    <div class="moz-cite-prefix">William - You're correct, I was
      confused - thanks for setting me straight!<br>
      <br>
      Regards,  Gary<br>
      <br>
      On 3/1/13 1:05 PM, William Miller wrote:<br>
    </div>
    <blockquote
      cite="mid:6.0.1.1.2.20130301103756.02f91ec0@millersolar.com"
      type="cite">
      Gary:<br>
      <br>
      I think you are a little confused about the operating modes of the
      XW
      inverter:<br>
      <br>
      In the AC Passthru mode, no battery charging occurs.  Below is the
      passage from the manual that describes this:<br>
      <br>
      <i>The AC connected to the AC1 or AC2 input is passing directly
        through
        the Xantrex XW<br>
        Series Inverter/Charger to the loads. The batteries are not
        being charged
        in this state.<br>
        <br>
      </i>In the normal transfer mode, battery charging does occur.  It
      is
      my clear understanding that the Xantrex SW and XW inverters and
      the
      Outback FX and Radian inverters will regulate battery charging so
      that
      the charger circuit uses only excess amperage available.  For
      example:  If the input breaker size is programmed for 60 amps and
      there is 60 amps of load, 0 amps of AC will be used for battery
      charging.  If the load decreases to 50 amps, 10 amps of AC will be
      used for battery charging, etc..  Therefore, the OCPD does
      <u>not</u> need to be sized to accommodate both uses of input
      AC.<br>
      <br>
      Below is a passage from the XW Operating Manual that describes
      this:<br>
      <br>
      <i>In addition, the battery charger can reduce its charging
        current to
        the batteries<br>
        so the combined charge AC current and total load current does
        not exceed
        the<br>
        capacity of the generator or trip its output breakers or fuses.<br>
        <br>
      </i>Extending this discussion beyond the current topic (pun
      intended), we
      need to understand what happens if the connected loads exceed the
      input
      breaker rating.  Here the game changes.  The FX inverter can
      not prevent the overload from passing to the input breaker,
      possibly
      tripping it.  The SW, XW and Radian inverters can provide
      "Generator Support."  Do not confuse Generator Support
      with Generator Remote start functions.  Generator Support allows
      the
      inverter to sync to, and assist the AC input source in powering
      loads.  To use the example above:  If the load rises to 70
      amps, the inverter draws energy from the batteries to provide the
      last 10
      amps. <br>
      <br>
      Below is the passage from the XW manual that describes this:<br>
      <br>
      <i>AC2 Breaker:  Sets the AC2 (Gen) breaker size, based on the
        size
        of the installed AC breaker. The<br>
        breaker size must not exceed the capacity of the generator. The
        Xantrex
        XW Series<br>
        Inverter/Charger limits the maximum input current to this
        setting by
        derating its charging<br>
        current to an equivalent of 80% of the AC breaker size. If the
        connected
        loads exceed the<br>
        AC2 breaker setting, the AC breaker trips. The breaker may not
        trip if
        Gen Support is<br>
        enabled and Gen Amps is configured not to exceed the generator’s
        rated
        output current.<br>
        <br>
      </i>I hope this information is relevant, correct and helpful.<br>
      <br>
      Sincerely,<br>
      <br>
      William Miller<br>
      <br>
      <br>
      <br>
      <br>
      At 08:24 AM 3/1/2013, you wrote:<br>
      <blockquote type="cite" class="cite" cite="">Larry:<br>
        <br>
        In the case of the Xantrex XW Series, while in the "AC
        Pass-Thru" Mode, the internal transfer switch relay connects the
        protected loads directly to the AC1 grid input. The XW internal
        battery
        charger is then activated to recharge the battery bank.<br>
        <br>
        The OCPD(s) through which the protected load amps and charging
        amps are
        passing must be sized to accommodate both at the same time.<br>
        <br>
        Regards,<br>
        <br>
        Gary Willett<br>
        Icarus Solar</blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>