<div dir="ltr"><div><div>Hi Kent and Wrenches,<br><br></div>Thanks for sharing that image.  We have some readings that we captured with a Hioki Power Quality Analyzer.<br><br></div>I have this as a PDF, and can send it to anyone who would like to see this, but have also attached a .tiff file that meets the file size requirements of the list.  Send an email to me off-list if you'd like the PDF. <div class="">

<div id=":1ik" class="" tabindex="0"><img class="" src="https://mail.google.com/mail/u/0/images/cleardot.gif"></div></div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Feb 7, 2013 at 10:21 AM, Kent Osterberg <span dir="ltr"><<a href="mailto:kent@coveoregon.com" target="_blank">kent@coveoregon.com</a>></span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <div>The <a href="http://www.aclaratech.com" target="_blank">Aclara</a> <a href="http://www.aclaratech.com/AclaraPLS/pages/default.aspx" target="_blank">TWACS</a>
      signal that knocks the Enphase inverters off line is difficult to
      capture because it only last a few seconds every time the meter
      replies to a ping or data request. I did manage to capture it
      using <a href="http://www.zelscope.com/" target="_blank">Zelscope</a> with a long
      recording time. The attached image shows a pulse at the zero
      crossing of the ac waveform; some crossings don't have a pulse  -
      I think that is a binary zero and the pulse represents a one. The
      pulse does not change the ac frequency and has only a negligible
      effect on the rms ac voltage. However, the time between zero
      crossings is not always 16.67 ms.<br>
      <br>
      Messing with the zero crossing like that is an ugly thing to do to
      the ac voltage. Many things other than inverters can be messed up
      by this. It caused one of my digital clocks to run fast. Our local
      utility has had complaints about numerous other devices that it
      has messed up. I've got some SunnyBoy systems with remote
      monitoring that don't seem to be bothered by this signal. The
      Enphase inverters do not tolerate it. I'm glad to hear that
      Enphase is working on a fix and hope that it is rolled out soon.<span class="HOEnZb"><font color="#888888"><br>
      <pre cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a href="http://www.bluemountainsolar.com" target="_blank">www.bluemountainsolar.com</a>
</pre></font></span><div><div class="h5">
      On 2/5/2013 2:38 PM, Nick Soleil wrote:<br>
    </div></div></div><div><div class="h5">
    <blockquote type="cite">
      <div dir="ltr">
        <div>
          <div>
            <div>Hi wrenches,<br>
              <br>
              The frequency out of range issue is being caused by some
              utility meter's communication "ping".  This ping is
              actually affecting the utility voltage and frequency, and
              can be viewed with a power quality analyzer.  It is highly
              likely that this is affecting a wide variety of
              utility-interactive inverters, but is only noticeable with
              the Enphase systems; due to the high level of visibility
              that our Enlighten monitoring and reporting provides.<br>
            </div>
            <div><br>
            </div>
          </div>
          These changes required that the software undergo a new
          certification process. We have completed our CSA certification
          of the new software, and are validating it's functionality
          before pushing out the solution to our entire population of
          microinverters.  We are in the process of beta testing the
          software fix, and are hoping to have this resolved in
          February.<br>
          <br>
        </div>
        Thank you for your patience as we work to resolve this issue.</div>
      <div class="gmail_extra"><br>
        <br>
        <div class="gmail_quote">On Tue, Feb 5, 2013 at 9:24 AM, <span dir="ltr"><<a href="mailto:penobscotsolar@midmaine.com" target="_blank">penobscotsolar@midmaine.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Dave,<br>
               It doesn't happen often, and the longest I've seen him
            stay "down" is<br>
            about a half hour, but it seems to get progressively worse
            as time goes<br>
            on for some reason (initially only the five minutes, but
            longer down<br>
            times lately). This particular customer is difficult and
            picky, to<br>
            boot. I hope yours is a bit kinder. Mine seems to think we
            did him an<br>
            injustice of monumental proportions.<br>
               We have had the utility out there logging events,
            meetings with the<br>
            utility and another solar company in Maine to discuss all
            this, and<br>
            have kept Enphase in the loop throughout. Enphase has
            responded in a<br>
            responsible and reasonable manner throughout.<br>
               If you want to discuss this with Enphase, call and ask
            for Bret. He's<br>
            the engineer I previously dealt with, although he is second
            tier, he is<br>
            accessible.<br>
            <div>
              <div><br>
                <br>
                <br>
                <br>
                > Thanks Daryl. Does your system also sometimes stay
                off for longer periods<br>
                > sometimes? My clients system can stay off for up to
                64 minutes.<br>
                ><br>
                > Dave<br>
                ><br>
                > -----Original Message-----<br>
                > From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a><br>
                > [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>]
                On Behalf Of<br>
                > <a href="mailto:penobscotsolar@midmaine.com" target="_blank">penobscotsolar@midmaine.com</a><br>
                > Sent: Tuesday, February 05, 2013 12:01 PM<br>
                > To: RE-wrenches<br>
                > Subject: Re: [RE-wrenches] Enphase "AC Frequency
