breakers for
        charge controllers or dc utilization circuits that have AIC
        ratings of only 5000 amps directly to the battery. So while the
        inverter may be protected with a breaker having an AIC rating
        25,000 or 50,000, other devices don't. BOS manufacturer's should
        include on the dc breaker panel data showing the <big>lowest</big>
        AIC breaker that is connected directly to the battery. Then
        installers would have at least half of the information needed to
        decide when a fuse is needed to backup the dc breakers. And
        shouldn't the instructions for BOS equipment point out that a
        fuse may be necessary at the battery.<br>
        <br>
        The short circuit current from a single string of golf cart
        batteries or L16 batteries is probably less than 5000 amps.
        Fuse(s) are probably needed in most installations with larger
        batteries or battery systems with multiple strings of batteries.
        2011 NEC 240.21(H) allows overcurrent protection to be installed
        as close as practical to battery terminals - even in classified
        locations. <br>
        <br>
        <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
</pre>
        <br>
        On 4/6/2013 7:29 AM, Phil Undercuffler wrote:<br>
      </div>
      <blockquote
cite="mid:CAPLQxEL9K1yPVccqJ0J671gy+JLZDGUvzhvupL_s9e3ymAf55Q@mail.gmail.com"
        type="cite">Ray,
        <div><br>
        </div>
        <div>690 does offer the protection, it's just that most
          maufacturers haven't made it easy.</div>
        <div><br>
        </div>
        <div>690.71 Installation</div>
        <div class="pa-70-2011-58-para"
          style="margin-top:3.6pt;margin-bottom:3.6pt">
          <p class="pa-70-2011-58-para"
            style="margin-left:7.2pt;margin-top:1pt;margin-bottom:1pt"><font><span
style="line-height:normal;background-color:rgba(255,255,255,0)"><span
                  style="font-weight:bold">(C)</span> <span
                  style="font-weight:bold">Current Limiting.</span> A
                listed, current-limiting, overcurrent device shall be
                installed in each circuit adjacent to the batteries
                where the available short-circuit current from a battery
                or battery bank exceeds the interrupting or withstand
                ratings of other equipment in that circuit. The
                installation of current-limiting fuses shall comply with
                690.16.<span></span></span></font></p>
        </div>
        <div><br>
        </div>
        <div>
          <div style="">The telcom industry has been doing this for
            years.  Their norm is to have each string of batteries on a
            shelf, and terminate at a breaker.  Each string then is
            combined at a bus bar or plate, to help ensure equal current
            on each string.  The loads and charging sources all come to
            that same bus bar.  It has some advantages, as individual
            strings can be monitored and serviced without taking the
            entire system down.</div>
        </div>
        <div style=""><br>
        </div>
        <div style="">
          <div>FWIW, OutBack makes a battery rack for AGM batteries with
            series string overcurrent and disconnects on every string.
