    <div class="moz-cite-prefix">The NEC 100 definition for a wet
      location includes "unprotected locations exposed to the weather."
      Obviously the roof is a wet location. NEC 334.1(A) says NM cable
      is permitted in normally dry locations and 334.1(B) says it shall
      not be used in damp or wet locations. That said, inspectors here
      have allowed a short length (up to 18" stub) of NM cable through
      conduit to a j-box or outlet on the roof provided that the box and
      cover are appropriate for the location. This is a topic that you
      should probably address with the inspector when your project
      permit is pulled. Don't expect everyone to accept this practice.
      You might need a j-box in the attic to change wire type to NMC
      cable or THWN wire.<br>
      <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
</pre>
      On 11/1/2012 5:07 AM, Chris Mason wrote:<br>
    </div>
    <blockquote
cite="mid:CAG6C1qnzkwvHAQysG2wp_bZvO_r+eBO0PPwQ2ec18D9aXGOX8Q@mail.gmail.com"
      type="cite">I remember from a project we were doing that required
      Romex that it is listed for damp locations such as outdoor areas
      likely to see some rain, wet locations are literally underwater
      rated and designate conduits running underground likely to flood.
      <div>
        <br>
        <div class="gmail_quote">On Wed, Oct 31, 2012 at 10:50 AM, Glenn
          Burt <span dir="ltr"><<a moz-do-not-send="true"
              href="mailto:glenn.burt@glbcc.com" target="_blank">glenn.burt@glbcc.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div bgcolor="white" link="blue" vlink="purple" lang="EN-US">
              <div>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Seems
                    if the Romex is not listed as being suitable for use
                    in a wet location, having not been tested by UL for
                    that situation, it would not be suitable for use in
                    that environment, regardless of how its internal
                    conductors are rated.</span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Glenn
                    Burt</span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                <div>
                  <div style="border:none;border-top:solid #b5c4df
                    1.0pt;padding:3.0pt 0in 0in 0in">
                    <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
                        Ray Walters [mailto:<a moz-do-not-send="true"
                          href="mailto:ray@solarray.com" target="_blank">ray@solarray.com</a>]
                        <br>
                        <b>Sent:</b> Friday, October 26, 2012 10:28 PM<br>
                        <b>To:</b> <a moz-do-not-send="true"
                          href="mailto:glenn.burt@glbcc.com"
                          target="_blank">glenn.burt@glbcc.com</a>;
                        RE-wrenches</span></p>
                    <div>
                      <div class="h5"><br>
                        <b>Subject:</b> Re: [RE-wrenches] Enphase and
                        Romex</div>
                    </div>
                  </div>
                </div>
                <div>
                  <div class="h5">
                    <p class="MsoNormal"> </p>
                    <p class="MsoNormal" style="margin-bottom:12.0pt">So
                      if the Romex is loaded with THHN/THWN (damp/wet
                      rated), and no where does the outer covering of
                      the Romex itself get exposed to the wet location,
                      that should be sufficient? <br>
                      <br>
                      Ray Walters</p>
                    <div>
                      <p class="MsoNormal">On 10/26/2012 7:45 PM, Glenn
                        Burt wrote:</p>
                    </div>
                    <blockquote
                      style="margin-top:5.0pt;margin-bottom:5.0pt">
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">300.9
                          Raceways in Wet Locations Above Grade.</span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Where
                          raceways are installed in wet locations
                          abovegrade, the interior of these raceways
                          shall be considered to be a wet location.
