<DIV><FONT size=2 face=Arial>For claification, the two installs with 
which I'm concerned are:</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>1) Grid or 8.5kW Genset ---> Manual transfer 
switch ---> FlexPower One w/GVFX3524, FM80, Mate ---> transformer to 
240vac ---> Residential Loads. </FONT></DIV>
<DIV><FONT size=2 face=Arial>This set up also has batteries and an 
old 600Wstc PV array tied in to the FP1.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>2) Grid or ~10kW Genset determined 
by auto transfer switch, all located at utility main 
panel/meter located </FONT></DIV>
<DIV><FONT size=2 face=Arial>about 400' from main residence ---> Subpanel and 
sub meter at main residence <--- PV-designated subpanel <--- 8.4kW PV 
array w/Enphase micros.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>It's good to hear (thanks Phil) that PV doesn't 
auto disconnect when the genny kicks on (didn't think this was the case) but 
if the PV does not disconnect don't we end up with PV potentially 
backfeeding to the genset?? Isn't this thread discussing how PV backfeeding 
to a genny is a dangerous configuration??</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>David, I can't disconnect the GVFX when the grid is 
down and the genny on as both grid and genset supply the AC-IN to the inverter 
via the manual transfer switch. But your comment begs the question: Why do you 
recommend disconnecting the inverter?</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Still trying to connect to an Outback tech (Katee 
Wood)...</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV>Eric</DIV>
<DIV><FONT size=2 face=Arial>SunHarvest</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV>----- Original Message ----- </DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=dkatz@aeesolar.com href="mailto:dkatz@aeesolar.com">David Katz</A> 
  </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Wednesday, January 16, 2013 8:12 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] off grid PV 
  connected to generator</DIV>
  <DIV><BR></DIV>Phil,<BR>If Eric is using the FX ot GTFX in an AC coupled mode, 
  he would need to disconnect the grid tie inverter when the generator was 
  running.  From the thread, I cannot tell if this is his 
  situation.<BR>David Katz<BR><BR>Sent from my HTC smartphone on the Now Network 
  from Sprint!<BR><BR><BR>
  <DIV id=htc_header>----- Reply message -----<BR>From: "Phil Undercuffler" 
  <<A href="mailto:solarphil@gmail.com">solarphil@gmail.com</A>><BR>To: 
  "RE-wrenches" <re-wrenches@lists.re-wrenches.org><BR>Subject: 
  [RE-wrenches] off grid PV connected to generator<BR>Date: Tue, Jan 15, 2013 
  8:07 pm<BR><BR></DIV><BR><BR>
  <DIV>
  <DIV dir=ltr>
  <DIV class=gmail_extra>Eric, </DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra>Good questions, and you hit on a number of topics so 
  let me see if I can address them one at a time, not necessarily in 
  chronological order. </DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra>Yes, the optimal application for the GTFX / GVFX 
  inverter series is grid tie with battery backup.  If you just want backup 
  to the grid, the traditional FX is a great solution.  If you need 
  extended run-time and want to integrate a generator, then the Radian series is 
  a better solution because it can not only integrate both grid and generator, 
  but it can change its operating parameters based on which input it's connected 
  to. </DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra>The SW, XW and Radian inverters are all capable of 
  operating on-grid (grid-interactive or backup) or off-grid (with or without a 
  generator).  However, none will automatically disconnect the PV when the 
  genny auto-starts, nor would I suggest that they should.  Realistically, 
  the system should only start the genny when the batteries are near depletion 
  -- if it's started, the batteries need all the help they can get. 
   Rather, the generator should only be disconnected (turned off) when the 
  batteries reach the absorb setpoint.  BTW, I can't speak for everyone but 
  none of those inverters have that functionality, at least not yet.</DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra>With 600 Watts of connected PV, I wouldn't worry about 
  disconnecting the PV.  Even with a small battery bank, the sun will set 
  before that size of array drives the bank anywhere close to an absorb voltage. 
   Add another zero to the PV size and my answer would be different, of 
  course.</DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra>Also, if you do wind up installing an automatic 
  transfer switch with a battery-based inverter system, don't allow the ATS to 
  control the generator starting, even if that flies against every tradition of 
  the generator sales guy.  You don't want the genny running through every 
  minute of the power outage, you want the system to start the genny only when 
  the batteries are low.</DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra>Good luck with it, and enjoy the sun!</DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra>Phil</DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra><BR></DIV>
  <DIV class=gmail_extra><BR>
  <DIV class=gmail_quote>On Tue, Jan 15, 2013 at 1:50 PM, SunHarvest <SPAN 
  dir=ltr><<A href="mailto:eric@harvesthesun.com" 
  target=_blank>eric@harvesthesun.com</A>></SPAN> wrote:<BR>
  <BLOCKQUOTE 
  style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" 
  class=gmail_quote>
    <DIV id=:31>Further, I recently installed a GVFX for a customer. I'm hearing 
    from certain sources that the grid-tied line of inverters from Outback are 
    not designed to interface with a generator. Really??<BR><BR>I was told by 
    Outback to install a transfer switch line/supply side of the inverter; that 
    this was the only way to interface the genny with the inverter; that the AC 
    Hot In could come from grid or a genset. And indeed, this is the only way I 
    can figure out how to get the genny to charge the batteries when the grid 
    goes down. But then again, I don't have the extensive electrical background 
    that allows me to think outside the box as often as I would like...that's 
    why I'm posing my query here for the pros. In this Outback install I have to 
    again advise the homeowner to open the PV breaker to the inverter during 
    generator operation, right? Even though he has a modest 600W (STC) array and 
    an 8.5kW Kohler genset. Hardly the opportunity for solar to feed back to the 
    genny under the most sunny and cool of days. I'm more concerned with the 
    Enphase install.<BR><BR>The Xantrex SW series inverters are fully capable of 
    operating on-grid or off-grid with a genset. So do those inverters 
    automatically disconnect the PV when the genny auto-starts? And with the 
    Outback, is the Mate supposed to do the same (as long as the genny is 
    operated by the auto-start and not a transfer 
  switch)?</DIV></BLOCKQUOTE></DIV><BR><BR></DIV></DIV></DIV>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>