    <div class="moz-cite-prefix">As a courtesy to the Wrenches who
      posted in response to my request, a design followup:<br>
      I completed the design using two Midnite Classic 200s. I specified
      one Classic Lite after learning that the Classic could be used to
      program both units and both could send their data to the web. I'll
      use one MNPV-6 on each 8-module subarray (each needs 4 spaces for
      2P ganged high-voltage breakers, so MNPV-3s won't work). The
      Classics can share a common negative, properly sized.<br>
      <br>
      The rack issue had a fair amount to do with visual height in the
      desired location. Four- and eight-module racks used modules in
      landscape orientation. Six-module racks used landscape also, but
      both three-module and nine-module racks are in portrait
      orientation - both too high (taller than four modules in
      landscape) and visually unappealing. <br>
      <br>
      Re Kent's concerns below: Multiple temperature sensors are not an
      issue. No equalization is necessary with sealed batteries in GTWB,
      and synchronization of absorption and float modes will seldom
      matter - when the utility is up the inverter determines modes of
      both, and when the grid is down the Classics will determine the
      modes of both.As far as voltage adjustment for grid-tie mode, I'm
      not sure to what Kent is referring.<br>
      <br>
      Until this design I had not realized the fundamental limitation of
      the Outback controllers. At 48 Vnom, they will only work with 3
      60-cell module series strings in a cold climate - no more, no
      less. To me that quite limits their applicability. As Kent says,
      even given certain disadvantages to mixing products, "Not one of
      these is a significant enough issue to merit choosing the FM".
      I'll offer that Outback is suddenly way behind the curve on this
      one.<br>
      Allan<br>
      <br>
      <div class="moz-signature">
        <meta http-equiv="content-type" content="text/html;
          charset=ISO-8859-1">
        <title></title>
        <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
        <small><a href="mailto:Allan@positiveenergysolar.com"><font
              face="Times New Roman, Times, serif" color="#000099"><u>Allan@positiveenergysolar.com</u></font></a></small><font
          face="Times New Roman, Times, serif"><br>
          <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
            Installer<br>
            NABCEP Certified Technical Sales Professional<br>
            New Mexico EE98J Journeyman Electrician<br>
            Founder and Chief Technology Officer<br>
            <b>Positive Energy, Inc.</b><br>
            3209 Richards Lane (note new address)<br>
            Santa Fe, New Mexico 87507<br>
            <b>505 424-1112</b><br>
            <a href="http://www.positiveenergysolar.com/"
              target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
        <p class="MsoNormal" style="margin-right: 722.25pt;"><span
            style="font-size: 10pt;"><font face="Times New Roman, Times,
              serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                  w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
              style=""><br>
            </b></span></p>
        <span style="font-size: 10pt;"><br>
        </span> </div>
      On 12/16/2012 1:17 PM, Kent Osterberg wrote:<br>
    </div>
    <blockquote cite="mid:50CE2C6D.4050307@coveoregon.com" type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <div class="moz-cite-prefix">Allen,<br>
        <br>
        I agree with Kirpal's comments. In fact, because the 300-volt
        breakers take up so much extra space, I'd stay with the
        three-modules-in-series design even if using the Classic charge
        controller; unless the PV array was so far away that you need
        the extra voltage to reduce wiring losses. But, for the example
        you are talking about with four modules in series you would want
        a Classic 200 not the Classic 150 because the Classic 150 would
        goes into non-operational hyper-Voc mode at 28°C (82°F),
        measured at the cell. <br>
        <br>
        The fact that the FM charge controller will talk to the Mate has
        advantages: 1) Only one temperature sensor is needed, 2) Voltage
        adjustment for grid-tie mode, and 3) Synchronization of
        equalize, absorb, and float modes. Not one of these is a
        significant enough issue to merit choosing the FM, and suffering
        from it's lower efficiency and poor MPPT tracking, over the
        Midnite Classic or Morningstar TriStar MPPT charge controllers.<br>
        <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>


</pre>
        On 12/16/2012 10:51 AM, Kirpal Khalsa wrote:<br>
      </div>
      <blockquote
cite="mid:CAM5ziKc4wUL8-eeCge4_eZZ65o4=BUzPK20TjGbHNu-o6gne0Q@mail.gmail.com"
        type="cite">Allan...indeed this is a limitation....and yes i
        agree with you that a higher voltage charge controller would be
        a welcome update to Outbacks line up.....Looking at the DPW top
        of pole list, i would suggest to you a design using 15 255 watt
        modules with the FM80 charge controller which would both meet
        your total wattage requirements, would still only  need one
        charge controller, as well as conform to the 3 module
        multiplication requirement....additionally it would require less
        foundation/excavation work, but would in fact be a honker of an
        array....just an idea! Locally in your area I know Focused
        Energy has a good price and availability of the US made
        SolarWorld 255's which we use often...
