<DIV><FONT size=2 face=Arial>Last flat roof mount I did was in San Francisco 
(high winds, strict building codes). We worked with a roofer who requested that 
we simply place an L-foot on top of a 3-1/2" block of PT wood or IPE and 
lay the block on a pad of EPDM straight on the roof; lag down an L-foot 
through the block into the supporting roof members and the roofer would 
come behind us and flash around the block & foot. Not sure if this will work 
in your case...</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Stikes</FONT></DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=wirewiz@gmail.com 
  href="mailto:wirewiz@gmail.com">wirewiz@gmail.com</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, December 31, 2012 6:17 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] EPDM Roof 
  Attachment/Flashing</DIV>
  <DIV><BR></DIV>
  <DIV>Hello Wrenches,</DIV>
  <DIV><BR></DIV>Installing rail mounted PV array on a 2 1/2 / 12 pitch EPDM 
  residential roof. It's a flat section of roof in the middle of the house. Need 
  to keep it low so would like to use 3" or 4" Unirac standoffs. The standard 
  1-6" peel and stick witches hat is fine for a 7" standoff but too 
  tall for the 3-4" standoff. Unirac and Oatey have advised against using the 
  Oatey aluminum flashing although the roofer who did the roof said it 
  would be OK using seam tape between the Oatey and the EPDM. Another roofer I 
  know has said absolutely not. 
  <DIV><BR></DIV>
  <DIV>I did find a rubber Masterflash (6" x 6" base) that's a good fit but all 
  their images show it used on metal roofs only and it's not a peel and stick. 
  Can I use it with seam tape and/or caulking.</DIV>
  <DIV><BR></DIV>
  <DIV>Do I just need to go with the 7" standoff and the standard peel and 
  stick witches hat and forget the low profile?</DIV>
  <DIV><BR></DIV>
  <DIV>Or is their some other system out there (roof attachment/flashing) that 
  would keep it low. The ridge height is already at the 35 ft limit and the 
  upper row of mod's would go above the ridge with the 7" standoff.</DIV>
  <DIV><BR></DIV>
  <DIV>I will work with a roofer but would like to figure this out before just 
  turning it over to the roofer</DIV>
  <DIV><BR></DIV>
  <DIV>Very much appreciate any thoughts.</DIV>
  <DIV><BR></DIV>
  <DIV>Thank you and Happy New Year to you all.</DIV>
  <DIV>
  <DIV><BR></DIV>Larry Liesner<BR>Design and Installations<BR>Elektron Solar, 
  LLC<BR>49 Richmondville Ave Suite 107<BR>Westport, CT 06880<BR>203-557-3127 
  (office)<BR>203-644-2404 (cell)<BR>203-549-0977 (fax)<BR><A 
  href="mailto:wirewiz@gmail.com" target=_blank>wirewiz@gmail.com</A><BR>NABCEP 
  Certified PV Installer (# 032611-184)<BR></DIV>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE>
<DIV> </DIV></BODY></HTML>