<html><head><meta http-equiv="Content-Type" content="text/html charset=us-ascii"><base href="x-msg://673/"></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><div>I've got a question about battery string fusing. Typically we size the wire from the batteries to the inverter based on continuous rating procedures (max power/efficiency)*125%. </div><div><br></div><div>However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling the source current. That is no big deal for the wire, because it is a short time frame... little heat will be generated. However, in fusing the sub-strings, you need to account for that peak surge current so you don't blow fuses all the time. But if you put a 500-1000 amp fuse on a 4/0 wire, above the max surge draw of the inverter, the wire will be under-protected for its ampacity rating. Any thoughts on the catch-22?</div><div><br></div><div><br></div><div apple-content-edited="true">
<span class="Apple-style-span" style="border-collapse: separate; border-spacing: 0px; "><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><span style="font-size: 11px; ">thanks,<br><br>Troy Harvey<br>---------------------<br>Principal Engineer<br>Heliocentric<br>801-453-9434<br><a href="mailto:taharvey@heliocentric.org">taharvey@heliocentric.org</a><br><br></span></div></span></div></body></html>