        <div> Good luck.</div>
        <div>Kirpal<br>
          <br>
          <div class="gmail_quote">On Sun, Dec 16, 2012 at 10:41 AM,
            Allan Sindelar <span dir="ltr"><<a
                moz-do-not-send="true"
                href="mailto:allan@positiveenergysolar.com"
                target="_blank">allan@positiveenergysolar.com</a>></span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              <div text="#000000" bgcolor="#FFFFFF"> Wrenches,<br>
                Please tell me if I'm overlooking something, in what
                appears to be a design weakness:<br>
                <br>
                I would like to use an Outback Radian system for a
                standard GTBB system. In order to take full advantage of
                the system's capabilities, I have to use all of
                Outback's main components; in this case the FM60 or FM80
                charge controller. The problem is that the most common
                (and lower-cost) modules today are 60-cell, meaning 20
                Vnominal. Given the 150V DC hard maximum voltage limit
                of the FM-series charge controller, in our cold climate
                I can only use these 20V modules in 60 Vnominal series
                strings; that is, in multiples of three modules. As the
                Radian is (wisely) offered in 48V only, pairs of modules
                would provide too low a voltage, and series strings of
                four modules would exceed 150 Voc in cold weather. <br>
                <br>
                The base Midnite Classic 150 will safely operate to 198
                VDC in this application, but it won't communicate with
                the Mate3.<br>
                <br>
                Is this a fundamental design limitation in the Radian
                system, suggesting that Outback is due for a controller
                upgrade, or am I missing something obvious? It appears
                that arrays and racks have to be sized in ~720-watt sets
                of three-module series strings, which can be problematic
                in some designs. In the design in question I would like
                to use 16 240W modules on two 8-module pole-top racks
                (for seasonal adjustability); nothing in sets of three
                meets the customer's output and aesthetic needs. <br>
                <br>
                Any solutions would be welcome.<br>
                Thank you,<br>
                Allan<span class="HOEnZb"><font color="#888888"><br>
                    <div>-- <br>
                      <font face="Times New Roman, Times, serif"><b>Allan

                          Sindelar</b></font><br>
                      <small><a moz-do-not-send="true"
                          href="mailto:Allan@positiveenergysolar.com"
                          target="_blank"><font face="Times New Roman,
                            Times, serif" color="#000099"><u>Allan@positiveenergysolar.com</u></font></a></small><font
                        face="Times New Roman, Times, serif"><br>
                        <span style="font-size:10pt">NABCEP Certified
                          Photovoltaic Installer<br>
                          NABCEP Certified Technical Sales Professional<br>
                          New Mexico EE98J Journeyman Electrician<br>
                          Founder and Chief Technology Officer<br>
                          <b>Positive Energy, Inc.</b><br>
                          3209 Richards Lane (note new address)<br>
                          Santa Fe, New Mexico 87507<br>
                          <b><a moz-do-not-send="true"
                              href="tel:505%20424-1112"
                              value="+15054241112" target="_blank">505
                              424-1112</a></b><br>
                          <a moz-do-not-send="true"
                            href="http://www.positiveenergysolar.com/"
                            target="_blank"><u>www.positiveenergysolar.com</u></a></span></font>
                      <p class="MsoNormal" style="margin-right:722.25pt"><span
                          style="font-size:10pt"><b><br>
                          </b></span></p>
                      <span style="font-size:10pt"></span> </div>
                  </font></span></div>
            </blockquote>
          </div>
        </div>
      </blockquote>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>