Hello wrenches,<div><br></div><div>I am looking for advice on how the 120% rule applies to feeders for a subpanel.  I have this scenario:</div><div>150A bus rating on subpanel with main breaker of 100A.  The conductors feeding this subpanel are 100A rated conductors.  Can I backfeed with a 40A breaker?</div>
<div><br></div><div>Thanks<br clear="all"><div><br></div>-- <br><div><br></div><div><font color="#305A78" face="'times new roman', serif"><br></font></div><div><br></div>Mac Lewis<br><br><span style="font-family:'Times New Roman';font-size:medium;color:rgb(255,153,0)"><b><font face="Arial, Helvetica, sans-serif" size="3"><p align="left">
<font color="#000000" face="Verdana, Arial, Helvetica, sans-serif"><span style="font-size:small"><span style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font face="'times new roman', serif">"Yo solo sé que no sé nada." </font><span style="font-weight:700;color:rgb(104,104,104)"><font face="'times new roman', serif">-Sócrates</font></span></span></span></font></p>