                out of Range"<br>
                ><br>
                > Dave,<br>
                >   We have been having the same problem with an
                Enphase system in Maine. I<br>
                > have been dealing directly with the third tier
                engineers at Enphase and<br>
                > they<br>
                > are working on a software fix for this. The"event"
                itself is only a<br>
                > fraction<br>
                > of a second but IEEE requirements are that the
                inverter shut down for five<br>
                > minutes. I only found out about this problem when
                it started for this<br>
                > customer. It sems that Enphase has already
                addressed the problem with a<br>
                > software fix for the M-190's. The M-215 fix should
                come, according to<br>
                > Enphase, by the end of March. It will be
                automatically downloaded through<br>
                > the Enlighten router.<br>
                >    It's a known issue with Smart Meters with
                Enphase, but should be<br>
                > reconciled soon.<br>
                ><br>
                > Daryl DeJoy<br>
                > NABCEP Certified PV installer<br>
                > Penobscot Solar Design<br>
                > <a href="http://www.penobscotsolar.com" target="_blank">www.penobscotsolar.com</a><br>
                ><br>
                ><br>
                ><br>
                >> Wrenchsters,<br>
                >><br>
                >><br>
                >><br>
                >> I have an Enphase 7.5kW system on a residence
                with utility Smart<br>
                >> Metering, both the PV Production Meter as well
                as the utility billing<br>
                >> meter being "read" every hour. This system has
                experienced many "AC<br>
                >> Frequency Out Of Range" events since the system
                was installed. Below<br>
                >> is copied the Enphase Event message. This
                particular event was for 5<br>
                >> minutes. Most of the events (all events are AC
                Frequency Out Of Range)<br>
                >> last 5 to 10 minutes but occasionally they have
                lasted from 45 minutes<br>
                >> to<br>
                > 64 minutes.<br>
                >><br>
                >><br>
                >><br>
                >> My question is: Could the use of the smart
                metering increase the<br>
                >> likely hood that AC Frequency events happen? Or
                is this just a<br>
                >> coincidence and that we are dealing with
                fluctuating utility power AC<br>
                >> Frequency issues?<br>
                >><br>
                >><br>
                >><br>
                >> <<<br>
                >><br>
                >><br>
                >><br>
                >> Started on: Mon February 04, 2013 12:49 PM EST<br>
                >><br>
                >> Cleared on: Mon February 04, 2013 12:54 PM EST<br>
                >><br>
                >><br>
                >><br>
                >> Recommended action<br>
                >><br>
                >><br>
                >><br>
                >> This condition should correct itself. No action
                is required.<br>
                >><br>
                >> Details<br>
                >><br>
                >><br>
                >><br>
                >> The microinverter reports that the frequency
                coming from the utility<br>
                >> is either too low or too high as specified by
                applicable regional<br>
                > standards.<br>
                >><br>
                >><br>
                >><br>
                >> AC frequency is the frequency at which voltage
                varies on the utility<br>
                >> grid.<br>
                >> Frequency Out of Range events are usually
                transient and<br>
                >> self-correcting by the utility.<br>
                >><br>
                >><br>
                >><br>
                >> When the microinverter detects an out of
                frequency condition, it must<br>
                >> remain offline until the utility has been
                within acceptable limits<br>
                >> continuously for a short period of time
                (seconds to minutes, varies by<br>
                >> region). If during that time the utility again
                exceeds or falls short<br>
                >> of acceptable limits, the five-minute timer
                must restart and the<br>
                >> microinverter may not begin producing power for
                an additional short<br>
                >> period following the last out-of-bounds
                condition.  >><br>
                >><br>
                >><br>
                >><br>
                >> Best,<br>
                >><br>
                >> Dave<br>
                >><br>
                >><br>
                >><br>
                >><br>
                >><br>
                >> David Palumbo<br>
                >><br>
                >> Independent Power LLC<br>
                >><br>
                >> 462 Solar Way Drive<br>
                >><br>
                >> Hyde Park, VT 05655<br>
                >><br>
                >> <a href="http://www.independentpowerllc.com" target="_blank">www.independentpowerllc.com</a><br>
                >><br>
                >> Vermont Solar Partner<br>
                >><br>
                >> 25 Years Experience, <a href="tel:%28802%29%20888-7194" value="+18028887194" target="_blank">(802)
                  888-7194</a><br>
                >><br>
                >><br>
                >><br>
                <br>
              </div>
            </div>
          </blockquote>
        </div>
      </div>
      <br>
    </blockquote>
  </div></div></div>

