<DIV>Alan,</DIV>
<DIV> </DIV>
<DIV>        It seems like a full load analysis is 
a requirement for off-grid.  If you're simply encouraging a customer to do 
a load analysis you may as well hand them a tail and hope they find the 
donkey.  Granted it's easy to slide on it as it represents a great deal of 
time and most customers don't really "get it". It's the most difficult part of 
off-grid.</DIV>
<DIV> </DIV>
<DIV>        Fairly large?.....Hmmm, 20-25 CF? I 
would figure 1.7 KWhr/day.  With a freezer being a constant load and winter 
having less solar, of course your idea of having the freezer outside would 
help.  Though you're having to cool more in the summer, there is more 
solar to do so.</DIV>
<DIV> </DIV>
<DIV>        Will a DC-to-DC converter run a DC 
freezer?  </DIV>
<DIV> </DIV>
<DIV>        Yes, I think 55 watts is a good 
number for the "typical" 48", slow-med speed AC ceiling fan.  They 
certainly have their place but there goes another 1.3 KWhrs/day as people tend 
to leave them on all the time.</DIV>
<DIV> </DIV>
<DIV>Bill</DIV>
<DIV><IMG height=112 alt="" hspace=0 
src="cid:B64605BA2AEB4789A216511C992EC7AE@D8XG8YH1" width=302 align=baseline 
border=0></DIV>
<DIV> </DIV>
<BLOCKQUOTE 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=allan@positiveenergysolar.com 
  href="mailto:allan@positiveenergysolar.com">Allan Sindelar</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, December 10, 2012 8:12 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] Two Load 
  Questions</DIV>
  <DIV><BR></DIV>Wrenches,<BR>We still try to encourage prospective off grid 
  customers to do a full load analysis as an initial step in the system design 
  process. To the point:<BR><BR>1) What is a good watt-hours/day figure to use 
  for a typical, modern, new, carefully chosen, fairly large conventional AC 
  chest freezer, if kept in a heated indoor location? Assume 65 degrees and 
  seldom opened.<BR><BR>I will encourage that the freezer be located in a 
  shaded, protected outdoor location, in order to greatly reduce winter energy 
  consumption, but I need a good base figure to work with. <BR><BR>The proposed 
  system will most likely be 48Vnom, so a Sundanzer or similar DC freezer is 
  out.<BR><BR>2) Same question for a ceiling fan, for general slow circulation 
  of winter heat. The energystar.gov list gives relative cfm efficiency but not 
  wattages. Is 55W still a good figure to use as a default?<BR><BR><BR>I have 
  attached a condensed energystar.gov list for the freezers, but wonder what 
  other off grid Wrenches typically use. Also, I'm not sure that Wrenches posts 
  allow attachments, so this may not appear with my message.<BR><BR>Thank 
  you,<BR>Allan<BR>
  <DIV class=moz-signature>-- <BR><FONT 
  face="Times New Roman, Times, serif"><B>Allan Sindelar</B></FONT><BR><SMALL><A 
  href="mailto:Allan@positiveenergysolar.com"><FONT 
  face="Times New Roman, Times, serif" 
  color=#000099><U>Allan@positiveenergysolar.com</U></FONT></A></SMALL><FONT 
  face="Times New Roman, Times, serif"><BR><SPAN style="FONT-SIZE: 10pt">NABCEP 
  Certified Photovoltaic Installer<BR>NABCEP Certified Technical Sales 
  Professional<BR>New Mexico EE98J Journeyman Electrician<BR>Founder and Chief 
  Technology Officer<BR><B>Positive Energy, Inc.</B><BR>3209 Richards Lane (note 
  new address)<BR>Santa Fe, New Mexico 87507<BR><B>505 424-1112</B><BR><A 
  href="http://www.positiveenergysolar.com/" 
  target=_blank><U>www.positiveenergysolar.com</U></A><O:P></O:P></SPAN></FONT> 
  <P class=MsoNormal style="MARGIN-RIGHT: 722.25pt"><SPAN 
  style="FONT-SIZE: 10pt"><FONT 
  face="Times New Roman, Times,             serif"><ST1:PLACE 
  w:st="on"><ST1:CITY w:st="on"></ST1:CITY><ST1:STATE 
  w:st="on"></ST1:STATE><ST1:POSTALCODE 
  w:st="on"></ST1:POSTALCODE></ST1:PLACE></FONT><B><BR></B></SPAN></P><SPAN 
  style="FONT-SIZE: 10pt"><BR></SPAN></DIV>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>