<html><body><div style="color:#000; background-color:#fff; font-family:arial, helvetica, sans-serif;font-size:10pt">We've got dozens of installs here, and more recently in Hawaii with Romex coming out of the bottom of a soladeck into the attic space, just make sure the Romex in the attic is labeled and it's sized correctly....<br><div><span><br></span></div><div><span></span></div><div> </div><div><span style="font-family: tahoma,new york,times,serif;">Max Balchowsky</span><br style="font-family: tahoma,new york,times,serif;"><span style="font-family: tahoma,new york,times,serif;">Design Engineer</span><br style="font-family: tahoma,new york,times,serif;"><span style="font-family: tahoma,new york,times,serif;">SEE Systems</span><br style="font-family: tahoma,new york,times,serif;"><span style="font-family: tahoma,new york,times,serif;">1048 Irvine Ave Suite 217</span><br style="font-family: tahoma,new york,times,serif;"><span style="font-family:
 tahoma,new york,times,serif;">Newport Beach, Ca. 92660</span><br style="font-family: tahoma,new york,times,serif;"><span style="font-family: tahoma,new york,times,serif;">760-403-6810</span><span style="font-family: tahoma,new york,times,serif;"></span><br></div>  <div style="font-family: arial,helvetica,sans-serif; font-size: 10pt;"> <div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"> <div dir="ltr"> <font face="Arial" size="2"> <hr size="1">  <b><span style="font-weight: bold;">From:</span></b> benn kilburn <benn@daystarsolar.ca><br> <b><span style="font-weight: bold;">To:</span></b> RE-wrenches <re-wrenches@lists.re-wrenches.org> <br> <b><span style="font-weight: bold;">Sent:</span></b> Friday, October 26, 2012 11:02 AM<br> <b><span style="font-weight: bold;">Subject:</span></b> Re: [RE-wrenches] Enphase and Romex<br> </font> </div> <br>
<div id="yiv4979869"><div><div><div><div>Glenn/Jason,</div><div>So you wouldn't use romex to feed an exterior outlet on an outside wall, or to any outside lights???</div><div><br></div><div>Canadian Electrical Code's (CE Code) definitions…</div><div><u>wet location</u> -a location in which liquids may drip, splash, or flow on or against electrical equipment.</div><div><u>Damp location</u> –an exterior or interior location that is normally or periodically subject to condensation of moisture in, on, or, adjacent to electrical equipment an includes partially protected locations under canopies, parquees, roofed open porches, and similar locations.</div><div><u>Dry location </u>–a location not normally subject to dampness, but that may include a location subject to temporary dampness as in the case of a building under construction, provided that ventilation is adequate to prevent an accumulation of moisture. </div><div><br></div><div>If inside
 your attic is considered a "wet location", then you have other issues.  Are you sure the NEC's definition of 'wet location' is relating to the location of the romex?</div><div>I just spoke to one of my inspectors and he sees no issue with entering the bottom of a soladeck with romex.  </div><div><br></div><div>On the grounding/bonding, I have been using the bare wire in the romex for the enphase system ground (within the enphase cable) and running a #6 from the mod frames and rails into the soladeck and along side the romex back to the panelboard.</div><div><br></div><div>I need to get myself a copy of your NEC so I can be on the same page as you guys.  I hear it is written in a way that is much easier to interpret than the CE Code, which is written in a very legal jargon.</div><div><br></div><div>Cheers,</div><div>benn</div><div><div><div>DayStar Renewable Energy Inc. </div><div>www.daystarsolar.ca  *  Ph:
 780-906-7807 </div><div>Construction Electrician Solar Photovoltaic Systems Certified</div><div>Certificate # 0007S</div><div>HAVE A SUNNY DAY</div></div></div></div></div><div><br></div><span id="yiv4979869OLK_SRC_BODY_SECTION"><div><div>On 25/10/12 9:37 AM, "Glenn Burt" <<a rel="nofollow" ymailto="mailto:glenn.burt@glbcc.com" target="_blank" href="mailto:glenn.burt@glbcc.com">glenn.burt@glbcc.com</a>> wrote:</div></div><div><br></div><div><style><!--
#yiv4979869  
 _filtered #yiv4979869 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}
 _filtered #yiv4979869 {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
 _filtered #yiv4979869 {font-family:Verdana;panose-1:2 11 6 4 3 5 4 4 2 4;}
#yiv4979869  
#yiv4979869 p.yiv4979869MsoNormal, #yiv4979869 li.yiv4979869MsoNormal, #yiv4979869 div.yiv4979869MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New Roman", "serif";}
#yiv4979869 a:link, #yiv4979869 span.yiv4979869MsoHyperlink
        {color:blue;text-decoration:underline;}
#yiv4979869 a:visited, #yiv4979869 span.yiv4979869MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
