Hello Wrenches,<div><br></div><div>We have commissioned a new SI system (240V single phase residential) and want to ensure testing is adequate to ensure the system will perform as desired.</div><div><br></div><div>The system consists of two SI5048s, 5kW PV array, SB5000US, battery bank, transfer switch, backup generator, and supplemental digital relay to activate DigIn signal on Grid DOWN condition.</div>
<div><br></div><div>I am sure there are many test scenarios to run through to qualify the system.  Here is one.</div><div>Test Case 1</div><div><ol><li>Verify SOC is 95%+</li><li>Modify GnSocTm1Str and GnSocTm1Stp to artificially high numbers (85% and  90% respectively)</li>
<li>Power off SB5000US to eliminate charging from solar</li><li>Simulate Grid Outage</li><li>Verify Transfer switch moves to generator input position</li><li>Verify DigIn signal to SI5048 reflects grid state (grid is down)</li>
<li>Monitor SOC and verify that when SOC reaches GnSocTm1Str (85%) the SI starts the generator</li><li>Monitor SOC and verify that when SOC reaches GnSocTm1Stp (95%) the SI stops the generator</li><li>Power ON the SB5000US</li>
<li>Reset GnSocTm1Str and GnSocTm1Stp to system specific values.</li><li>End Test </li></ol><div>Another test would be to bring the grid back up after step 7 or after step 8 and verify correct behavior.</div></div><div><br>
</div><div>I would love to hear from those who have commissioned similar SI configurations, about other scenarios we should be testing to adequately qualify the system.</div><div><br></div><div>Carl Adams</div><div>SunRock Solar</div>
<div>NABCEP Certified PV Installer</div>