                          Insulated conductors and cables installed in
                          raceways in wet locations abovegrade shall
                          comply with 310.8(C).</span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">“Section
                          300.9, new for the 2008 Code and similar to
                          300.5(B), draws attention to the inside of all
                          raceways and enclosures installed in an
                          abovegrade wet location. The inside of these
                          raceways and enclosures now definitively
                          requires conductors and cables suitable for
                          use in wet locations in accordance with to
                          310.8.” – Explanatory note</span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">310.8
                          Locations.</span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">(C)
                          Wet Locations. Insulated conductors and cables
                          used in wet locations shall comply with one of
                          the following:     </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">(1)
                                   Be moisture-impervious metal-sheathed
                        </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">(2)
                                   Be types MTW, RHW, RHW-2, TW, THW,
                          THW-2, THHW, THWN, THWN-2, XHHW, XHHW-2, ZW </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">(3)
                                   Be of a type listed for use in wet
                          locations</span></p>
                      <p class="MsoNormal">
                        <span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                      <div>
                        <div style="border:none;border-top:solid #b5c4df
                          1.0pt;padding:3.0pt 0in 0in 0in">
                          <p class="MsoNormal">
                            <b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
                              <a moz-do-not-send="true"
                                href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                                target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>
                              [<a moz-do-not-send="true"
                                href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                                target="_blank">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
                              <b>On Behalf Of </b>benn kilburn<br>
                              <b>Sent:</b> Friday, October 26, 2012 2:03
                              PM<br>
                              <b>To:</b> RE-wrenches<br>
                              <b>Subject:</b> Re: [RE-wrenches] Enphase
                              and Romex</span></p>
                        </div>
                      </div>
                      <p class="MsoNormal"> </p>
                      <div>
                        <div>
                          <div>
                            <p class="MsoNormal">
                              <span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">Glenn/Jason,</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">So
                                you wouldn't use romex to feed an
                                exterior outlet on an outside wall, or
                                to any outside lights???</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"> </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">Canadian
                                Electrical Code's (CE Code) definitions…</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><u><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">wet
                                  location</span></u><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"> -a
                                location in which liquids may drip,
                                splash, or flow on or against electrical
                                equipment.</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><u><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">Damp
                                  location</span></u><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">
                                –an exterior or interior location that
                                is normally or periodically subject to
                                condensation of moisture in, on, or,
                                adjacent to electrical equipment an
                                includes partially protected locations
                                under canopies, parquees, roofed open
                                porches, and similar locations.</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><u><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">Dry
                                  location </span></u><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">–a
                                location not normally subject to
                                dampness, but that may include a
                                location subject to temporary dampness
                                as in the case of a building under
                                construction, provided that ventilation
                                is adequate to prevent an accumulation
                                of moisture. </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"> </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">If
                                inside your attic is considered a "wet
                                location", then you have other issues.
                                 Are you sure the NEC's definition of
                                'wet location' is relating to the
                                location of the romex?</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">I
                                just spoke to one of my inspectors and
                                he sees no issue with entering the
                                bottom of a soladeck with romex.  </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"> </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">On
                                the grounding/bonding, I have been using
                                the bare wire in the romex for the
                                enphase system ground (within the
                                enphase cable) and running a #6 from the
                                mod frames and rails into the soladeck
                                and along side the romex back to the
                                panelboard.</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"> </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">I
                                need to get myself a copy of your NEC so
                                I can be on the same page as you guys.
                                 I hear it is written in a way that is
                                much easier to interpret than the CE
                                Code, which is written in a very legal
                                jargon.</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"> </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">Cheers,</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">benn</span></p>
                          </div>
                          <div>
                            <div>
                              <div>
                                <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">DayStar
                                    Renewable Energy Inc. </span></p>
                              </div>
                              <div>
                                <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"><a
                                      moz-do-not-send="true"
                                      href="http://www.daystarsolar.ca"
                                      target="_blank">www.daystarsolar.ca</a>
                                     *  Ph: <a moz-do-not-send="true"
                                      href="tel:780-906-7807"
                                      value="+17809067807"
                                      target="_blank">780-906-7807</a> </span></p>
                              </div>
                              <div>
                                <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">Construction
                                    Electrician Solar Photovoltaic
                                    Systems Certified</span></p>
                              </div>
                              <div>
                                <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">Certificate
                                    # 0007S</span></p>
                              </div>
                              <div>
                                <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">HAVE
                                    A SUNNY DAY</span></p>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"> </span></p>
                      </div>
                      <div>
                        <div>
                          <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">On
                              25/10/12 9:37 AM, "Glenn Burt" <<a
                                moz-do-not-send="true"
                                href="mailto:glenn.burt@glbcc.com"
                                target="_blank">glenn.burt@glbcc.com</a>>
                              wrote:</span></p>
                        </div>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue"> </span></p>
                      </div>
                      <div>
                        <div>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Soladeck
                              on the rooftop places it in an environment
                              that is considered ‘wet’.</span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">I
                              don’t think Romex is listed for use in a
                              wet environment.</span></p>
                          <p class="MsoNormal">
                            <span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">This
                              would force you to use the proposed jbox
                              in the attic for the transition location.</span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">I
                              also understood that you could combine the
                              EGC and GEC into a single conductor as
                              long as it is continuous or irreversibly
                              spliced, as part of the ’08 code.</span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">-Glenn
                              Burt</span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                          <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:blue">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:blue">
                              <a moz-do-not-send="true"
                                href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                                target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>
                              [<a moz-do-not-send="true"
                                href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                                target="_blank">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
                              <b>On Behalf Of </b>Jason Szumlanski<br>
                              <b>Sent:</b> Thursday, October 25, 2012
                              9:13 AM<br>
                              <b>To:</b> RE-wrenches<br>
                              <b>Subject:</b> [RE-wrenches] Enphase and
                              Romex</span></p>
                          <p class="MsoNormal"><span style="color:blue"> </span></p>
                          <p class="MsoNormal"><span style="color:blue">I'm
                              sure this has been covered, but I could
                              not find it in the archives.</span></p>
                          <div>
                            <p class="MsoNormal"><span
                                style="color:blue"> </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
                                style="color:blue">We are considering
                                using Romex in the attic for the first
                                time. My plan was to use the new Enphase
                                coupler to connect the trunk cable to
                                Type TC-ER, enter a Soladeck passthrough
                                box on the roof into a junction box in
                                the attic where I would make the
                                transition to 10/3 Romex. I'm hung up on
                                the GEC going back to the service panel.