#yiv4979869 p
        {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman", "serif";}
#yiv4979869 span.yiv4979869EmailStyle20
        {font-family:"Calibri", "sans-serif";color:#1F497D;}
#yiv4979869 .yiv4979869MsoChpDefault
        {font-family:"Calibri", "sans-serif";}
 _filtered #yiv4979869 {margin:1.0in 1.0in 1.0in 1.0in;}
#yiv4979869 div.yiv4979869WordSection1
        {}
--></style><div lang="EN-US"><div class="yiv4979869WordSection1"><div class="yiv4979869MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125); font-family: Calibri,sans-serif;">Soladeck on the rooftop places it in an environment that is considered ‘wet’.</span></div><div class="yiv4979869MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125); font-family: Calibri,sans-serif;">I don’t think Romex is listed for use in a wet environment.</span></div><div class="yiv4979869MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125); font-family: Calibri,sans-serif;">  </span></div><div class="yiv4979869MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125); font-family: Calibri,sans-serif;">This would force you to use the proposed jbox in the attic for the transition location.</span></div><div class="yiv4979869MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125); font-family: Calibri,sans-serif;">I
 also understood that you could combine the EGC and GEC into a single conductor as long as it is continuous or irreversibly spliced, as part of the ’08 code.</span></div><div class="yiv4979869MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125); font-family: Calibri,sans-serif;">  </span></div><div class="yiv4979869MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125); font-family: Calibri,sans-serif;">-Glenn Burt</span></div><div class="yiv4979869MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125); font-family: Calibri,sans-serif;">  </span></div><div class="yiv4979869MsoNormal"><b><span style="font-size: 10pt; font-family: Tahoma,sans-serif;">From:</span></b><span style="font-size: 10pt; font-family: Tahoma,sans-serif;"> <a rel="nofollow" ymailto="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank"
 href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a> [<a rel="nofollow" ymailto="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Jason Szumlanski<br><b>Sent:</b> Thursday, October 25, 2012 9:13 AM<br><b>To:</b> RE-wrenches<br><b>Subject:</b> [RE-wrenches] Enphase and Romex</span></div><div class="yiv4979869MsoNormal">  </div><div class="yiv4979869MsoNormal">I'm sure this has been covered, but I could not find it in the archives.</div><div><div class="yiv4979869MsoNormal">  </div></div><div><div class="yiv4979869MsoNormal">We are considering using Romex in the attic for the first time. My plan was to use the new Enphase coupler to connect the trunk cable to Type TC-ER, enter a Soladeck passthrough box on the roof into a junction box in the attic where
 I would make the transition to 10/3 Romex. I'm hung up on the GEC going back to the service panel. Any suggestions?</div></div><div><div class="yiv4979869MsoNormal">  </div></div><div><div class="yiv4979869MsoNormal" style="margin-bottom: 12pt;">By the way, we are on NEC 2008, and in most cases there is also a requirement for an additional grounding electrode per NEC 690.47(D) (that shouldn't really relate to my issue).</div><div id="yiv4979869WISESTAMP_SIG_2952"><div><div style="margin-bottom: 6pt;"><div style="margin: 0in 0in 0.0001pt;"><b><span class="yui_3_7_2_18_1351279790841_117" style="font-size: 10pt; color: gray; font-family: Verdana,sans-serif;">Jason Szumlanski</span></b><i><span class="yui_3_7_2_18_1351279790841_118" style="font-size: 10pt; color: gray; font-family: Verdana,sans-serif;"> </span></i><span style="font-size: 10pt; font-family: Verdana,sans-serif;"></span></div><div style="margin: 0in 0in 0.0001pt;"><i><span
 class="yui_3_7_2_18_1351279790841_120" style="font-size: 10pt; color: gray; font-family: Verdana,sans-serif;">Fafco Solar</span></i><span style="font-size: 10pt; font-family: Verdana,sans-serif;"></span></div></div></div></div></div></div></div></div> _______________________________________________
List sponsored by Home Power magazine

List Address: <a rel="nofollow" ymailto="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
<a target="_blank" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a target="_blank" href="http://www.members.re-wrenches.org/">www.members.re-wrenches.org</a>

</span></div></div><br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a ymailto="mailto:RE-wrenches@lists.re-wrenches.org" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules & etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br><br><br> </div> </div>  </div></body></html>