<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <div class="moz-cite-prefix">William,<br>
      For this I went deep into the catacombs of our hardware file
      cabinet, and quickly found a 1996 spec sheet from an Ananda Power
      Technologies SafeT-Block. For the young'uns, Ananda was a quality
      company, the originator of the listed Powercenter - the breaker
      and terminal block hardware that is part of every batttery-based
      system nowadays. Ananda became APT, then Pulse, then part of Trace
      (the PC250 and PC500) as part of a short-lived marriage followed
      by a messy divorce, the results of which led, as an act of revenge
      insurrection, to the introduction into the U.S. market of the
      Sunny Boy and AC-coupled systems, and the rest is even more wacky
      history. But I digress, after a run-on sentence bad enough that my
      high school English teacher is rolling over in her grave...<br>
      <br>
      I have attached a scan of page two of the spec sheet. In the upper
      left corner is a chart of current vs. time for a Class T fuse.
      Once I understood this chart I never again worried about nuisance
      tripping, as whether described as fast-acting or not, Class T
      fuses have an inherent surge capacity of about 2 1/2 times their
      rating, and thus can handle surges.<br>
      <br>
      If you put them on individual battery strings, the point is to
      prevent overcurrent on one string, which is only likely to occur
      when either 1) a terminal is corroded sufficiently that one string
      fails to carry its share of the load or charge (we have seen this)
      or 2) one string fails when the batteries reach end-of-life. When
      the Class T fuses blows in that situation it has done its job.<br>
      Allan<br>
      <br>
      <div class="moz-signature">
        <meta http-equiv="content-type" content="text/html;
          charset=ISO-8859-1">
        <title></title>
        <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
        <small><a href="mailto:Allan@positiveenergysolar.com"><font
              face="Times New Roman, Times, serif" color="#000099"><u>Allan@positiveenergysolar.com</u></font></a></small><font
          face="Times New Roman, Times, serif"><br>
          <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
            Installer<br>
            NABCEP Certified Technical Sales Professional<br>
            New Mexico EE98J Journeyman Electrician<br>
            Founder and Chief Technology Officer<br>
            <b>Positive Energy, Inc.</b><br>
            3209 Richards Lane (note new address)<br>
            Santa Fe, New Mexico 87507<br>
            <b>505 424-1112</b><br>
            <a href="http://www.positiveenergysolar.com/"
              target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
        <p class="MsoNormal" style="margin-right: 722.25pt;"><br>
          <img src="cid:part3.05040800.01070904@positiveenergysolar.com"
            alt=""></p>
        <span style="font-size: 10pt;"><br>
        </span> </div>
      On 4/5/2013 8:29 PM, William Miller wrote:<br>
    </div>
    <blockquote
      cite="mid:6.0.1.1.2.20130405192312.03083f90@millersolar.com"
      type="cite">
      Friends:<br>
      <br>
      Good topic.  Some questions:<br>
      <br>
      1. Most manufacturer's present an installation guide that shows
      one OCPD
      in the battery circuit and that is in the BOS cabinet.  This means
      the battery leads are unprotected.  Do we need an OPCD at the
      battery terminals?<br>
      <br>
      2. Class T fuses are generally recommended for this application. 
      The data shows them as "fast acting."  Is this a
      problem?  Will they act too fast and open during normal surge
      loads?<br>
      <br>
      Thanks in advance!<br>
      <br>
      William Miller<br>
      <br>
      <br>
      <br>
      <br>
      <br>
      <blockquote type="cite" class="cite" cite="">Troy,<br>
         <br>
        Overcurrent device size is matched to the conductor size. The
        inverse
        time constant nature of an overcurrent device can typically
        handle the
        surge currents as long as conductor sizing has truly been done
        correctly
        for the conductor. Circuit breakers are preferred to fuses
        because they
        can be reset. <br>
         <br>
        There has been volumes written on this issue. The constant
        current at
        lowest battery voltage should be used, plus the ac ripple
        content on the
        battery circuit. This is usually a much larger conductor than
        your
        average designer will plan for. The best thing is to look at
        Midnight,
        Outback, and Schneider and see what size overcurrent devices
        they require
        for their products. That will give you a good clue as to how to
        size the
        conductor and overcurrent device.<br>
         <br>
        Bill.<br>
         <br>
        <b>From:</b> <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
        [<a moz-do-not-send="true"
          href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
          eudora="autourl">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
        <b>On Behalf Of </b>Troy Harvey<br>
        <b>Sent:</b> Friday, April 05, 2013 3:38 PM<br>
        <b>To:</b> RE-wrenches<br>
        <b>Subject:</b> [RE-wrenches] Fuse sizing in battery circuits<br>
         <br>
        I've got a question about battery string fusing. Typically we
        size the
        wire from the batteries to the inverter based on continuous
        rating
        procedures (max power/efficiency)*125%. <br>
         <br>
        However a 6kW inverter, can peak at 12kW for 5-10 seconds,
        doubling the
        source current. That is no big deal for the wire, because it is
        a short
        time frame... little heat will be generated. However, in fusing
        the
        sub-strings, you need to account for that peak surge current so
        you don't
        blow fuses all the time. But if you put a 500-1000 amp fuse on a
        4/0
        wire, above the max surge draw of the inverter, the wire will be
        under-protected for its ampacity rating. Any thoughts on the
        catch-22?<br>
         </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>