             It's also to my knowledge the first UL1741 Listed device
            available -- the other stuff I've seen is either not listed,
            or is trading on old 508a standards.  AGMs might not be for
            every installation, but for jobs where they are appropriate
            this could be a good, code-compliant solution.</div>
        </div>
        <div style=""><br>
        </div>
        <div style=""><br>
        </div>
        <div style="">Phil Undercuffler</div>
        <div style="">OutBack Power</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
          <br>
          On Friday, April 5, 2013, Ray Walters wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div text="#000000" bgcolor="#FFFFFF">
              <div>I just finished a rewire and we kept the Ananda power
                center, Allan <span><span> :-) </span></span><br>
                Back when we used class T fuses more they were always
                over sized relative to Heinemann breakers.<br>
                400 amp class T fuse = 250 amp breaker= 4/0 cable<br>
                200 amp class T fuse = 175 amp breaker= 2/0 cable<br>
                <br>
                I still think class T fuses are superior in some ways to
                breakers: they have better interrupt capacity and trip
                faster in a short circuit condition.<br>
                <br>
                However, If you spend too much time thinking about and
                looking at the trip curves, you'll break your brain and
                special order some weird fuses and breakers.  (anybody
                need a 350 amp class T fuse?)<br>
                 Just follow the inverter manufacturer's recommendations
                and all will be well.<br>
                On the other hand, William has brought up a topic I have
                harped on for years:  Having the OCPD in the cabinet
                doesn't protect the majority of the circuit.  Class T
                fuses at the battery terminals do, but they're not rated
                for the corrosive environment.  I have thrown a few
                class T fuses away that had acid eating away at the
                ends.<br>
                I don't have the solution, but I will continue to point
                out that this is a real problem. Dropping a wrench
                across the battery terminals can lead to a spectacular
                failure that not only can cause a fire, but might even
                cause a battery explosion, yet NEC offers no
                protection.  <br>
                We use insulated wrenches from experience, and hope for
                the best.  <br>
                <pre cols="72">R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760</pre>
                On 4/5/2013 8:29 PM, William Miller wrote:<br>
              </div>
              <blockquote type="cite"> Friends:<br>
                <br>
                Good topic.  Some questions:<br>
                <br>
                1. Most manufacturer's present an installation guide
                that shows one OCPD in the battery circuit and that is
                in the BOS cabinet.  This means the battery leads are
                unprotected.  Do we need an OPCD at the battery
                terminals?<br>
                <br>
                2. Class T fuses are generally recommended for this
                application.  The data shows them as "fast acting."  Is
                this a problem?  Will they act too fast and open during
                normal surge loads?<br>
                <br>
                Thanks in advance!<br>
                <br>
                William Miller<br>
                <br>
                <br>
                <br>
                <br>
                <br>
                <blockquote type="cite">Troy,<br>
                   <br>
                  Overcurrent device size is matched to the conductor
                  size. The inverse time constant nature of an
                  overcurrent device can typically handle the surge
                  currents as long as conductor sizing has truly been
                  done correctly for the conductor. Circuit breakers are
                  preferred to fuses because they can be reset. <br>
                   <br>
                  There has been volumes written on this issue. The
                  constant current at lowest battery voltage should be
                  used, plus the ac ripple content on the battery
                  circuit. This is usually a much larger conductor than
                  your average designer will plan for. The best thing is
                  to look at Midnight, Outback, and Schneider and see
                  what size overcurrent devices they require for their
                  products. That will give you a good clue as to how to
                  size the conductor and overcurrent device.<br>
                   <br>
                  Bill.<br>
                   <br>
                  <b>From:</b> <a moz-do-not-send="true"
                    href="javascript:_e({}, 'cvml',
                    're-wrenches-bounces@lists.re-wrenches.org');"
                    target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>
                  [<a moz-do-not-send="true" href="javascript:_e({},
                    'cvml',
                    're-wrenches-bounces@lists.re-wrenches.org');"
                    target="_blank">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
                  <b>On Behalf Of </b>Troy Harvey<br>
                  <b>Sent:</b> Friday, April 05, 2013 3:38 PM<br>
                  <b>To:</b> RE-wrenches<br>
                  <b>Subject:</b> [RE-wrenches] Fuse sizing in battery
                  circuits<br>
                   <br>
                  I've got a question about battery string fusing.
                  Typically we size the wire from the batteries to the
                  inverter based on continuous rating procedures (max
                  power/efficiency)*125%. <br>
                   <br>
                  However a 6kW inverter, can peak at 12kW for 5-10
                  seconds, doubling the source current. That is no big
                  deal for the wire, because it is a short time frame...
                  little heat will be generated. However, in fusing the
                  sub-strings, you need to account for that peak surge
                  current so you don't blow fuses all the time. But if
                  you put a 500-1000 amp fuse on a 4/0 wire, above the
                  max surge draw of the inverter, the wire will be
                  under-protected for its ampacity rating. Any thoughts
                  on the catch-22?<br>
                   </blockquote>
                <br>
                <fieldset></fieldset>
              </blockquote>
            </div>
          </blockquote>
        </div>
      </blockquote>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>