<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><br>-- <br><p style="margin:0in 0in 0.0001pt"><span style="font-size:14pt">Cordially,</span></p><p style="margin:0in 0in 0.0001pt"><b><span style="font-size:14pt">Nick Soleil</span></b><span style="font-size:14pt"></span></p>



        <p style="margin:0in 0in 0.0001pt"><b><span>Field Applications Engineer<br></span></b></p>
        <p style="margin:0in 0in 0.0001pt"><b><span style="color:rgb(227,108,10)">Enphase Energy</span></b></p><p style="margin:0in 0in 0.0001pt"><span></span><span>Mobile: <a value="+17073212937">(707) 321-2937</a></span></p>

<p style="margin:0in 0in 0.0001pt"><br><b><span style="color:rgb(227,108,10)"></span></b></p><p style="margin:0in 0in 0.0001pt"><a href="http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012" target="_blank"><font><span style="font-family:Arial,sans-serif"><b>Enphase Commercial Solar.</b> <b><span style="color:rgb(255,102,0)">Limitless.</span></b></span></font></a></p>

<p style="margin:0in 0in 0.0001pt"><a href="http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012" target="_blank"><font><span style="font-family:Arial,sans-serif"><b><span style="color:rgb(255,102,0)"><br>

</span></b></span></font></a></p>
        <p style="margin:0in 0in 0.0001pt"><span>1420 North McDowell<br></span></p>
        <p style="margin:0in 0in 0.0001pt"><span>Petaluma, CA
            94954</span></p><p style="margin:0in 0in 0.0001pt"><span></span></p>
        
        <p style="margin:0in 0in 0.0001pt"><span><a href="http://www.enphaseenergy.com/" target="_blank">www.enphase.com</a></span></p>
        <p style="margin:0in 0in 0.0001pt"><span>P: (707)
            763-4784 x7267</span></p>
        <p style="margin:0in 0in 0.0001pt"><span>F: (707)
            763-0784</span></p>
        <p style="margin:0in 0in 0.0001pt"><span>E: <a href="mailto:nsoleil@enphaseenergy.com" target="_blank">nsoleil@enphaseenergy.com</a></span></p><p style="margin:0in 0in 0.0001pt"><span></span></p><span></span>

<p><span style="font-size:11pt;font-family:"Garamond","serif";color:rgb(31,73,125)"><img src="cid:image002.jpg@01CCADC1.BF83EFD0" alt="nabcep logo" border="0" height="38" width="96"> Certified
Solar PV Installer #03262011-300</span></p><p>“Don’t get me wrong: I love nuclear energy! It’s just that I prefer 
fusion to fission. And it just so happens that there’s an enormous 
fusion reactor safely banked a few million miles from us. It delivers 
more than we could ever use in just about 8 minutes. And it’s wireless! 
.”  <br></p><p>- William McDonough
<span></span></p>
</div>

<pre>

This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message.