    <div class="moz-cite-prefix">John (and other Wrenches),<br>
      I read with great interest this post about Sunny Island breaker
      size. We are about to install a large semi-off grid system for a
      wealthy and eccentric customer. The system has 17kW of PV, and
      four SI5048 inverter/chargers, along with an Outback Radian
      serving as an inverter only to some separate protected circuits.
      The system has utility backup power available as well as a backup
      30kW generator, but for a complicated reason the system can't be
      set to feed back into the grid; the SIs' sell function will be
      disabled.<br>
      <br>
      The four SIs are set up as a pair on each 120V phase, as SMA
      allows. After consultation with SMA tech support, I have designed
      each SI to be on a 125A dc breaker. This is done to keep the total
      protected ampacity of the dc battery cabling and bussing to 850
      amps (125 A x 4 = 500 A, plus 175 A x 2 for the Radian, all
      passing through a common 1,000 A shunt to allow accurate SOC
      metering). It's hard enough to address battery cabling and
      shunting with 850 amps; with 175 A dc breakers the total would be
      1,050 amps, and with 250 A dc breakers the total would be 1,350
      amps. <br>
      <br>
      Given that the loads supplied are residential, primarily
      electronic and resistive, and thus few if any large surges, and
      given that the inverters on each phase are paralleled, how much
      should I worry about the 125a dc breaker size? Are there SI
      programming settings that I should know about to better protect
      against nuisance tripping?<br>
      <br>
      Thank you,<br>
      Allan<br>
      <br>
      <div class="moz-signature">
        <meta http-equiv="content-type" content="text/html;
          charset=ISO-8859-1">
        <title></title>
        <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
        <small><a href="mailto:Allan@positiveenergysolar.com"><font
              face="Times New Roman, Times, serif" color="#000099"><u>Allan@positiveenergysolar.com</u></font></a></small><font
          face="Times New Roman, Times, serif"><br>
          <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
            Installer<br>
            NABCEP Certified Technical Sales Professional<br>
            New Mexico EE98J Journeyman Electrician<br>
            Founder and Chief Technology Officer<br>
            <b>Positive Energy, Inc.</b><br>
            3209 Richards Lane (note new address)<br>
            Santa Fe, New Mexico 87507<br>
            <b>505 424-1112</b><br>
            <a href="http://www.positiveenergysolar.com/"
              target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
        <br>
        <br>
        <span style="font-size: 10pt;"> </span> </div>
      On 2/4/2013 1:29 PM, John Berdner wrote:<br>
    </div>
    <blockquote
      cite="mid:B448FC9E37458B469E77EA0BB954AD4702B681E976@mailbox01"
      type="cite">
      <pre wrap="">Ryan:
Not sure what is in the manual now but...The lugs in the SI 5048U are dual 2/0.

We had to use parallel AWG #1 because we kind of painted ourselves into a corner.
The breaker in the SI ended up being 250 Amps, the conduit fitting was only 1.5" and the wire bending space was too small for a 3/0.
The only way to get enough Ampacity in a 1.5" conduit and that wire bending space was to go with dual #1's.

The 250 Amp breaker was used just to get enough current for the very short duration surges without tripping the breaker (12kW per SI).
If not for this a 200 A breaker would have been fine.

Note that the actual full power ampacity required for normal operation is 5kW @ 40 Vdc = 125 Amps continuous.
It is the high surge loads that require more current.
I run mine with a single 2/0 and we have never even come close to hitting full power.
Worst case current is typically while charging not when inverting and I set the current limit so that I do not exceed ampacity of 2/0.
In my experience it takes >= 14kW generator to drive a pair of SI's to full power while charging