Hi Garrison,<div><br></div><div>This is a great discussion and I think I've read all the responses. If I missed this question, please forgive me.  But, in your original post you refer to a 200 amp service.  I don't, though, see mention of the rating of the bus bars.  The bus bars may be rated for something more than 200 amps, depending upon the panel, even if they're protected by a 200 amp main disconnect.  If so, that would increase your backfeed breaker sizing options.</div>
<div><br></div><div>Best wishes, </div><div><br></div><div>Ross Taylor</div><div><br></div>