    <div class="moz-cite-prefix">Jeff,<br>
      <br>
      Is there any surge protection in the combiner boxes? Any damage
      visible in the combiner boxes? Any fuses or breakers open in the
      combiner boxes? Is each pole a single string of modules or
      multiple strings of modules?<br>
      <br>
      While there where undoubtedly ground currents flowing they
      probably didn't cause the damage in the module junction boxes. The
      PV module and wiring to it form a loop - often a loop with a large
      area in the vicinity of the module. The current from the lightning
      strike has a tremendous dI/dt and the changing magnetic field from
      it will induce voltages in any wire loop. <br>
      <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
t: 541-568-4882

</pre>
      On 9/7/2012 7:40 AM, Jeff Irish wrote:<br>
    </div>
    <blockquote
      cite="mid:3F29743641444D499E478C7E358A5F046BEB578B@HVCE1.hvce.local"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 14 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Arial","sans-serif";
        color:windowtext;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";}
.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri","sans-serif";}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">A
            customer of ours has recently suffered lightning damage to
            31 out of 160 top of pole mounted modules.  This is the
            first time in 10 years that I’ve seen modules damaged by
            lightning.  Lots of inverter GF fuses and a few inverters,
            but never modules.  We’re trying to determine if it was
            caused by the lightning flash irradiating the modules or
            ground currents. 
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">The
            array consists of 16 DP&W top of pole mounts with 10
            modules each, arranged in a square of 4 poles E-W and 4 rows
            N-S.  The poles are 13 feet center to center E-W and the N-S
            row spacing is about 50 feet.  The poles are 6 inch
            galvanized Technoposts, augured 5 – 7 feet into the firm
            ground, connected with a network of about 160 feet of bare
            #6 copper and at least 8 copper plated ground rods. 
            Altogether we have about 130 square feet of bare metal
            surface area connected and buried in the ground at and
            around the array.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">The
            customer saw lightning strike just after dawn a few weeks
            ago a couple hundred feet to the southwest where it also
            destroyed two utility pole mount distribution transformers
            and ran along the utility wires 100 feet south of the
            array.  The inverters are 200 feet NW and suffered no
            damage.  The array and modules look totally fine, except
            some of the J-boxes are deformed from heat.  Opening the
            J-boxes shows varying levels of damage to one or more
            diodes, from discoloration to being broken and cracked
            open.  <o:p>
            </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">The
            odd thing is the pattern of damage (we’ve tested all the
            modules individually for Voc and Isc).  Only modules in the
            south row of 4 poles are damaged, and the damage is
            concentrated on the modules closest to the ground; modules
            higher up in the air appear OK.  Also, damage is less
            frequent as you move east, away from the direction of the
            strike. 
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">If
            it was caused by ground currents, why would the current want
            to go up the poles, why only the southern row of poles, and
            why damage more modules closer to the ground and not those
            at the top?  Is it possible a flash near the ground
            irradiated the modules causing a current spike and the
            southern row shielded the other rows from most of the
            flash?  Anyone have experience with this?<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:10.5pt;color:black"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">Jeff
            Irish, PE</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">President</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">Hudson
            Solar</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">13
            Hook Road</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">Rhinebeck,
            NY 12572</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">T.845.876.3767x110</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">F.845.876.3912</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><a
              moz-do-not-send="true" href="mailto:jeff@hudsonsolar.com"><span
                style="color:blue">jeff@hudsonsolar.com</span></a></span><o:p></o:p></p>
        <p class="MsoNormal"><i><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">Solar
              Electric Systems</span></i><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><o:p></o:p></span></p>
        <p class="MsoNormal"><i><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">NYSERDA
              Eligible PV Installer</span></i><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><o:p></o:p></span></p>
        <p class="MsoNormal"><i><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">NABCEP
              Certified Solar PV Installer</span></i><i><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:purple"></span></i><i><span
              style="color:purple"><o:p></o:p></span></i></p>
        <p class="MsoNormal"><i><span
style="font-size:10.0pt;font-family:"Arial","sans-serif"">NABCEP
              Certified PV Technical Sales</span></i><o:p></o:p></p>
        <p class="MsoNormal"
          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
            style="color:#919191"><a moz-do-not-send="true"
href="applewebdata://B5F2562A-2B67-4161-84E4-42F12DC28720/www.hudsonsolar.com"><span
                style="color:blue">HudsonSolar.com</span></a></span><span
            style="font-size:10.5pt;color:black"><o:p></o:p></span></p>
        <p class="MsoNormal"
          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
            style="font-size:9.0pt;color:#6D6D6D">2011 NYSERDA
            Excellence in Quality Award | 2011 NYSEIA Award Winner |
            2009 Best of the Hudson Valley | 2008 SunPower Dealer of the
            Year | EDC Business Excellence Award for Innovation</span><span
            style="font-size:10.5pt;color:black"><o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>