                                Any suggestions?</span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"><span
                                style="color:blue"> </span></p>
                          </div>
                          <div>
                            <p class="MsoNormal"
                              style="margin-bottom:12.0pt"><span
                                style="color:blue">By the way, we are on
                                NEC 2008, and in most cases there is
                                also a requirement for an additional
                                grounding electrode per NEC 690.47(D)
                                (that shouldn't really relate to my
                                issue).</span></p>
                            <div>
                              <div>
                                <div style="margin-bottom:6.0pt">
                                  <p
                                    style="margin:0in;margin-bottom:.0001pt"><strong><span
style="font-size:10.0pt;font-family:"Verdana","sans-serif";color:gray">Jason
                                        Szumlanski</span></strong><em><span
style="font-size:10.0pt;font-family:"Verdana","sans-serif";color:gray"> </span></em></p>
                                  <p
                                    style="margin:0in;margin-bottom:.0001pt"><em><span
style="font-size:10.0pt;font-family:"Verdana","sans-serif";color:gray">Fafco
                                        Solar</span></em></p>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                      <p class="MsoNormal"><span
style="font-size:8.5pt;font-family:"Arial","sans-serif";color:blue">_______________________________________________
                          List sponsored by Home Power magazine List
                          Address: <a moz-do-not-send="true"
                            href="mailto:RE-wrenches@lists.re-wrenches.org"
                            target="_blank">RE-wrenches@lists.re-wrenches.org</a>
                          Options & settings: <a
                            moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                            target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
                          List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                            target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
                          List rules & etiquette: <a
                            moz-do-not-send="true"
                            href="http://www.re-wrenches.org/etiquette.htm"
                            target="_blank">www.re-wrenches.org/etiquette.htm</a>
                          Check out participant bios: <a
                            moz-do-not-send="true"
                            href="http://www.members.re-wrenches.org"
                            target="_blank">www.members.re-wrenches.org</a>
                        </span></p>
                      <p class="MsoNormal"><br>
                        <br>
                        <br>
                      </p>
                      <pre>_______________________________________________</pre>
                      <pre>List sponsored by Home Power magazine</pre>
                      <pre> </pre>
                      <pre>List Address: <a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a></pre>
                      <pre> </pre>
                      <pre>Options & settings:</pre>
                      <pre><a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></pre>
                      <pre> </pre>
                      <pre>List-Archive: <a moz-do-not-send="true" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></pre>
                      <pre> </pre>
                      <pre>List rules & etiquette:</pre>
                      <pre><a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a></pre>
                      <pre> </pre>
                      <pre>Check out participant bios:</pre>
                      <pre><a moz-do-not-send="true" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a></pre>
                      <pre> </pre>
                    </blockquote>
                    <p class="MsoNormal">
                       </p>
                  </div>
                </div>
              </div>
            </div>
            <br>
            _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Options & settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules & etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm"
              target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
            <br>
          </blockquote>
        </div>
        <br>
        <br clear="all">
        <div><br>
        </div>
        -- <br>
        Chris Mason
        <div>President, Comet Systems Ltd</div>
        <div><a moz-do-not-send="true"
            href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div>
        <div>
          Cell: 264.235.5670</div>
        <div>Skype: netconcepts</div>
        <br>
      </div>
    </blockquote>
    <br>
  </body>
</html>